Selection of an AC Motor to Replace the DC Motor

03/31/2014 3:08 AM

Hi;

In a "Single Facer" unit of our Corrugator machine, the "take up conveyor" has a DC motor 5.9KW 2700RPM. We want to replace this DC motor with an AC motor and inverter. On the driven side, there is a gear box with two sprockets which rotate two rolls on which a belt is installed. As there is no high starting torque required, so I am going to select a 10KW 2pole AC inverter duty motor. What do you think, is it ok?

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32209
Good Answers: 839
#1

Re: Selection of an AC motor to replace the DC motor

03/31/2014 4:47 AM

It won't be OK unless the power supply is altered to AC as well.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Sep 2009
Posts: 1058
Good Answers: 88
#2

Re: Selection of an AC motor to replace the DC motor

03/31/2014 6:03 AM

10KW 2 pole to me looks marginal for this application. How can you tell the starting torque is always low? For such a modification, I'd use more than double the original DC motor capacity. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#3

Re: Selection of an AC motor to replace the DC motor

03/31/2014 7:55 AM

A AC motor and inverter as a direct replacement will not work. The rollers on most of these machines do not start up at full speed. Control of the speed on a DC motor is voltage driven on an AC motor it is frequency. More will need to be considered on how to control the ramp up of the speed.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1694
#4

Re: Selection of an AC Motor to Replace the DC Motor

03/31/2014 9:15 AM

The DC motor was used for a reason in the original design, probably speed control.

I'd say it's an overall cost vs proper application decision.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Selection of an AC Motor to Replace the DC Motor

03/31/2014 10:19 AM

Why not 7.5KW 4-pole? How often does the motor start/stop?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#6
In reply to #5

Re: Selection of an AC Motor to Replace the DC Motor

03/31/2014 12:32 PM

To your point, why not a 4-pole motor? I'm guessing they looked at the RPM ratings for a 2-pole motor and decided that since it was faster than a 4-pole motor that it would be more suited to their 2700 rpm DC motor speed.

Surely their inverter would go faster than "rated speed" and take a 4-pole motor to 2700 rpm. And I'm thinking (although thinking can be dangerous) that the loading would be distributed better in the motor/bearings of a 4 pole motor verses a 2 pole motor. Then again, maybe that is single phase thinking.....

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9
In reply to #5

Re: Selection of an AC Motor to Replace the DC Motor

03/31/2014 7:23 PM

Typo; I meant 2-pole, and guessed that 7.5kW is a standard size.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#7

Re: Selection of an AC Motor to Replace the DC Motor

03/31/2014 1:36 PM

Given your present info I do not see why either running a 2 pole motor below its stock speed or running a 4 pole motor above its stock speed via a VFD unit would cause any problems.

As far as starting torque with and decent VFD unit thats not an issue being most will allow a programmable starting torque boost to go 200 - 400% over the continuous running torque and let the user select the overall ramp up and ramp down times to be user programed to whatever works best for the application.

If it was me I would be more inclined to use a 6 KW 4 pole motor running above its normal stock speed over using an over sized 2 pole motor running at below its stock speed.

Everything else is just a matter of personal choice regarding what brands and models of components you use and how you chose to set the system up. No need to over complicate it with 'what ifs'.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4499
Good Answers: 137
#13
In reply to #7

Re: Selection of an AC Motor to Replace the DC Motor

04/01/2014 12:27 PM

I'd agree with a 4 pole motor but 6 kW isn't a standard rating. Assuming it's a 400 volt 50 Hz system as in Europe, I would go for a 5.5 kW motor, star connected at 400 volt. But connect it in delta and set up the inverter to give 230 volt at 50 Hz, and it will deliver 5.5 kW in those conditions. Can then increase the Hz and the volts by √3 times, to 86.6 Hz and 400 volt, giving power √3*5.5 = 9.5 kW, plenty of power, at speed ~ 1450*√3 = 2511 rpm. That's not quite the 2700 rpm required, so Hz has to raised to ~ 93 Hz at constant voltage (and power).

__________________
Give masochists a fair crack of the whip
Register to Reply
Power-User

Join Date: Jan 2008
Location: kuwait
Posts: 132
Good Answers: 2
#8

Re: Selection of an AC Motor to Replace the DC Motor

03/31/2014 3:54 PM

10kw 2 pole is much bigger than your need ,just replace it with 7.5kw -2pole

and a vfd ... initial torque can be set from your vfd parameters .

just a month back i have replaced the 8 dc motors of a cylindrical grinder machine with all ac drives and all are working well on full load................

__________________
love4everyone
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#10

Re: Selection of an AC Motor to Replace the DC Motor

03/31/2014 10:47 PM

Ask the conveyor manufacturer to recommend a suitable ac motor.

__________________
pnaban
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#11

Re: Selection of an AC Motor to Replace the DC Motor

04/01/2014 1:06 AM

Apart from saving one conductor why was this a DC motor to start with?

Is this a repurposed locomotive bogie motor or something?

How are you generating the DC and are there batteries involved here?

More information please.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#12
In reply to #11

Re: Selection of an AC Motor to Replace the DC Motor

04/01/2014 7:32 AM

Dear All;

Thanks for input. The DC motor is connected with a DC drive.

If I select a 7.5KW 4pole 50HZ motor and run it above 50HZ, is their any harm for motor? There are almost 40start/stop per day.

Dear Suhail0110

What was the rating and RPM of old DC motor and the rating and RPM of new AC motors?

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4499
Good Answers: 137
#14
In reply to #12

Re: Selection of an AC Motor to Replace the DC Motor

04/02/2014 9:36 AM

4 pole motor running above 50Hz is no problem, your 2700 rpm is below speed of a 2 pole motor (at 50 Hz).

40 starts per day unlikely to be an issue, unless it's a very high inertia load. In a typical situation 6 starts/hour is OK.

__________________
Give masochists a fair crack of the whip