How to Connect Inverter with RCBO ?

04/16/2014 7:56 AM

I have main connection of 4KW , I wanted to put a RCBO - 32 A ( 30 mA - 2 pole - Siemens) , I also have a inverter of 800VA , which will auto connect to my lighting and some smaller loads i.e loads like refrigerator,Water Pump,AC , Iron , water Heater,Microwave will be excluded from inverter.

My electrician suggested like the RCBO will be put on the mains , and the inverter will be feed into individual MCB's. I felt like this will make the RCBO to trip as there will always a difference of current RCBO will detect.

Please let me know if I am correct . if correct how do I protect my circuit using RCBO , at the same time , I should be able distribute the inverter power to appropriate appliances.A small example will be of immense help to me.

Looking forward to your help

Sujit Roy

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#1

Re: How to Connect Inverter with RCBO ?

04/16/2014 11:14 PM

Sketch please.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: How to Connect Inverter with RCBO ?

04/17/2014 7:12 AM

Follow British Standard 7671.

If there is a difference in current and the RCBO trips on the difference, then there is a fault downstream that requires immediate disconnection and rectification before reconnection as a load.

If the RCBO trips on overcurrent, then there is too much load connected to that particular circuit for the wiring to withstand long-term.

If in doubt, consult a qualified Electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856