Electrical Motor Starter in Star Delta

04/16/2014 8:21 AM

My motor is 30kw, so I want to know how much current takes during starting(star) and normal running condition(delta).

plz also explain........

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: electrical motor starter in star delta

04/16/2014 9:49 AM

Buy one of these:

Read the instructions, that'll explain it.

Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Electrical Motor Starter in Star Delta

04/16/2014 10:26 AM

The current drawn during normal running is dependent upon the load connected to your motor. You can only determine it using the aforementioned high-tech method espoused by member Lyn.

The current during starting (star) will be 33.333333333333333333333333% of what it would be if the motor was started in delta**. That amount is dendent upon the motor design, something you did not divulge. ASSuming it is a Design B motor, typical DOL starting current is 500-600% of the nameplate Full Load Current of the motor, whatever that is. The DURATION of that current is again load dependent.

** except that if it is an open transition star-delta starter scheme, as most are, during the transition from star to delta there is the potential for a brief spike of up to 2000% of the nameplate FLC.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Electrical Motor Starter in Star Delta

04/16/2014 11:27 AM

What voltage?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Associate

Join Date: Apr 2014
Posts: 51
#4

Re: Electrical Motor Starter in Star Delta

04/16/2014 11:49 AM

First go and read about Star-Delta Starter

But for your simplicity i will clear you in Star connection during starting starting current will be 3-4 times rated current and in delta it will take load upto motor rating depending upon load connected at motor end.

For your clarification about Star-Delta Starter you may click link below:-

http://electrialstandards.blogspot.com/2014/04/star-delta-starter-and-applications.html

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Electrical Motor Starter in Star Delta

04/17/2014 7:07 AM

No-one here knows, because no-one except the Original Poster knows either about the mechanical load to which the motor is connected or the voltage of the supply when under load.

So see #1 above.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Participant

Join Date: Mar 2018
Posts: 4
#6

Re: Electrical Motor Starter in Star Delta

03/06/2018 7:04 AM

Most induction motors are begun directly on line(DOL) strters, however when large motors are begun that way, they cause an disturbance of voltage on the supply lines because of substantial starting current surges.

To restrain the starting current surge, large induction motors are begun at decreased voltage and after that have full supply voltage reconnected when they keep running up to close rotated speed.

Reply
Reply to Forum Thread 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

JRaef (1); lyn (1); magnumswitch (1); navdeep_goyal (1); PWSlack (1); Tornado (1)

Previous in Forum: How to Connect Inverter with RCBO ?   Next in Forum: Book Name - Electrical Design

Advertisement