We are facing a major problem , very high frequency Electro Magnetic Noise is being observed in one of the DC Motor, of Rating 450 kW, 1500 RPM, This motor is with Compensating winding.
The Electro Magnetic Noise is observed when the motor is tested on No Load Condition, at rated speed, and on Noise Level Meter the same is read at about 95 to 98 dB(A).
This noise is observed when the Electrical Power is given to the motor, once we disconnect the Electrical Power, the Noise vanishes.
We have taken the Vibration readings of this motor at various locations, Vibration Velocity chnages if the location is changed (we have taken vibration Velocity near to shaft on Right hand side it is 2.2 mm/sec and at Left Hand it is as high as 11 mm/sec. We have also taken the Displacement at these two locations, wherein the Displacement observed to be 2 Microns at noth locations) we feel that this chnage in Vibration Velocity is due to the Noise Frequency.
We have also studied the vibration spectrum of this machine, however, no conclusion can be arrived, as the measurement has not shown any dominant peak through the measurement range.
We are in deep trouble, we have no clue about the generation and resolution of this High Pitch Noise.
Please Help
Re: High Pitch Noise in DC Motor
04/27/2014 6:16 AM
Sorry I can't answer the question, but I lodge an interest in the replies, because a few years ago I investigated the possibility of using a DC electric motor to drive the propeller of my narrowboat, but a couple of demo boats I looked at had motors that gave off a shrill whine that was extremely uncomfortable on the ears.
"...they do that ! ...you'll get used to it !....." was the response.
They couldn't explain it. No thanks! I thought. Although oddly enough, in the confined space of the engine compartment , it was difficult to pinpoint the the exact spot where the noise was coming from.
I appreciate I am only talking of a couple of horsepower compared to your motor but it put me off the idea.
Good Answers: 82
04/27/2014 8:21 AM
This motor has a VFD power drive unit? What's its PWM frequency? What frequency is the noise? Magnetostriction can be a pretty effective acoustic noise generator, and there may be a mechanical resonance involved as well. You said, E-M noise (observed how?), but then mention vibration in the same breath.
Thanks, Win
04/27/2014 10:22 AM
Dear WH,
Yes the Motor is being driven by 6 Pulse DC Drive. We have not measured the Noise Frequency, as do not have any equipment to measure the same.
We feel that this is EM Noise as the Noise practically reduces to ZERO when the Electrical power to the motor is Switched OFF, while Motor Armature is still in motion.
Good Answers: 82
04/27/2014 11:03 AM
A variable-frequency drive (VFD motor-driver's pulse-width modulation (PWM) occurs at a high repetition rate, to simulate a pure low-frequency AC drive power for the motor. A six-phase drive using six half-bridge IGBT switches is common. But the nature of the high-power switching circuits involved can mean the design's PWM frequency is not as high as you might like, e.g. 5kHz or lower. Furthermore, it may have subharmonic components.
The PWM drive waveform creates unwanted high-frequency currents in the coils, which results in high-frequency mechanical forces and core dimension changes due to the magnetostriction effect, and this results in acoustic noise or a loud singing. When you momentarily remove the VFD PWM power, the noise of course disappears. If you do a Google search on VFD drive magnetostriction noise you will find plenty of material.
I am not a motor expert, but I have heard experts talking about this problem. Certain details of a motor's mechanical design. laminations, etc., may make it more susceptible to the problem, but arguably the blame should be rightly placed on the VFD system, with its too-low switching frequency.
My experience has been in the context of designing high-power passive LC filters to attenuate the high-frequency PWM to the coils, and thereby reduce the noise, without any effect on the motor's normal performance. Here are some 2011 CR4 posts on the subject.
My post there includes a schematic (above) and mentions commercial filters, see pic., and gives guidance to find a 41-page filter quide by Danfoss.
Modern VFDs solve or reduce the problem by operating their PWM at higher switching frequencies, like 15 to 25kHz or even higher. These are not only above the audible range, but the inertial mass of the laminations may not respond at these frequencies. Some VFDs may also include internal high-frequency power filters, which are much easier to make at the higher PWM frequencies.
Thanks, Win
04/27/2014 11:29 AM
From the added information we now have, I agree that this is likely a magnetostriction noise problem. I discounted the idea originally because as you point out this happens with an older VFD design that switches in the audible frequency range. An older design and installation would presumably be operational with or without this noise already deemed acceptable. Something changed, I guessed a mechanical or other failure.
Good Answers: 804
04/27/2014 1:34 PM
Lol, the OP keeps telling us it is a DC drive and motor, WH keeps responding about AC VFDs...
Ironically though, WH is on the likely correct path, even though discussing an incorrect mode of transport. The issue is still about what is called the "carrier frequency" in a PWM output. Long ago, DC drives were simpler devices with an SCR based voltage control front end rectifier and filter circuit feeding that variable voltage to the motor. Some time ago, most manufacturers switched to using a PWM DC drive technology wherein the AC line is converted through a passive diode rectifier, then the constant voltage DC bus is controlled via PWM firing of transistors to provide a variable voltage DC output to the motor. PWM DC provides more precise control of motor performance and a smaller cooler drive design. A bigger benefit to the drive mfrs, often not discussed because it means little to the user, is that the design and many of the components used are often interchangeable with AC PWM drives, which reduces the manufacturing costs for those selling both.
In that design change however, the issue of the carrier frequency, basically the clock rate at which the transistors are fired to create the PWM output, is something that DC drive users had not previously experienced. The whine sound is, in a nutshell, the nearly molecular vibrations of the laminations in the stator core due to the pulsations of magnetic force, called "magnetostrictive vibration". You perceive it to increase as load on the motor is decreased, but often that is the result of the fact that there is more OTHER noise that occurrs under load, so the whine represents a greater proportion of the total noise relative to that. But additionally, the carrier frequency inside of your drive may be changing under load because you need better control. When the carrier frequency rises above about 10kHz, even young humans no longer hear it (us older folk stop hearing it at about 5kHz). So as load is decreased and control of it gets easier, the DC drive backs off on the carrier frequency to reduce switching losses, but it makes the whine sound more noticeable.
Good Answers: 82
04/27/2014 2:13 PM
Hah, hah, ha!! Sorry, AC or DC, who's paying attention, not me! That magnetostriction whine completely blocked it out.
Thanks, Win
04/28/2014 8:38 AM
on a piece of equipment we had designed, there where (2) 40 HP Baldor Super 'E' AC motors with a frequency drive.
And the 'whine' that came from them was very uncomfortable. When I asked the elec. engineer about this, I believe he mentioned it had something to do with 'carrier frequency', I believe he mentioned something about it hitting a natural residence frequency. This was (10) years ago.
I never really experience quite as pronounced with over 12 years of designing I thought it had to do with using the efficiency motors.
Good Answers: 42
04/28/2014 11:46 AM
I was aware of SAF playing with this a few years ago, and they were attaempting to use their AC drive to give a DC output on 2 phases, but the new DC drives in the power rating of 450kw DC from Rockwell (Powerflex DC) and ABB (DCS800) I have only seen the traditional rectified 6 or 12 pulse (creating 360HZ or 720Hz "noise").
I have always heard the "carrier" from theses drives, and often have complaints from the vibration folk they can see the carrier on their instruments, even though it is sometimes recorded even with the probe in mid air just beside the motor .
A 'scope picture of the DC supply voltage to the motor would tell a story, possibly identify the driving source and the frequency.
Good Answers: 122
04/28/2014 3:58 PM
Is this a new condition that followed a drive or motor repair or replacement?
If this is a new condition following a drive failure and/or any work performed on the drive I would analyze all components of the drive for compliance with OEM design.
You did not state if the drive is an IGBT or GTO design or SCR or (?) Knowing this is also helpful when giving advice for troubleshooting.
Have you examined the reconstitued waveform with an oscilliscope to identify any/all harmonics present?
We had a similar issue with a drive that we traced to a failed capacitor in the harmonic filter section on the DC bus side of the drive.
It is very important that all OEM specifications are met when replacing any component in a DC or AC drive otherwise transient noise as well as drive and/or motor failure can occur.
04/27/2014 9:25 AM
My initial guess is a bearing in the motor has failed. That is if this is a mechanical and not an electromagnetic noise. Staying in the mechanical noise realm, my next two guesses are a loose rotor lamination or possibly excessive pitting of the commutation contact area. The only way to identify any of these failures are to disassemble the motor. Most people will just replace the motor. The failing motor can then be repaired by a firm with all of the tools and expertise to measure all of the critical dimensions.
A common mechanical problem that can damage the motor bearings is the coupling of motor to mechanical load may not be properly aligned. Again this can only be examined by a qualified person on site examining the machine. If you are very lucky, a misalignment can be corrected before motor damage happens.
I almost forgot, there could also be other mechanical damage that is not in the motor itself.
If the noise is an electromagnetic radiation that interferes with another piece of electronics then either a shielding drain wire or capacitor on the drive circuitry has failed.
04/27/2014 10:26 AM
Dear Redfred,
We have done the Vibration Spectrum Analysis of this motor under free suspended condition as per IEC guidelines. The Vibration spectrum does not show any significant peaks.
The problem with Bearing and Loose Lamination should have got recorded in the Vibration Spectrum. We have checked the commutator as well, but it is very clean ( No Pitting)
Thanks..
04/28/2014 1:38 PM
You have the equipment for vibration spectrum analysis, but you don't have a microphone to plug into the spectrum analyzer?
Hunh?
common knowledge...less common than common sense
Good Answers: 444
04/27/2014 10:04 AM
How about a frequency spectrum for the noise; what is its shape, are there any notable peaks, how does it roll-off, does voltage, current, or load, affect the pitch and/or shape? Next we need some design details of the motor; number of poles, slots, winding pitch for both stator and rotor, number of commutator faces, how connected, number of brush groups, angles, etc. Another thing, what is your DC source; DC generator, AC line rectification, active electronics AC/DC converter, etc.? What type of bearings, floating, fixed, roller, ball, tapered, sleeve, etc?
The fact that the noise diminishes when unpowered does not rule out bearing noise, it's possible that the bearings are being affected when the magnetic forces affect the centerline of the shaft. Before you tear the machine down for inspection I would run it at various combinations of load and speed (if it is a variable speed motor) and see how/if the noise spectrum changes, same thing for powered, unpowered. You've got to rule out as many variables as possible, and don't be surprised if the noise magically disappears after you inspect and reassemble the motor.
04/27/2014 10:31 AM
Dear RaMConsult,
We have arranged for recording the Noise Spectrum, shall come back with the details.
Today we have taken one more trial, we were feeling that the Noise is because of the Compensating winding design, so we have disconnected the Interpole and Compensating winding of this motor and run the motor at No Load 1500 RPM (Rated PRM), surprisingly the Noise did not disappear..
Does this gives any clue..
Thanks..
Good Answers: 88
04/27/2014 11:10 AM
If the noise is within audio spectrum, you don't really need expensive equipment to diagnose, you already have a PC, get a mic, record the noise and spectrum analyze it with a free software tool like audacity, you can even do it real time with a directional mic. If it's because of the drive switching frequency and you MUST get it under control, you can use a sutable DC reactor in series. But with the limited provided data, I believe it's just the drive complaining for the no-load condition. S.M.
04/28/2014 1:36 PM
As it happens, I deal with the noise in a small Maxon motor, noise generated by some unbalance. I intended to perform a Fourier analysis and, because some 15 years ago I used a TI eval board for one of their DSP chips, performing Fourier, I was ready to buy one. Well, you mentioned FREE spectrum analyzers over the internet, and that's exactly what I am going to do. Thank you for opening my eyes.
Bridge rule #1: Nobody is as good as he thinks about himself nor as dumb, as his partner thinks...
Good Answers: 137
04/27/2014 12:52 PM
I suppose this is a new installation? I.e. it hasn't operated OK in the past but the noise has just started?
04/27/2014 2:15 PM
If you have a smart phone, there is an free app called "Audalyzer" that will let you get a good estimate of the frequency. There's also an Iphone/Ipad app called SpectrumView (also free) that might help.
Just another thought: Is it possible it is a bearing noise and the bearing is being loaded when power is applied to the motor?
Have you tried using a stethescope (or a screwdriver held up to the ear) to try to localize the sound?
04/27/2014 2:45 PM
As a PS to my first post 1, the power supply was 48 volts from 4 x 12 vdc batteries connected in series. I do not know what form of speed control was used.
Good Answers: 804
04/27/2014 5:13 PM
Regarding all of the tangential ideas about this being bearing noise, I submit this from the original post:
"This noise is observed when the Electrical Power is given to the motor, once we disconnect the Electrical Power, the Noise vanishes."
That would NOT be the case if the noise was, in any way, attributable to anything mechanical, which would be inclusive of bearing noise. So the spectrum analysis might be interesting, but not likely relevant.
Good Answers: 444
04/27/2014 10:59 PM
I considered that but there are subtle mechanical changes that can take place when any motor is energized/de-energized. In particular the centering of the rotor both vertically and horizontally can be affected by the magnetic field. Depending upon the temperature of rotor and the skill of the aligner during its mechanical alignment, it's possible for the journals to shift slightly and contact the bearings differently and cause a bearing whine. The noise from the misalignment might be what's being heard; it may seem like a stretch for the uninitiated but I've heard it in large DC exciters. It's one of the reasons why a spectrum analyzer will help pinpoint the cause of the noise.
From another site where you also post:
"...The magnetic center is the driving parameter for alignment and coupling. Failure to consider magnetic center results in axial loads in places they should not be..." As we know misaligned bearings can manifest themselves by being noisy, de-energizing the motor shifts the alignment ever so slightly and the noise ceases.
04/28/2014 8:23 AM
Reading through these posts, the OP still hasn't answered the question, that being 'is this 450kw motor being driven by pure dc or dc fed to a variable frequency drive feeding the motor.' Which is it, as this would help explain the source of the noise.
04/28/2014 3:30 PM
Don't know how I missed it, (hadn't had my coffee yet I suspect) but the OP did state 6 pulse dc and wondering if this was a common type, looked it up and sure enough high order harmonics are a common problem on these drives.
http://ecmweb.com/power-quality/six-pulse-conversion-and-harmonics