SCADA CPU Recommendation

05/05/2014 2:27 AM

Gentlemen,

In our rendering plant the environment is very stick, which effect the control room also. The SCADA client CPUs in that area having too much issue with power supplies, Hard disks and mother Board.

Can you Please suggest me some PC which can sustain in tough environment also.

__________________
All the problems of the world could be settled easily if men were only willing to think. The trouble is that men very often resort to all sorts of devices in order not to think, because thinking is such hard work.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#1

Re: SCADA CPU Recommendation

05/05/2014 4:01 AM

You should be looking for "industrial computer".

Quote your specific environment to the Vendors (Siemens comes up in the search) and get some quotes!

Good luck!

__________________
Common Sense Dictates
Register to Reply
Active Contributor

Join Date: Oct 2013
Location: Down street Space ship 4, Desertech,
Posts: 12
#7
In reply to #1

Re: SCADA CPU Recommendation

05/06/2014 12:57 AM

I have checked the Siemens Idustrial PC, Its No doubt a better option. Thanx

__________________
All the problems of the world could be settled easily if men were only willing to think. The trouble is that men very often resort to all sorts of devices in order not to think, because thinking is such hard work.
Register to Reply
Commentator

Join Date: Apr 2011
Location: KCM, chingola; copperbelt; zambia; southern africa.
Posts: 75
#2

Re: SCADA CPU Recommendation

05/05/2014 6:52 AM

industrial PC is the only way, or go to the manufactures with your complaints

__________________
an error does'nt become a mistake if corrected!
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#3

Re: SCADA CPU Recommendation

05/05/2014 7:36 AM

Place all but the mouse and the keyboard in a cabinet that has a gasket sealing the door on it. Pressurize it with 10-15 inches of H2O with clean fresh air with a source from outside the "sticky" area. Put a switch or valve controlling an annunciator on so that it activates an annunciator when the door is opened. When the mouse or keyboard are no longer useable toss it and replace it with another inexpensive replacement.

Monitor can also be accommodated in the cabinet if there is a glass or Plexiglas window in the door or a side of the cabinet. Another possibility would to put a very clear plastic bag over the monitor and tie is around the base or mountings of it.

This is a time proven method of enclosing instrumentation in dusty, high humidity, some XP areas and other environments detrimental to the operation of computers or other equipment.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#4

Re: SCADA CPU Recommendation

05/05/2014 9:44 AM

First you need to clean up the environment in the control room. Otherwise you are going to continue to replace computers.

Industrial computers, and sealed cabinets will help extend the time between replacements, but that doesn't address the root cause: Poor environmental controls.

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Register to Reply
Power-User

Join Date: Jul 2010
Posts: 136
Good Answers: 19
#5

Re: SCADA CPU Recommendation

05/05/2014 2:46 PM

I had just tossed this email away, but retrieved the URL - it's a soft sales pitch for Siemens industrial PCs.

http://www.totallyintegratedautomation.com/2014/05/industrial-pcs-true-meaning-industrial/

The others' comments on cleaning up the environment on spot on. One doesn't do commercial food preparation in the back of garbage truck.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: SCADA CPU Recommendation

05/05/2014 8:37 PM

I also highly suggest using solid state drives instead of hard disk drives (rotating media).

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Bud (1); DmanEng (1); IdeaSmith (1); JRaef (1); Kilowatt0 (1); old salt (1); tehseen (1)

Previous in Forum: Stablize an Unstable System with Open-loop Controller   Next in Forum: Shock From Solar Panel Cable

Advertisement