Tripping by Neutral Displacement Relay

05/10/2014 5:58 AM

IN OUR POWER PLANT WE HAVE TRIPPING OF LV SIDE BRKS. FOR OUR 50 MVA, 220kV/6.9 kv STATION TRANSFORMERS BY THE ACTION OF NEUTRAL DISPLACEMENT RELAYS.

BUT FOR OUR 15 MVA, 15.75kV/6.9 kV UNIT AUXILLIARY TRANSFORMERS, TRIPPING OF LV BRKS or GENERATOR BRK IS NOT PROVIDED FOR ACTION OF NEUTRAL DISPLACEMENT RELAY AND ONLY ANNUCIATION IS PROVIDED.

WHY IS THIS

PL. REPLY

Register to Reply
Pathfinder Tags: clarifications/doubts
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: TRIPPING BY NEUTRAL DISPLACEMENT RELAY

05/10/2014 11:31 AM

This is happening because your power plant employs people that prefer to SHOUT IN PANIC instead of following proper troubleshooting protocol.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Active Contributor

Join Date: Mar 2014
Posts: 19
#2

Re: TRIPPING BY NEUTRAL DISPLACEMENT RELAY

05/10/2014 1:20 PM

friend,

be reasonable in reply and donot act too smart..

Register to Reply
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3
In reply to #2

Re: TRIPPING BY NEUTRAL DISPLACEMENT RELAY

05/10/2014 2:37 PM

The relays that are tripping protect your hardware from catastrophic damage. Proper troubleshooting will first identify the type of fault that makes this relay to trip. Next a good troubleshooter will be determine if that fault condition actually exists or if the relay is triggered by a false fault. The troubleshooter will respond accordingly.

The last thing one should do is to shout at a public forum that you do not understand how to do your job. What you really do not grasp is if you showed any comprehension of your circumstance by saying what testing you've done or even what settings your relay were at when they tripped then people here will help.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Active Contributor

Join Date: Mar 2014
Posts: 19
#7
In reply to #3

Re: TRIPPING BY NEUTRAL DISPLACEMENT RELAY

05/12/2014 2:00 AM

sir,

thank you for valuable comments

Register to Reply
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: TRIPPING BY NEUTRAL DISPLACEMENT RELAY

05/10/2014 2:53 PM

Although you have not provided the vector group for each transformer I suspect that the secondary of the unit auxilliary transformer is delta connected. If so then it was done like that to ensure continued operation in the event of the first ground fault; that's why you only get an annunciation. However if you ignore the alarm the second fault will provide some really big clues as to its location.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 3)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: TRIPPING BY NEUTRAL DISPLACEMENT RELAY

05/10/2014 4:25 PM

If that happens, please send us a video so that lyn can update his arc flash example.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#6
In reply to #5

Re: TRIPPING BY NEUTRAL DISPLACEMENT RELAY

05/10/2014 5:03 PM

Here is a surveillance video. It looks like they were manually racking out a breaker that "looked" open but wasn't.

Here's a collection especially for those posters who think we cry "wolf" too often.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ANANDANRCR (2); RAMConsult (2); redfred (2); Tornado (1)