Anonymous Poster #1

Soft Starter Issue

05/10/2014 3:42 AM

Hi

We are experiencing a problem in starting the pumps using soft starter. Our pump capacity is 55kW(Sewage application) with rated current 94A and full load current current of 945A at 415V. the soft starter selected was ATS48C11Y from Scheider, based on the type 2 coordination parameters.

when attempting to start the pump for the first time, all the fuses protecting the soft starter has blown. then the panel builder bypassed the fuse and attempted to start the motor, but failed as the motor was not achieving the full speed and the soft starter is not switching to the bypass mode.

on physical verification of the parameters it is observed that the motor is drawing 400A constantly and thus tripping the feeder.

Any possible solutions to overcome this issue

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Soft Starter issue

05/10/2014 4:39 AM

Find the metal object that is stuck in the pump and fish it out of there.

Some of your numbers don't seem consistent.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Score 1 for Off Topic
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#2

Re: Soft Starter issue

05/10/2014 8:38 AM

test the motor without a load....

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Soft Starter issue

05/10/2014 11:36 AM

Do you have any idea how much torque you need to start moving the pump shaft?

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Member

Join Date: Jul 2013
Posts: 8
#7
In reply to #3

Re: Soft Starter issue

05/11/2014 1:45 AM

1803 Nm, moment of inertia 1.83kg m2

Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Soft Starter issue

05/10/2014 11:42 AM

I have to assume that you made a typographical error on the 945A figure. That number would not be correct even for Locked Rotor Amps.

Soft starters are not magic, they reduce current, but they also reduce TORQUE as a result. If you have the soft starter set for Current Limit starting, the starter artificially limits the current which limits the torque and if that value is less than what the load acceleration curve requires, you never finish the task of accelerating and run into a thermal limit on something, either the Over Load setting or the soft starter, or the protective device ahead of it. In your case, by bypassing the fuse (REALLY bad idea), you proved this to be the case, as well as proved that your motor overload settings in the soft starter are likely wrong.

The reason why the bypass contactor does not come on is because the soft starter has an algorithm designed to maintain the current limit. So it monitors the current and needs to see it drop on its own to recognize that the motor accelerated. If it never drops (because the torque is insufficient to allow it to accelerate), it keeps limiting the current until it does or something takes it off line.

400A on a motor rated for 94A is representing a Current Limit setting of 425%. In most cases that SHOULD accelerate a centrifugal pump, but not knowing any details on your pump, I cannot say with any certainty if that is valid.

But for sure if something is jamming the pump, that would explain the lack of acceleration. I would start there and eliminate that possibility.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 3)
Member

Join Date: Jul 2013
Posts: 8
#8
In reply to #4

Re: Soft Starter issue

05/11/2014 2:12 AM

Dear JRaef

Thanks for the response.

The starting parameters mentioned in the motor performance data sheet is as follows

Starting current 914 A

starting torque 1803 Nm

Moment of inertia 1.83kg m2

Rated power 55kW

Nominal speed 990rpm

Number of poles 6

Rated voltage 415V

Pump Datas

Density 1kg/dm3

viscosity 1.57 mm2/s

rated speed 990rpm

flow 96.3l/s

head 26.7

rated power 34.8kW

frequency 50 Hz

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#10
In reply to #8

Re: Soft Starter issue

05/11/2014 8:49 AM

If the starting torque of this motor and the actual required torque to get the pump to start turning are as you stated both 1803 Nm then this is your problem. Your motor is under sized for this mechanical load. The slight bit of over design by the motor manufacturer is the only thing that is getting this to move at all. You are getting precisely the results of an undersized motor for the mechanical load. I suspect that somebody mistook the pump's starting load for a motor recommendation specification, or that you are quoting the same number in this and your earlier reply to me.

I would prefer your motor starting torque to be at least twice the starting torque of the load (pump). I've seen smaller margins when static friction was anticipated to be significantly greater than rolling friction. I do not expect static friction with a pump of any type.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11
In reply to #10

Re: Soft Starter issue

05/11/2014 11:50 AM

I think those are the motor capability values, not the pump torque requirements. It's hard to see those charts, but this appears to be a true centrifugal pump that will have a very low starting torque requirement. It requires 34.7kW and is connected to a 55kW motor, driven by a soft starter at 425% current limit. That motor SHOULD have accelerated with no problem whatsoever. So this is back to something blocking the pump impeller or a defective bearing, in other words a mechanical issue.

The only electrical possibities are a defective soft starter, for example a shorted SCR, or you connected the motor in Delta when it was supposed to be connected in Star. But if it were a shorted SCR, I would be surprised that the soft starter did not indicate that on the display. If you misconnected the motor, the torque capability is reduced by 2/3, so when you also reduce it via the soft starter, it immediately stalls and because the soft starter is artificially limiting current, it stays that way until the fuse blows.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#12
In reply to #11

Re: Soft Starter issue

05/11/2014 1:01 PM

Agreed. My bet is on a bearing failure, with the supposition that this did at one time work properly. My second bet is that the impeller of this sewage pump is clogged with some semi-solid muck. A torque measurement or at least a wrench assisted hand feeling of the pump shaft load will help to identify this. Come to think of it, there is also the possibility that a down stream obstruction (collapsed valve, clogged screen) could be happening. A pressure reading would help sort out this possible problem.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#14
In reply to #12

Re: Soft Starter issue

05/12/2014 10:11 AM

Good point by Redfred. If the pump WAS working and no longer accelerates, then it is surely a mechanical issue such as a blockage or bearing. Only if this is the INITIAL commisioning start up can my other possibilities can enter into it.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Member

Join Date: Jul 2013
Posts: 8
#9
In reply to #4

Re: Soft Starter issue

05/11/2014 2:14 AM

data sheets

Reply
Active Contributor

Join Date: May 2014
Posts: 14
#5

Re: Soft Starter Issue

05/10/2014 9:02 PM

Before supplying the power for pump, did you remove the coupling of the pump? We always should run no load before power for the device. Or you can use a small motor for testing all function of the softstarter. After that you use it with your motor.

Reply Score 1 for Good Answer
Associate

Join Date: Apr 2014
Posts: 51
#6

Re: Soft Starter Issue

05/11/2014 12:55 AM

I have all soft-Starters for compressor applications i will tell you settings just do them and you will get started motor easily:-

Set current limiting value at 250% and use fuse rating of 150A then you will start that motor very easily

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13

Re: Soft Starter Issue

05/12/2014 4:32 AM

Do remember that the fuses are there to protect the wiring, not the motor. The motor should be protected with an overload trip device in the starter circuit.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Commentator

Join Date: Apr 2011
Location: KCM, chingola; copperbelt; zambia; southern africa.
Posts: 75
#15

Re: Soft Starter Issue

05/13/2014 3:31 AM

check your motor there should be some restriction of some kind and make sure your starter can stand full load. i had a similar problem, but in my case it was the drives and they where blowing. lost six of them.

__________________
an error does'nt become a mistake if corrected!
Reply
Member

Join Date: Jul 2013
Posts: 8
#16

Re: Soft Starter Issue

05/15/2014 4:38 AM

Hi All

thanks for the interest in my query and the replies. The problem is now solved and the pump is running. we are still not clear about the trouble. we assume that it could be a mis-programming or setting in the soft starter. the panel manufacturer has yet to confirm this. just to get themselves saved from the blame the panel builders allegation was that the motor winding was not getting the full voltage and it is due to the bad quality of terminal lug used for terminating the cable(By the way we are not accepting this allegation, and love to believe that it is a soft starter setting issue)

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#17
In reply to #16

Re: Soft Starter Issue

05/15/2014 3:17 PM

I can imagine that if the "bad lug" was exhibiting so much resistance so as to cause the current to increase to 400A on something designed for around 100A, and stay there until the fuse blew, the terminal would have melted.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Reply to Forum Thread 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: