Temperature Rise Test on Panels with VFD Feeders

05/20/2014 12:55 AM

Hi,

I am designing VFD feeders inside panels. There are many heat loss producing components like VFD, choke, contactors etc. Is there any way to conduct a temperature rise test by passing actual current through VFD at power frequency of 50Hz, like we do for busbars and other circuits, besides the conventional method of adding heat loss resistors.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Temperature rise test on Panels with VFD feeders

05/20/2014 12:58 AM

Search: IR thermometer.

Register to Reply
Active Contributor

Join Date: May 2012
Posts: 20
#2
In reply to #1

Re: Temperature rise test on Panels with VFD feeders

05/20/2014 1:02 AM

I want to conduct a test in the first place. Measurement is to be done through thermocouples. I want to know is there a way to run the VFD with the acutal load.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #2

Re: Temperature rise test on Panels with VFD feeders

05/20/2014 1:14 AM

And what, exactly, are your technical qualifications for this????????????????

I'm skeptical that you can do this, at all.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#5
In reply to #2

Re: Temperature rise test on Panels with VFD feeders

05/20/2014 1:31 AM

Sure there is! Connect the load and run it!

Or did you mean to run with a load that actually is not a load?

Then see here!

__________________
Common Sense Dictates
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6
In reply to #5

Re: Temperature rise test on Panels with VFD feeders

05/20/2014 10:13 AM

Love the loop back...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Temperature rise test on Panels with VFD feeders

05/20/2014 1:10 AM

Hook up a load bank.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Temperature Rise Test on Panels with VFD Feeders

05/20/2014 10:19 AM

Your worst case for producing heat in the cabinet will be with the VFD set for maximum operating frequency at maximum rated load at maximum allowable carrier frequency where your losses in the entire circuit are greatest, so yes, you MUST conduct a load test. If you cannot do that with a dynamometer, you must simulate it with a load bank.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User
Engineering Fields - Petroleum Engineering - Rig Electrician United States - Member - the Oil Patch Engineering Fields - Power Engineering - Drives & Gen's Engineering Fields - Instrumentation Engineering - Drive Control Popular Science - Cosmology -

Join Date: Jan 2010
Location: Houston off/on-shore @ Oil Patch
Posts: 223
Good Answers: 2
#10
In reply to #7

Re: Temperature Rise Test on Panels with VFD Feeders

05/20/2014 12:54 PM

I once mistakenly programmed a closed loop VFD for a 1024 ppr Encoder but it was really a 1200 ppr Encoder on the motor. The motor was free and when they cracked the throttle it went to 150% amps turning slowly. What does the lumberjack [JRaef] think of fooling with the parameters to load the VFD.

__________________
Why do they make manhole covers round? so they won't fall in [before asking "Who is John Galt?"]
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#12
In reply to #10

Re: Temperature Rise Test on Panels with VFD Feeders

05/20/2014 5:37 PM

I once mistakenly programmed a closed loop VFD for a 1024 ppr Encoder but it was really a 1200 ppr Encoder on the motor. The motor was free and when they cracked the throttle it went to 150% amps turning slowly. What does the lumberjack [JRaef] think of fooling with the parameters to load the VFD.

Hmmm... interesting idea, never thought of that. Over fluxing the motor as a way to increase the current out of the drive without actually requiring the motor to have a load connected to it, by essentially turning the motor into a heater. We do a similar thing for STOPPING a motor, called Flux Braking. I think it could be adapted. You couldn't do it for long though, the motor wouldn't take it.

Oh, unless you use a motor much larger than the VFD capacity, and TELL the drive it is smaller so it's easier to over flux it!

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#14
In reply to #12

Re: Temperature Rise Test on Panels with VFD Feeders

05/20/2014 5:43 PM

Probably not a good idea in this case when trying to calculate temperature rises as these tests can take a while.

__________________
jack of all trades
Register to Reply
Associate

Join Date: Apr 2014
Posts: 51
#8

Re: Temperature Rise Test on Panels with VFD Feeders

05/20/2014 10:31 AM

You can put full load on VFD and test the same by temperature

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #8

Re: Temperature Rise Test on Panels with VFD Feeders

05/20/2014 11:00 AM

Using what?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#11

Re: Temperature Rise Test on Panels with VFD Feeders

05/20/2014 3:41 PM

We have never bothered because the heat loss figures were clearly indicated in the VFD manuals and the heat loss of other simple resistive and inductive devices could be calculated or estimated using ohms law (etc).

If you really wanted to perform the test you could connect a resistive or motor load to the VFD. You may be able to hire one if making one is going to be too expensive.

Perhaps you should check the manual or VFD application notes again.

__________________
jack of all trades
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#13
In reply to #11

Re: Temperature Rise Test on Panels with VFD Feeders

05/20/2014 5:40 PM

We have never bothered because the heat loss figures were clearly indicated in the VFD manuals and the heat loss of other simple resistive and inductive devices could be calculated or estimated using ohms law (etc).

If you were needing to get a UL listing on an enclosed version of a VFD that is not already offered in a listed enclosed version, or for example to put it in an MCC cabinet and get a UL845 listing, UL would not accept calculated values, you must do a physical test. I would use the calculated values to know what to use IN that physical test so as to only do it once, but the actual test must be performed.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Active Contributor

Join Date: May 2012
Posts: 20
#15
In reply to #13

Re: Temperature Rise Test on Panels with VFD Feeders

05/21/2014 1:13 PM

Thanks for your really interesting inputs. I just wanted to know further, that what if I keep dummy equipments of same volume as that of the VFDs chokes filters MCCB fuse etc inside an MCC panel and keep some equivalent heater loads (Watt loss that specified in manufacturers catalog) inside these dummy equipment and then check for surrounding ambient which I want to be around 50 deg celcius or less. Will it give me the same results and if not what is the real difference between passing actual current or creating a heat loss through small heater.

Also what can be an ideal way of heat dissipation. Whether an inbuilt VFD fan suffices or external fans are needed. Above 22kW VFD feeders generally produce lot of heat. At present I am thinking of providing air inlet through indivdual feeder compartment and taking it out through the cable chamber at the side by giving a fan on top. Any ideas on ventilation shall be highly appreciated.

Register to Reply