Thermocouple Cable

06/06/2014 4:47 AM

CAN WE USED K TYPE COMPENSAING CABLE FOR S TYPE THERMOCOUPLE?

Register to Reply
Pathfinder Tags: thermocouple cable
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: THERMOCOUPLE CABLE

06/06/2014 5:31 AM

Depends whether or not you want to read the correct temperature.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Score 1 for Good Answer
Participant

Join Date: Jun 2014
Posts: 3
#2
In reply to #1

Re: THERMOCOUPLE CABLE

06/06/2014 6:40 AM

What will be the temperature difference in case or can I calculate permanent error in such case & feed the same value in transmitter for compensating.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#4
In reply to #2

Re: THERMOCOUPLE CABLE

06/06/2014 6:42 AM

Why don't you just use the right cable and be done with it?

__________________
Good moaning!
Register to Reply
2
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#5
In reply to #2

Re: THERMOCOUPLE CABLE

06/06/2014 6:45 AM

You can't just calculate a number & apply it as a correction factor - it depends on the temperatures of all the junctions between dissimilar metals.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Good Answer (Score 2)
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#3

Re: THERMOCOUPLE CABLE

06/06/2014 6:40 AM

It also depends on whether we have got any to use and the bit that we have got is long enough.

__________________
Good moaning!
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6

Re: THERMOCOUPLE CABLE

06/06/2014 7:10 AM

No.

Register to Reply Score 1 for Good Answer
3
Guru

Join Date: Apr 2014
Posts: 1869
Good Answers: 67
#7

Re: THERMOCOUPLE CABLE

06/06/2014 8:48 AM

No. It is called a 'K-type compensating cable' for a reason. Were it to work with S-type thermocouples, why then would they call it a 'K-type compensating cable.' The name is a clue as to its intended purpose.

But! If you decide to use it anyway, you can save yourself some money and use doorbell wire instead. It's much cheaper whilst also giving you incorrect readings.

Register to Reply Good Answer (Score 3)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8

Re: Thermocouple Cable

06/07/2014 12:23 PM

Does the processor have the ability to embed a lookup table? (Which would then need to be created.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
2
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#9

Re: Thermocouple Cable

06/07/2014 5:51 PM

Type R or S thermocouple extension wire consists of a copper wire and a copper alloy wire since it would be prohibitively expensive to use platinum for extension wires.

The extension wire is actually compensating cable, designed to have the same EMF gradient characteristic at (relatively) low temperatures as either an R or S thermocouple.

The positive leg is pure copper and the negative leg is alloy #11, primarily copper, 97% copper with a balance of 3% Ni/Mn. It is a relatively inexpensive wire and can be used in environments up to approximately 204ºC.

In the absence of the correct Type S compensating wire, there is no means of determining the error created by the junction of K wire and the S thermocouple, so there's nothing to 'look-up' and correct for.

Register to Reply Good Answer (Score 2)
Guru
United States - Member - Charter Member Engineering Fields - Instrumentation Engineering - Charter Member

Join Date: Mar 2008
Location: The People's Republic of Massachusetts
Posts: 1946
Good Answers: 73
#10
In reply to #9

Re: Thermocouple Cable

06/09/2014 11:51 PM

Well put Iris, GA

__________________
I go into every human encounter expecting to be framed for a crime I didn't commit. Dilbert, 2013
Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#11
In reply to #9

Re: Thermocouple Cable

06/10/2014 12:14 AM

Regardless of what the cumulative sum of junctions is, one could measure actual temperatures versus recorded temperatures, and create a lookup table. In many cases, a simple offset would probably adjust adequately for temperatures in the range of interest, such as near a setpoint.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Jun 2014
Posts: 3
#12
In reply to #9

Re: Thermocouple Cable

06/10/2014 12:46 AM

Thanks Iris for detailed explanation.

Now the mistake had happened in the past & I have to resolve for which simply I have to go for the option of buying new s type cable.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #12

Re: Thermocouple Cable

06/12/2014 11:19 AM

Go away and spend the money, then.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Bricktop (1); Crabtree (2); europium mkII (1); Iris (1); JohnDG (2); luck_shubh (2); lyn (1); PWSlack (1); Tornado (2)