Selection of an Engine Driven Pump for Chilled water Application

06/18/2014 12:44 AM

We have a requirement to pump chilled water from a district cooling plant-24X7 with Electric motors. However, black-out situation demands an Engine driven pump. The existing specifications of pump is 467 liters/second and 50 Meter Head, 1160 RPM (present motor is 300kW,480V,60 HZ). Can anyone suggest the engine-sizing, availaibality and specific controls while selecting the engine. My Best Regards. Govindaraj

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Selection of an Engine Driven Pump for Chilled water Application

06/18/2014 1:09 AM
Register to Reply Good Answer (Score 2)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Selection of an Engine Driven Pump for Chilled water Application

06/18/2014 1:49 AM

An engine for 300kW @ 1160 rpm, with a governor, shouldn't be hard to find. The pump coupled to it would be the same as existing.

Alternatives are possible at 1800 rpm, or even higher, and would probably be more economical.

Why is the head so high?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#3

Re: Selection of an Engine Driven Pump for Chilled water Application

06/18/2014 7:08 AM

Several questions need to be considered.

Is the electric pump existing or just the spec? Is the spec mandatory? Higher speed might be more economical (though it's a fairly hefty pump).

Is the engine driven pump in addition (standby) to the electric pump or instead of? If instead of you could choose a pump at higher speed, which would likely be more economical for pump and engine. Need to discuss with both suppliers to optimise. If pump is in addition same thing applies, unless there is a requirement for identical pumps. If the 1160 RPM is mandatory higher engine speed with V-drive (or gearbox etc) might be the way to go.

How is the electric pump controlled? Does it run at fixed speed, with flow control (if any) via throttling valves, or variable speed? If fixed speed you could just start the engine and raise the speed till flow is right, and leave the speed control there. There might be some variation in speed as the system throttling varies, causing change in absorbed power, but likely to be minimal.

If the electric pump is variable speed it depends on what basis, and you need to consider how the speed control signal is input to the engine controls.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Selection of an Engine Driven Pump for Chilled water Application

06/18/2014 11:04 AM

If the engine drive pump idea is for backup it the power fails, why not just get a back up Deisel generator that can run the existing electric motor for the pump?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Marine Engineering - New Member

Join Date: Sep 2008
Location: Vancleave, Ms about 30 miles inland from Biloxi and the coast
Posts: 3197
Good Answers: 106
#5

Re: Selection of an Engine Driven Pump for Chilled water Application

06/18/2014 3:26 PM

Use a clutch and coupling from the engine to the electric pump. You would be using only one pump with two means of driving it. If you use a second pump, you will have to provide additional valves and piping, adding up to higher cost.

__________________
Mr.Ron from South Ms.
Register to Reply
Active Contributor

Join Date: May 2011
Posts: 23
Good Answers: 2
#6

Re: Selection of an Engine Driven Pump for Chilled water Application

06/18/2014 11:11 PM

Hi srgovind,

IF you must use a engine driven pump, Look at a fire pump --Clark is one US brand I am familiar with--they are auto start on loss of pressure and could be readily coupled in to a system-- or as someone said use a back up genset and transfer switch with which would also keep your BOP running.

Register to Reply
Participant

Join Date: Jan 2014
Posts: 2
#7

Re: Selection of an Engine Driven Pump for Chilled water Application

06/19/2014 12:44 AM

I would suggest you size the generator not only for your pump but also for your other electrical loads such as lighting, air conditioning, and other significant loads. It would be very hard to do maintenance and trouble shooting when there is a power failure. You also need to install Automatic Transfer Switch. You use the same pump and motor without providing additional piping.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8

Re: Selection of an Engine Driven Pump for Chilled water Application

06/19/2014 12:48 AM

How do you run the chillers during a blackout? The pump is small potatoes.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster #1
#10
In reply to #8

Re: Selection of an Engine Driven Pump for Chilled water Application

07/09/2014 9:50 AM

Point is right. The black-out condition demand circulation of secondary chilled water through 15 kM reticulation pipe lines from a large Thermal Energy Storage-Chilled ater tank, till power is restored. Hence thsibeing critical, we are proposing an engine driven pump also, along with one Electric-generator pump-(in the event of generator failure).

Register to Reply Off Topic (Score 5)
Active Contributor

Join Date: Jun 2014
Posts: 15
#9

Re: Selection of an Engine Driven Pump for Chilled water Application

06/22/2014 11:57 PM

Thank you all for reply concerning the case of engine driven chilled water pump which is critical to any District Cooling Plant to keep circulating Chilled water from thermal storage tank even if chillers trip out. Suggestions like website information, Clutch-motor-engine type, fire-application pumps, variable speed application, Use of Generator on Black-out instead of engine pump etc.

Register to Reply Score 1 for Good Answer
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Codemaster (1); Cris1025 (1); EXPAT07 (1); JRaef (1); lyn (1); ronseto (1); srgovind (1); Tornado (2)