Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/06/2014 12:17 PM

I would like to know genius advice on the usage of 415VAc 50 hz cable and 415vac 60 hz cable can be laid on a same cable tray. If so please provide relevant standard reference.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/06/2014 1:00 PM

NFPA-70e or BS 7161

You'll need your own copy.

Local codes may apply.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/06/2014 1:27 PM

Not enough information has been provided. You asked about the cable, the answer depends upon the nature of the systems those cables are connected to.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/06/2014 3:23 PM

Can this be done without any serious problem, yes it can. Can this produce a problem with one circuit or with inductive heating of the cable tray, yes this can produce a problem. Can you figure out which answer fits your situation, yes you can. I have faith in you.

Now that you have your "yes man" answers, go do your homework.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/06/2014 5:55 PM

How is it that you have two different line frequencies in the same facility?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#11
In reply to #4

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/06/2014 8:21 PM

He did not say that. Only that the cable is 50 or 60 hz.

You can lay them together but if you can operate them is the other question.

Also could you operate a 60 Hz cable with 50 Hz?

But that was not the question.

I am lost with this stuff anyway. Have fun!

__________________
Common Sense Dictates
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#16
In reply to #11

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/07/2014 1:59 AM

There is no such thing as 50Hz cable or 60Hz cable. Cable does not care whether is it 50Hz, 60Hz, 133-1/3Hz, or 0Hz (DC). So the only time you might be needing to consider this issue is if, for some really oddball reason, you had both a 50Hz supply source and a 60Hz supply source in the exact same place in order for them to be in the same tray. That's why I thought the conversation needed to start there, because it is far far more likely that this entire thread is a joke or demnstrative of having been started by someone who is so incompetent as to not being qualified to take the any further without local expert help anyway.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#21
In reply to #16

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/07/2014 11:40 PM

I was pretty sure there was not difference in the cable.

Still interested where and why there would be two different systems.

__________________
Common Sense Dictates
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#23
In reply to #21

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/08/2014 8:55 AM

How about a company that fabricates transformers for anywhere in the world. What about an international electric power equipment testing facility. You're only thinking of the final consumer.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#32
In reply to #23

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/26/2014 10:40 PM

You wrong on this one! I am not thinking at all! I am asking what it could be because even so you might be right you are still guessing.

For a testing facility they could just test seperately and would even use the same cable. What do we know?

And then you would expect and international electric power test company to know their stuff and not asking this here.

I keep running my stuff on 100Hz and dont worry about it!

__________________
Common Sense Dictates
Register to Reply
Anonymous Poster #1
#25
In reply to #16

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/12/2014 6:49 AM

Does frequency relate to the impedance and skin effect !!!!

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#26
In reply to #25

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/12/2014 8:15 AM

No, they're no relation at all. Not even distant cousins. Their offspring would be sterile like a mule. The conjugation would die at one generation. In fact neither are capable of any kind of procreation....

Oh, you mean the other meaning of relation, like correlation. Yes they correlate and influence each other.

They don't have feelings for each other.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Anonymous Poster #1
#30
In reply to #26

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/12/2014 11:13 AM

Hey my Uncle....They are relatives. Go back to the books

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#31
In reply to #30

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/12/2014 12:35 PM

Book'em Danno!

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/06/2014 6:14 PM

The OP hasn't learned much since this, "three phase transformer of capacity 3600 KVA,output voltage of 433vac,Rated current secondary : 4833 Amps.In this regard we want to run a cable from transformer secondary to Incomer ACB located at distance from 300 metres from the transformer location.How many runs of cables to be laid ? What are the design factors involved in designing the cables? otherwise selecting Busduct is good option or not? pl expain in details." posted in 2008.

All the questions presented by he/she/they display a similar grasp of electricity and it's use and application. In short, none.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#6

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/06/2014 7:01 PM

And I would like to know genius advice as to whereabouts on the planet the phenomenon of 415/50 and 415/60 can be found in the same tray! If it isn't in that country's electrical codes then it would be a glaring omission!

__________________
Good moaning!
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #6

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/06/2014 7:07 PM

I believe our helpless electrical "expert" is in India.

Re: 600V power armoured cable consruction at USA

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#12
In reply to #7

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/06/2014 9:32 PM

Possibly an international research facility that must produce all sorts of frequencies, currents, voltages and other what not that are outside of the nominal power distribution realm.

Oh, never mind me. I forgot that we're in student ridicule mode instead.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#14
In reply to #12

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/06/2014 10:58 PM

No, were in the clueless electrician working in India redicule mode.

Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#19
In reply to #12

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/07/2014 8:31 AM

Well maybe, but I am not aware of any country with 415VAC 60Hz. Does that exist anywhere but in the poster's mind? There is 380VAC in both frequencies, as the South American countries try to stay with the Western frequency "standard" (said somewhat facetiously), but use different voltages.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#8
In reply to #6

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/06/2014 7:08 PM

Japan has both 50hz and 60hz area's, I don't know if any co-mingle though....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9
In reply to #8

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/06/2014 7:14 PM

I can see someone in India getting a deal on 60 Hz equipment and using it at 50.

Not just India, but any place trying to squeeze the last penny out of a business venture.

It makes sense that they would give the job of making it work to the lowest bidder, regardless of the bidder's competence.

But, you know me. Always the cynic.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#10
In reply to #9

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/06/2014 7:35 PM

It's a miracle anything works.....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#20
In reply to #10

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/07/2014 9:33 AM

ACK!

Those pictures nearly gave me a heart attack.

That's like seeing those fake 'slumtown' pics, where the buildings look like ramshackle huts and rusted shipping containers stacked on each other at odd angles, with 'bay rooms' jutting out precariously out beyond the level below, the whole structure looking ready to collapse.

...

Please tell me those 'slumtown' pics are fake, even if you have to lie to me. My heart can't take two scares so close together.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#22
In reply to #20

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/07/2014 11:41 PM

If these huts are sea container then the earth is provided on the outside wall!

__________________
Common Sense Dictates
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#15
In reply to #8

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/07/2014 12:10 AM

I'd enough trouble getting my head around a plant using four different LV voltages. 660V, 550V, 433V and 380V. (It's a long story.)

Two frequencies would add all kinds of possibilities.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User
United Kingdom - Member - New Member Engineering Fields - Transportation Engineering - New Member Technical Fields - Marketing/Advertising - New Member Hobbies - Target Shooting - New Member

Join Date: Sep 2007
Location: South coast of England
Posts: 411
Good Answers: 36
#17
In reply to #6

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/07/2014 4:57 AM

I worked in a test facility where we had 0-800V 3 phase 50Hz, 60Hz and 400Hz in the same cable trays. Only 100kVA at 60Hz and 20kVA at 400Hz though. We had a shed outside with some elderly rotary converters.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#28
In reply to #17

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/12/2014 10:10 AM

Was there cable tray in the shed?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#13

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/06/2014 9:37 PM

Well I guess some type of answer is appropriate.

Under the Canadian code...

A cable tray is considered a raceway. The rules state that... If conductors or cables are connected to different sources of voltage...

They will be separated by the metal armour or metal sheaths of cable assemblies,

Or separated by non-metallic insulating barriers,

Or provide power to or control only remote devices and all conductors must all be rated for the highest voltage in the tray.

There are a few other requirements... but that is the important stuff. Time to hit the books my friend.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 2)
3
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#18

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/07/2014 5:32 AM

Now that lots of motors are driven by variable speed drives, cables with different frequencies are commonplace in industrial situations. Provided that the cables are shielded (wire armoring is sufficient) and the shield is grounded (at one end only to prevent ground loops), there are no problems.

Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: Oct 2008
Posts: 23
#24

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/09/2014 12:28 PM

in my case is totally different, supply voltage is 415AC 50 hz system.some of the equipments, we are getting from USA which are 480VAC,60hz system.

Hence we are proposing 60 hz 480VAC static frequency converter in the electrical where we kept main pcc.

That's why i asked this question whether 50 hz cables and 60 hz cables of voltages 415VAC and 480VAC respectively in a same cable tray or not.

hope you have might have understood my question. I want some technical reason to use same cable tray or not to use the same cable tray.

Register to Reply
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#27
In reply to #24

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/12/2014 9:12 AM

See answers 13 and 18. If you are installing armored or shielded cables they will not cause any problems and can go on the same tray. If you are installing unarmored or unshielded cables they could cause problems on long runs and in fault conditions, so you have to put them on different trays.

If you were planning to use unarmored/unshielded cable, calculate which is more cost effective, substituting armored/shielded cable or adding a second tray.

Paragraph 1 sums up the technical argument. Use paragraph 2 to back up your decision with an economic justification.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#29

Re: Using 50 hz 415VAC And 60 hz 415VAC Cable On Same Cable Tray

08/12/2014 10:10 AM

Metallic tray or non-metallic tray?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 32 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

adreasler (1); Anonymous Poster (2); Chankley (1); Crabtree (1); g_nraja (1); IdeaSmith (4); jhhassociates (2); JRaef (2); lyn (5); North of 60 (2); Phys (1); PWSlack (2); redfred (5); SolarEagle (2); TonyS (1)

Previous in Forum: Type of Grounding System   Next in Forum: The Birds on High Voltage Power Lines Question

Advertisement