Generator Tripping on Over Current

08/09/2014 6:31 AM

when a 4.5MVA generator synchronized with grid, its loss its excitation and tripped on over current as loss of excitation protection was not installed. what is the possible reason of that over current.

Register to Reply
Pathfinder Tags: "generator"
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Generator tripping on over current

08/09/2014 7:54 AM

Another ESO incident.

Current from the grid flowing back into the windings comes first to my mind.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#2

Re: Generator tripping on over current

08/09/2014 8:18 AM

sure fire case of a grounded flux capacitor

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Generator tripping on over current

08/09/2014 11:14 AM

Loss of excitation protection was not installed.

Next question.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#4

Re: Generator tripping on over current

08/09/2014 11:54 AM

Loss of excitation.

__________________
Good moaning!
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Generator Tripping on Over Current

08/09/2014 4:35 PM

Reverse power; i.e., power is going from the grid (or other generator) into the generator that lost excitiation, thus driving it like a motor.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
2
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6

Re: Generator Tripping on Over Current

08/10/2014 2:47 AM

Maybe am looking at this a little too simply but loss of excitation means that instead supplying current to the grid, it (the generator) will start to "take" current "from" the grid.

It turns a generator from a generator to a giant motor and could severely damage the generator and possibly the prime mover....possibly personnel too...

....so good generator installations have a "reverse power" sensing that drops the connection to the grid as good as "instantly" when this happens...

It would appear that you need to fault find your excitation circuits and control.....maybe even the hardware mounted on the generator itself, whatever that is!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Good Answer (Score 2)
Anonymous Poster #1
#7
In reply to #6

Re: Generator Tripping on Over Current

08/10/2014 9:25 AM

As already stated here, more succinctly:#5

Register to Reply
Anonymous Poster #1
#8
In reply to #7

Re: Generator Tripping on Over Current

08/10/2014 9:26 AM

And here:#1

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#10
In reply to #7

Re: Generator Tripping on Over Current

08/10/2014 10:54 AM

So because two people have already posted (very sparingly I might add. So sparingly that the OP may, or may not fully understand what the problem is!!), a third person (Moi!) is not allowed to post in a more proper and full manner that would be difficult to misunderstand????

To remind you, here are all three posts, my post was as follows:-

Maybe am looking at this a little too simply but loss of excitation means that instead supplying current to the grid, it (the generator) will start to "take" current "from" the grid.

It turns a generator from a generator to a giant motor and could severely damage the generator and possibly the prime mover....possibly personnel too...

....so good generator installations have a "reverse power" sensing that drops the connection to the grid as good as "instantly" when this happens...

It would appear that you need to fault find your excitation circuits and control.....maybe even the hardware mounted on the generator itself, whatever that is!!!

Post #1 (The first one that you "accidentally" mentioned second for some obtuse reason!!):-

Another ESO incident.

Current from the grid flowing back into the windings comes first to my mind.

Badly spelled words are shown underlined, in the also grammatically poor Post #5 (I wonder who that was ):-

Reverse power; i.e., power is going from the grid (or other generator) into the generator that lost excitiation, thus driving it like a motor.

The post you mentioned first was actually second!!! Possibly yours?

But in the future, DO try to do it like a man, using your own name for example.......

All I can say is "what a W*****!!!"

By the way, if you send me your email name for real, I will send you that perfect name for you in full AND the link on the Oxford dictionary so that you know exactly what it means.....in case you don't already!!

The English definition reads (The US definition would be erased from CR4) :-(

A contemptible person (used as a generalized term of abuse).

Maybe a bad hair day?

But here on CR4, you are certainly not alone!!!!

Thankfully though, you are in a VERY tiny minority! All with the same first names "Anonymous Poster".....Got it?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#9
In reply to #6

Re: Generator Tripping on Over Current

08/10/2014 10:15 AM

And the protection circuitry tripping out, as it is supposed to act, is why this is another ESO incident. Some prime mover mechanical connections have a planned weak point (shear pin) that will mitigate the mechanical damage if the relay contacts are fused closed or foolishly bypassed.

It was good of you to connect the dots already pointed out. I (for one) forget that we attract people in and out of engineering that need the dots connected.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#11
In reply to #9

Re: Generator Tripping on Over Current

08/10/2014 11:00 AM

Many thanks for your friendly comments redfred. I wish you a great day.

The "Anonymous Poster #1" (who we probably all know EXACTLY who he is), simply does not "get it!".....either with the technology, the spelling of certain word, or the use of good manners......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply Score 1 for Off Topic
Register to Reply 11 comments