Need Help ASAP....ZETA NPSX Gen S/C Gen FLT Alarm

08/18/2014 5:24 AM

Hi

How can i stop the Gen S/C , Zonal Fault, and Gen Flt alarm in our FDAS system. we already tried replacing the smoke detector on the zonal fault where the alarm led originates but we still kept on getting the same alarm. i already tried switching the keys on and off as what was describe in the manual but still it does not remedy the problem.

PS

Sometimes It also displays a Fire/zones alarm and switches from 1 zone to the other even without any fire.

thank you for the help

Register to Reply
Pathfinder Tags: "NPSX" "ZETA" Help ASAP"
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: NEED HELP ASAP....ZETA NPSX Gen S/C Gen FLT alarm

08/18/2014 5:29 AM

Easy. RING THE EQUIPMENT MANUFACTURER AND TALK THROUGH THE PROBLEM DIRECTLY.

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Jun 2014
Posts: 9
#2
In reply to #1

Re: NEED HELP ASAP....ZETA NPSX Gen S/C Gen FLT alarm

08/18/2014 5:36 AM

Thanks but we need to remedy the problem ASAP so calling the manufacturer is not an option right now

Register to Reply
Anonymous Poster #1
#3
In reply to #2

Re: NEED HELP ASAP....ZETA NPSX Gen S/C Gen FLT alarm

08/18/2014 5:40 AM

Harhahahahahahahahahaha!

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #2

Re: NEED HELP ASAP....ZETA NPSX Gen S/C Gen FLT alarm

08/18/2014 5:46 AM

<Resubscribes>

The expression <...ASAP...> applied to a task in the Microsoft Project domain means that it becomes lowest priority and therefore can go to the back of the queue behind other tasks. For example, New Year's Day 2023 is possible. Is that soon enough (rhetorical question - NNTR)?

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Jun 2014
Posts: 9
#5
In reply to #4

Re: NEED HELP ASAP....ZETA NPSX Gen S/C Gen FLT alarm

08/18/2014 5:59 AM

apologies for the misunderstanding

but we really need to settle this today

thank you

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6

Re: NEED HELP ASAP....ZETA NPSX Gen S/C Gen FLT alarm

08/18/2014 6:06 AM

Please report back tomorrow, and then the day after tomorrow. We wish you best success on solving this.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
4
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#7

Re: Need Help ASAP....ZETA NPSX Gen S/C Gen FLT Alarm

08/18/2014 8:54 AM

Sounds like the E.O.L. (End Of Line) resistance may be incorrect for your application.

Fire detection circuit impedance is critical and specific to the OEM requirement(s) for each application, fire panel type, and version.

The motherboard monitors each circuit by measuring the amount of current flowing through the loop at all times.

The circuit loop requires an End Of Line resistor or a configurable detector at the end position of the circuit or a configurable channel in the main panel to compensate for the quantity of detectors used.

Example:

Panel "A" requires circuit card A1B2 for all channels with 1 to 5 detectors and the total impedance for 5 detectors is: 1.2 ohms.

However the application only requires 3 detectors for one of the circuits.

This means the end of line detector must have a resistor connected across the sensor terminals of the correct value to meet the circuit impedance requirement for 5 detectors or the detector may be configurable with on-board dip switches or the panel motherboard cahennel will be configurable so that the circuit impedance can be matched to the panel.

The type of fire system and age of the unit determines which system is used.

This information is only available from the Original Equipment Manufacturer (OEM) and in some cases it is proprietary and only available through using the OEM field service department. (Too muchrisk & liability.)

Any attempts to repair or alter the fire system wihtout following the factory design specifications will yield an inoperable, faulty, unsafe system.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply Good Answer (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #7

Re: Need Help ASAP....ZETA NPSX Gen S/C Gen FLT Alarm

08/18/2014 9:12 AM

<...This information is only available from the Original Equipment Manufacturer (OEM)...>

This is why telephone skills and a desire to use it are so valuable. GA.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Jun 2014
Posts: 9
#9
In reply to #7

Re: Need Help ASAP....ZETA NPSX Gen S/C Gen FLT Alarm

08/19/2014 12:16 AM

Thank you so much we tried to place diode between the terminal (1n4001) this cause to stop the alarm except when we put it across terminal 3 which triggers the device. we want to try putting on 10k resistors

hoping for your feedback and corrections/suggestion

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#10
In reply to #9

Re: Need Help ASAP....ZETA NPSX Gen S/C Gen FLT Alarm

08/19/2014 9:36 AM

Installing any device other than that which is specified by the original equipment manufacturer in the correct location will cause unreliable operation and/or failure of the fire system.

It is imperative that you obtain the correct information required to solve the issue.

The only reliable, competent source for your needed information is from the original manufacturer or a factory authorized repair service.

Contact the factory and purchase the information and/or needed technical services before it is too late.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
Hobbies - Target Shooting - New Member

Join Date: Jan 2011
Location: Indiana
Posts: 558
Good Answers: 14
#11

Re: Need Help ASAP....ZETA NPSX Gen S/C Gen FLT Alarm

08/19/2014 12:13 PM

I would hate to be your Insurance provider. Most states have a requirement that you must be a certified fire tech to work on a fire control or alarm system of this order. Why are you trying to defeat your system by fooling with resister values you have no clue what they should be. If you do manage to turn the system off for the moment what happens when you go home tonight and the system doesn't go off like it is originally intended to if there is a fire . I do not want work in this building. A (CERTIFIED) fire tech, or inspector needs to work on this system not maintenance tech. I've seen too many botched fire and security systems destroyed by unqualified people trying to do a quick fix. All signs of building owners when they get the bill for the repairs when they thought they were saving money.Duke

__________________
Four boxes keep America Free The soap box, The ballot box, The jury box, & The cartridge box.
Register to Reply
Guru
Hobbies - Musician - New Member

Join Date: Feb 2012
Posts: 523
Good Answers: 17
#12

Re: Need Help ASAP....ZETA NPSX Gen S/C Gen FLT Alarm

08/19/2014 12:18 PM

You also need to consider liability issues. If the you do your own fixes or repairs, your insurance company may not feel obligated to pay if the fire detection system fails to detect.

Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Dexter531 (3); LOCKDUKE (1); PWSlack (3); reward54 (1); SHOCKHISCAN (2); Tornado (1)