Dear Sir,

what capacity of UPS required for 24vdc,30amp power supply ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#1

Re: ups requited.

09/06/2014 2:56 AM

It depends on how long you would like to keep it running after an interruption.

24Vx30A =>80 Watts will do approximately.

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply
Power-User

Join Date: May 2010
Posts: 146
Good Answers: 2
#2
In reply to #1

Re: ups requited.

09/06/2014 3:30 AM

24 x 30 = 80 ????????????????????????????????????????????????????????????????????????????????????????????

Register to Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#4
In reply to #2

Re: ups requited.

09/06/2014 5:36 AM

oh, sorry my bad, that should 800Watts, more than or equal to be precise.

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#3

Re: ups requited.

09/06/2014 3:46 AM

Dear Mr.khigupta1972,

The UPS Capacity should be decided in terms of AMPERE-HOUR, where the Time plays the deciding criterion. You may choose for Half-an-hour, or one hour or 2 hours and so on. The Battery capacity/size will decide the back up power supply duration.

So please decide - how much time you want back up power.

DHAYANANDHAN.S

Register to Reply Score 1 for Good Answer
Member

Join Date: Oct 2013
Posts: 5
#6
In reply to #3

Re: ups requited.

09/06/2014 8:47 AM

we want to hold 1hour in ups.

Register to Reply
Guru
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2011
Location: 18N 65W o
Posts: 1003
Good Answers: 28
#7
In reply to #6

Re: ups requited.

09/06/2014 9:21 AM

A UPS is a relatively inefficient source. I would contact the UPS manufacturer and get his input. While the load is easy to calculate, the amount the UPS "wastes" creating that power is significant.

Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#8
In reply to #6

Re: ups requited.

09/06/2014 1:28 PM

Well then your UPS needs 30 amp hour batteries at 24 volts DC.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: ups requited.

09/06/2014 7:19 AM

Required wattage capability = 720.

Required battery amp hours = 30 x as many hours of backup as you desire.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Sep 2011
Posts: 267
Good Answers: 7
#9

Re: UPS Required

09/06/2014 11:26 PM

Don;t forget that there are 24 VDC UPS's as well.

Register to Reply
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#10

Re: UPS Required

09/07/2014 6:27 AM

You don't need one. Obviously you have no consumption for no time.

If I am wrong and you do have some consumption and you want to maintain that consumption over 2 days ( for example ); tell us!

Jim

__________________
Where's the KaBoom? There should be a KaBoom!
Register to Reply
3
Associate

Join Date: Jan 2007
Location: Melbourne, Australia
Posts: 51
Good Answers: 5
#11

Re: UPS Required

09/07/2014 9:04 PM

The important things to specify in a DC UPS is the amount of time you want to maintain the load. You have now said 1 hour.

The other thing is that batteries are usually rated at the 10 hour rate. Therefore a 30 Amp Hour (AH) battery should give 3 amp for 10 hours.

At 30 Amp you will probably need about 45 AH minimum and I would go for about 60 AH to be sure you get your 30 A for an hour.

Also be aware that most DC UPS units run at the charging voltage of the battery around 28.8 V and when the main power fails go straight to the battery nominal voltage of just over 24 V. This will drop during the 1 hour at 30 A to about 22 V which is the lowest that the battery should be run down to. After that the unit should cut the supply to the load to avoid ruining the battery by running it down to very low voltage.

Can your application handle this voltage variation?

If you need to remain at 24 V +/- a small variation you need a unit with a regulated output during the normal running when the mains power is available. It is possible but quite expensive to also have a regulated output while the mains is unavaiable but this needs a DC - DC converter with a regulated output to step it up from the reduced battery voltage.

A final thing to remember is the recharge time after running the battery completely down to its minimum. Frequently this is in excess of 24 hours. If your power supply is too unreliable then you may suffer if there is a second interruption.

__________________
fsmit@dyne.com.au
Register to Reply Good Answer (Score 3)
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: