Transmitter Yokogawa EJX430 Show IOP and Normal Again

09/14/2014 7:34 AM

we are using yokogawa transmitter model EJX430 , ON SEAL PRESSURE VOTING SYSTEM on recycle gas compressor , after installing new one for third time the transmitter works for a year or so and it malfunction by giving iop reading ,please suggest the cause of the failure

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Transmitter Yokogawa EJX430 Show IOP and Normal Again

09/14/2014 3:44 PM

I would call the manufacturer to see if any similar failures have been reported, and what may be the cause....then, if necessary, do a forensic investigation to determine cause of failure....IE: take it apart to see what failed....then come back with all pertinent information to determine cause, if not apparent...

http://www.yokogawa.com/fld/doc/manual/fld-ejx-manual-01en.htm

http://www.yokogawa.com/us/products/field-instruments/pressure-transmitters/gauge-pressure/ejx430a.htm

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#2

Re: Transmitter Yokogawa EJX430 Show IOP and Normal Again

09/14/2014 6:28 PM

1) Yokogawa's EJA line is SIL 2/3 certified by TuV Nord, which testifies to its inherent ruggedness. The transmitter has advanced diagnostics. Given the frequency of failure you've encountered, what does the diagnostic data from the failures tell you?

2) Please clarify what "IOP reading" is, with a specific example of what g that is in this case.

3) In a voting situation , there are multiple transmitters each in its location.
3a) How many transmitters are involved at this process point?
3b) Is the one that fails from the same location where the previous failure occurred, or are the failures at different locations?

4). Please provide some details of the processs and environmental conditions:

- Max/min temperatures, ambient and process
- Process medium, what is it? How corrosive is it? Has it been tested for water content? pH?
- vibration at mounting location?
- pressure pulsations in process line? Frequency? Is xmtr output damped to limit pulsation?
- do the transmitters have lightning/surge protection/arrestors installed?
- were any of the xmtrs physically damaged by contact with wrenches, crow bars, or other solid objects at velocities above 0.0 m/s?
- was the area flooded in recent history?
- can water that condenses inside electrical conduit enter the transmitter or are there U trap installed to catch the condensation?
- how close is the nearest VFD installed to the transmitter?

Register to Reply
Commentator
India - Member - ADIL MOULA Engineering Fields - Instrumentation Engineering - Adil Moula

Join Date: Jun 2008
Location: India
Posts: 95
Good Answers: 1
#3
In reply to #2

Re: Transmitter Yokogawa EJX430 Show IOP and Normal Again

09/15/2014 12:17 AM

we have verify in error log view it shows P sensor error.in a day 4 to 5 times the alarm is initiated , the voting system 2 of 3 ,we have replaced all of 3 transmitter temperature is between 35 degrees centi. seal pressure measured is .06bar range of transmitter 0 to5 bar , surge protection is installed at the marshalling cabinet . no vfd near by , no flood nor any water condensation, no vibration .

the process is recycle gas compressor hydrogen with some mixture of H2S , trubine driven compressor 13670rpm generally operating.

hope the data is sufficent

Register to Reply
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Transmitter Yokogawa EJX430 Show IOP and Normal Again

09/15/2014 5:00 AM

A mismatch between the wetting fluid and the wetted materials has to be among the possibilities. Not knowing the circumstances surrounding the failure and also not being able to see it doesn't exactly help.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Commentator
India - Member - ADIL MOULA Engineering Fields - Instrumentation Engineering - Adil Moula

Join Date: Jun 2008
Location: India
Posts: 95
Good Answers: 1
#5
In reply to #4

Re: Transmitter Yokogawa EJX430 Show IOP and Normal Again

09/15/2014 6:06 AM

Full model number EJX430A-EAS4G-719DD , SURROUNDING I can say transmitter is installed near the compressor side where we have two make up gas compressor reciprocating plus this recycle gas compressor distance between them appoxi. 5mtrs all are in a roof shade and installed 3mtrs above the ground level.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #5

Re: Transmitter Yokogawa EJX430 Show IOP and Normal Again

09/17/2014 5:53 AM

Fluid composition? Temperatures? Pressures? Flowrates? Materials of construction of the pipework?

Please help the forum to supply the help required.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#6

Re: Transmitter Yokogawa EJX430 Show IOP and Normal Again

09/15/2014 6:34 AM

There is a very high probability that the problem is hydrogen ion migration. Go read Yokogawa's application note:

http://www.yokogawa.com/us/is/downloads/pdf/fieldinstruments/appnotes/Pressure/pd280001.pdf

Register to Reply Good Answer (Score 2)
Commentator
India - Member - ADIL MOULA Engineering Fields - Instrumentation Engineering - Adil Moula

Join Date: Jun 2008
Location: India
Posts: 95
Good Answers: 1
#7
In reply to #6

Re: Transmitter Yokogawa EJX430 Show IOP and Normal Again

09/15/2014 8:55 AM

thanks I ahve to look into it

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #6

Re: Transmitter Yokogawa EJX430 Show IOP and Normal Again

09/17/2014 5:58 AM

Ions in a gas? There are very few places near the Earth's surface where a plasma is to be found!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster #1
#10

Re: Transmitter Yokogawa EJX430 Show IOP and Normal Again

11/06/2014 2:20 AM

This is a common failure mode of the Yokogawa transmitters. We have had the same thing happen and have removed them from all critical functions. We now only use these transmitters in control situations.

We have approached Yokogawa about the problem and they are unable to explain the failure except to offer a new unit.

I personnally would start looking to a different brand.

Register to Reply
Participant

Join Date: Nov 2014
Posts: 1
#11

Re: Transmitter Yokogawa EJX430 Show IOP and Normal Again

11/08/2014 1:03 AM

Based on experience the EJA series are better than EJX series transmitters.

Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: