09/15/2014 8:35 PM

Hello, I have a doubt regarding capacitor bank in electrical system. Do Capacitor bank in leading mode have an effect on insulation of motors which are started in DOL as well as VFD. In our plant we are having ABB VFD's ACS 800 which is used to run 690V Kirloskar make motors. Twice our motor have failed on insulation grounds. Voltage is maintained at 688-694V. Kindly suggest what can be the reason if capacitor bank are not.

Register to Reply
Pathfinder Tags: Motor insulation failure
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42357
Good Answers: 1695
#1

Re: Motor Insulation Failure

09/15/2014 9:39 PM

Insulation failures are almost always caused by excessive heat.

If it's DOL starting, that may be the problem. You will have to decide.

Have you done any trouble shooting? Taken AMP readings at start-up?

What have you done?

I just park cars for a living, but I read somewhere..................................

Register to Reply
Participant

Join Date: Sep 2014
Posts: 2
#2
In reply to #1

Re: Motor Insulation Failure

09/15/2014 9:58 PM

HI, Ampere readings are normal at 110A running load condition, while its rated is 269A. Apart from that it is having a leakage current of approx. 1.5A in earthing cable. Output voltage is around 684V. At this moment no troubleshooting done on that, we have replaced the motor.

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42357
Good Answers: 1695
#4
In reply to #2

Re: Motor Insulation Failure

09/15/2014 10:15 PM

Starting current is what? For how long?

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8
In reply to #1

Re: Motor Insulation Failure

09/17/2014 2:34 AM

LOL!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
4
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 445
#3

Re: Motor Insulation Failure

09/15/2014 10:10 PM

Your doubts are well founded, especially if the capacitor bank is always in the circuit under varying load conditions. Poorly chosen capacitor sizes and/or control strategies can lead to unacceptably high transient voltage conditions during switching or anything other than full load conditions. There is also the chance for a resonance condition to occur, all of which may lead to punctured insulation in the capacitors and the motor windings.

This paper is an introduction to the problem, Google will provide many more references.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 4)
6
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Motor Insulation Failure

09/15/2014 10:35 PM

In our plant we are having ABB VFD's ACS 800 which is used to run 690V Kirloskar make motors. Twice our motor have failed on insulation grounds. Voltage is maintained at 688-694V. Kindly suggest what can be the reason if capacitor bank are not.

This sounds as though the insulation failure is on the motors that are run from the VFD, so I do not understand why you have raised the read herring (irrelevant issue) regarding DOL motors...

If so, this would have nothing to do with any PFC capacitors, although why you have them and why they run leading is an entirely different issue. Insulation damage done to motors being run from VFDs is a very well known problem, referred to as the "Reflected Wave" and/or "Standing Wave" phenomenon. There are countless documents available on the web explaining it and offering mitigation options, many referenced from within the history of this forum if you know how to search.

So did nobody take this issue into consideration when putting the VFD systems out for tender? Usually it is put to the VFD vendor to include the necessary mitigation options to prevent this, sometimes it is put onto the motor supplier but they often have no knowledge of how bad the problem will be, yet the VFD supplier will. So who was supposed to prevent this from happening on your project? Did nobody at ABB bother to mention it to you? If not, that would be EXTREMELY irresponsible in this day and age, and I know from the fact that you mentioned an ACS800 that this is not old equipment.

If it were me, and my tender offer included a clause that insisted that the motors be properly protected from insulation breakdown, I would be calling ABB for taking care of the failures. If nothing was mentioned and someone just bought the lowest cost package, then you got what you paid for. You can still mitigate it to protect the new motors, but first you need to find someone at your location who can come out and investigate it to provide the CORRECT solution. Otherwise you might be throwing good money after bad...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 6)
Guru

Join Date: Dec 2008
Location: Cd. Juarez, Chihuahua, Mexico.
Posts: 1023
Good Answers: 69
#6
In reply to #5

Re: Motor Insulation Failure

09/16/2014 10:39 AM

Absolutely, the O.P. needs inverter duty motors and/or true sine drives; GA.

__________________
No hay conocimiento ni herramienta que sustituya al sentido comun.
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#7
In reply to #5

Re: Motor Insulation Failure

09/16/2014 11:33 PM

The ABB installation manuals suggest various problems and remedies, including common mode chokes, line filters, grounding practices, and motor selection.

Register to Reply
Power-User

Join Date: May 2010
Location: Cambridge, MA
Posts: 390
Good Answers: 82
#10
In reply to #5

Re: Motor Insulation Failure

09/17/2014 8:12 AM

At Rockwell's literature site, there's an Allen-Bradley document where they describe the problem: excessive ringing on the sharp PWM line IGBT-switching edges, from the VFD and the long motor cables, and they show 'scope waveforms.

They show a 1264-volt ringing waveform (they say it can get as high as 2500 volts in a 575-volt system), which could be reduced to 1032 volts with a reactor, but they do better with a "terminator," placed at the motor, which clamps this to a safer 888 volts for a few microseconds only, and no ringing.

To solve the motor-winding-damage problem they suggest the use of their 1204 Motor Terminator, and the document gives details about selecting the right model, its installation and use.

__________________
Thanks, Win
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#12
In reply to #10

Re: Motor Insulation Failure

09/17/2014 11:41 AM

And those units often get stinking hot!

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#9

Re: Motor Insulation Failure

09/17/2014 2:44 AM

I'm learning a lot here ....and having a laugh too!! It really couldn't be better!!!

Its a new slant on this area for me personally. The Navy never used capacitor banks...

Thanks to all concerned.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#11

Re: Motor Insulation Failure

09/17/2014 11:40 AM

I trust you do not have any capacitors on the output of the VFD. No PF correction capacitors are allowed at that location.

Register to Reply
Participant

Join Date: May 2013
Location: Auckland
Posts: 3
#13

Re: Motor Insulation Failure

09/17/2014 2:12 PM

ensure the motor p.f is not leading with the capacitor bank. it should be lagging p.f, and the insulation class should be higher side if it comes to VFD, better to go for next higher KW. use separate cooling fan for cooling the motor.

Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Andy Germany (2); Anup Samantray (1); GW (3); JRaef (1); lyn (2); parthasarathy82 (1); RAMConsult (1); Winfield Hill (1); Yahlasit (1)

Previous in Forum: Reduce the Speed of Slip Ring Motor   Next in Forum: Electrical Software Use In Oil And Gas Field

Advertisement