Is 3 Phase Line Always Balanced?

09/24/2014 11:31 AM

I am looking for answers from people working / experienced in power generating / transmitting or distribution companies in Europe/ Canada/UK/ USA/ Australia -are all the 3 phases always balanced in terms of voltage / current? How much imbalance (say in terms of %) if any has been observed - during peak / off peak / night hours. If there are imbalances - what steps are taken to ensure that balance gets restored. Does imbalance lead to instability in operation of generators- thermal or hydro?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Is 3 phase line always balanced?

09/24/2014 11:37 AM

Can you post the questions from the test directly to the forum so we can dispense with the pretense that you have experienced some offense at the realization that you have no sense....of the true purpose of the test?

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Is 3 Phase Line Always Balanced?

09/24/2014 12:30 PM

Of course three phase lines are not fixed in balance. If they were always balanced then there would be no need for the adjective "balanced" to be used in this context.The real question here is can somebody be taught to think? I say no they cannot be taught to think. Sometimes one can be coerced into thinking with abuse, I prefer to use an argument today.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User
Engineering Fields - Control Engineering - Control Engineering Technical Fields - Education - Industrial Training Engineering Fields - Manufacturing Engineering - Manufacturing Training Engineering Fields - Electrical Engineering - Electrical engineering Training Engineering Fields - Instrumentation Engineering - Instrumentation Engineering United States - Member - New Member Engineering Fields - Energy Engineering - Become part of the larger group, change your world.

Join Date: Apr 2005
Location: Las Vegas, NV
Posts: 266
Good Answers: 1
#3

Re: Is 3 Phase Line Always Balanced?

09/24/2014 12:40 PM

"... are all the 3 phases always balanced in terms of voltage?" NO

" ... what is typical %" Varies

Above 4% is range for overheating concerns. With freq drives, depends on circuit design (see manual).

__________________
AB PLC Training onsite, On-Line, training software and more. BIN95.com
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Is 3 Phase Line Always Balanced?

09/24/2014 2:51 PM

3-phase lines are never truly balanced.

A 3-phase line connected only to a single phase load is about as unbalanced as it ever gets.

In the UK, what used to be the red phase always carries a higher current than the others, as the electrician always starts from the top left of the distribution board when adding new single phase circuits, and it is the former red at the top. The solution is to rewire some of the former red phase single phase loads onto the former yellow and the former blue.

The forum has dealt with this topic previously, as entering the words "balanced 3-phase" into the "Search all of CR4" box and clicking Go will reveal.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5
In reply to #4

Re: Is 3 Phase Line Always Balanced?

09/24/2014 4:46 PM

How about a 3 phase source driving two single phase load SWMPS that do not have power factor compensation circuitry.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Is 3 Phase Line Always Balanced?

09/24/2014 8:32 PM

Considering the OP has had a good answer in a thread on this very subject I find his question a little strange

As an aside. Whenever I've had to look in to loading on 3Ph supplies, red nearly always carries the heaviest load.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7

Re: Is 3 Phase Line Always Balanced?

09/24/2014 11:40 PM

What do standards/codes like BS,NEC,VDE,IEC etc say,what is the maximum unbalance in utilitiy's voltage allowed?.

__________________
pnaban
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#9
In reply to #7

Re: Is 3 Phase Line Always Balanced?

09/25/2014 2:31 AM

All on one phase and nothing on the other two, Boss. It doesn't need any code to do that, only a few switches.

__________________
Good moaning!
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 258
Good Answers: 2
#8

Re: Is 3 Phase Line Always Balanced?

09/25/2014 12:18 AM

In India I have been hearing about the three phases being unbalanced leading to heating of transformers. I also heard from someone that the thermal power generator is not stabilized and goes into oscillations whenever there are large load transients. Earlier- I used to listen to these passive as plain complaints. Now I am in a position to find a solution and have an opportunity to implement it.

First thought that came to my mind was - to check with CR4 whether this problem is a global phenomena or confined to India only.

This should answer various queries raised in this thread. I am happy to note that this seems to be a global phenomena and utilities need to find solution technologically and not be just making requests, cajoling , coaxing customers to ensure balanced load on all 3 phases all the time. I like taking up such challenges.

"Knowledge is the food of the soul." -- Plato

"Determine that the thing can and shall be done, and then we shall find the way." -- Abraham Lincoln

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#10
In reply to #8

Re: Is 3 Phase Line Always Balanced?

09/25/2014 2:33 AM

So why don't you make a start by spreading your own single phase loads around the distribution boards in a more balanced way, Mildred?

__________________
Good moaning!
Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#17
In reply to #8

Re: Is 3 Phase Line Always Balanced?

09/25/2014 6:38 PM

One of the reasons type "K" transformers are preferred now. The neutral is the same size as the three lines.

I often wonder how all the miles of 185mm2 3½c SWA in installed years ago is coping with imbalance and harmonics nowadays. It's rare to come across 3½c now, 4c is the cable of necessity.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 258
Good Answers: 2
#18
In reply to #17

Re: Is 3 Phase Line Always Balanced?

09/26/2014 4:32 AM

From the generating stations almost upto 11KV it is just 3 wire system. Neutral only comes at distribution level. Imbalances at 11 or 33 KV level are transferred right up to the generator. Hence the problem needs need to be solved right at distribution / user level.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#19
In reply to #18

Re: Is 3 Phase Line Always Balanced?

09/26/2014 5:59 AM

Thanks from me personally.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#11

Re: Is 3 Phase Line Always Balanced?

09/25/2014 3:20 AM

I guess that unless we design alternators to keep each separate phase voltage exactly the same in spite of load changes only affecting this phase, we are stuck with the problem.

Has anyone a better take on that idea?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#12
In reply to #11

Re: Is 3 Phase Line Always Balanced?

09/25/2014 3:26 AM

You should have 3 single phase alternators each with a separate AVR. There should be 3 neutrals too. Any comments.

__________________
pnaban
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#13
In reply to #12

Re: Is 3 Phase Line Always Balanced?

09/25/2014 3:45 AM

If an alternator (or the 3 phase supply after a transformer) stays with basically with the design s we have now, at some point the neutrals have to connected to each other.

In a domestic situation here in Germany where we have 3 phases coming into the house, they are linked in the house fuse box(es). 4 wire supply cable.

In the UK where usually only a single phase is supplied to a house generally, the links must be in some external distribution box where the 3 phases meet.

The only method I can see to keep neutrals separate is to only generate single phases per alternator....but what would industry do who need 3 phases?

Maybe 3 such alternators could be driven by a single prime mover, all on one shaft, and stay at 120° phase difference that way.....but any connection of three phases for say industry, except after a delta/wye transformer, would "link" them up again....

Most of the above is written when thinking, not always a good idea, so apologies if there are any major blunders......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#14
In reply to #12

Re: Is 3 Phase Line Always Balanced?

09/25/2014 9:44 AM

So how do you stop one of them overtaking the other two, or vice-versa? Then I'd be worried about powering a regular 3-phase motor with the arrangement you suggest. That it isn't done would suggest it's a bad idea.

__________________
Good moaning!
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#22
In reply to #12

Re: Is 3 Phase Line Always Balanced?

10/14/2014 3:20 AM

Due to voltage drop due to I & R voltage along the line will vary.

__________________
pnaban
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 258
Good Answers: 2
#23
In reply to #22

Re: Is 3 Phase Line Always Balanced?

10/14/2014 7:56 AM

But if we somehow balance all 3 phases at distribution level say many kilometers away by modifying the transformers - will the generators remain balanced?

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#24
In reply to #23

Re: Is 3 Phase Line Always Balanced?

10/14/2014 9:25 AM

In theory, yes if the distribution is balanced then the generators will be balanced. In practice one can never perfectly balance all three phases. Different single phase loads get switched on and off at different times, mechanical loads on motors change suddenly. Sometimes the mechanical load changes so quickly that for a brief period the motor acts as a generator putting power onto the grid instead of taking power. Then there's the time delay between generation sources and changing loads that produce the reflected waves described by Oliver Heaviside's telegraphers equations for transmission lines. [It still amazes me that these equations were codified in 1880, long before any oscilloscopes existed.]

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 258
Good Answers: 2
#25
In reply to #24

Re: Is 3 Phase Line Always Balanced?

10/14/2014 9:47 AM

I do agree with you. I take pleasure in revisiting things mentioned in 1880. Thomas Alva Edison invented the incandescent bulb- but later scientists found gas discharge tubes give more light- without heat generation as in incandescent bulb. I have always believed that very little improvements have taken place on things developed by Edison, while the communication field has seen lot of innovative developments compared to what Graham Bell's invention. That also menas there is scope for development in power sector and it is a challenge- undoubtedly- not mere talking. While I write all this- I am also cautiously gathering information. Thanks.

Register to Reply
Power-User
Engineering Fields - Control Engineering - Control Engineering Technical Fields - Education - Industrial Training Engineering Fields - Manufacturing Engineering - Manufacturing Training Engineering Fields - Electrical Engineering - Electrical engineering Training Engineering Fields - Instrumentation Engineering - Instrumentation Engineering United States - Member - New Member Engineering Fields - Energy Engineering - Become part of the larger group, change your world.

Join Date: Apr 2005
Location: Las Vegas, NV
Posts: 266
Good Answers: 1
#28
In reply to #24

Re: Is 3 Phase Line Always Balanced?

10/14/2014 6:06 PM

Ah, the Harmonics of it all.

__________________
AB PLC Training onsite, On-Line, training software and more. BIN95.com
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#27
In reply to #23

Re: Is 3 Phase Line Always Balanced?

10/14/2014 10:31 AM

We should not tamper with generated voltage but try to adjust voltage by boosters.

__________________
pnaban
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 258
Good Answers: 2
#26
In reply to #22

Re: Is 3 Phase Line Always Balanced?

10/14/2014 9:55 AM

I think you are from a Generating company.I wish to know- whether such imbalances on 3 phases lead to grid instability and wobbling/vibration in the generators- due to varying air gaps (back EMF effect), early wear and tear of bearings etc. Hence - I feel there is need to somehow solve the problem- not by utilities requesting, cajoling, coaxing customers to load all three phases equally- solution must be found through technology - not by prayers or hope!!!!!! Wish to know more from your practical experience.

"Success is not measured by what you accomplish but by the opposition you have encountered, and the courage with which you have maintained the struggle against overwhelming odds." -- Orison Swett Marden

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#15
In reply to #11

Re: Is 3 Phase Line Always Balanced?

09/25/2014 9:54 AM

I don't see it as a problem. Only a feature.

__________________
Good moaning!
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#16
In reply to #15

Re: Is 3 Phase Line Always Balanced?

09/25/2014 1:06 PM

Do you work in sales?

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Nov 2011
Posts: 258
Good Answers: 2
#20

Re: Is 3 Phase Line Always Balanced?

10/14/2014 2:47 AM

Today it occurred to me that instead of modifying transformers all over- it is better that generators in hydro or thermal power stations be modified so that even single phase loads will equally load all three phases equally. So generator manufacturers need to pay attention. 3 phases can still be transmitted over 3 lines as at present and customers can use it as 3 different single phases or 3 phase- but generator end will always be equally loaded always!!!!!!!!!!!

"Perplexity is the beginning of knowledge." -- Kahlil Gibran

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#21

Re: Is 3 Phase Line Always Balanced?

10/14/2014 3:18 AM

If alternator is designed with 3 AVRs for 3 phases there will be some balance.

__________________
pnaban
Register to Reply
Anonymous Poster #1
#29

Re: Is 3 Phase Line Always Balanced?

10/24/2014 6:06 AM

The balance of 3 phase electrical power systems is ideal. In fact, this has never happened. However, utilities always strive to make their power systems appropriately balanced in operation. So, the percentage of the imbalance is quite small.

Register to Reply
Register to Reply 29 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (4); Anonymous Poster (1); BIN95 (2); Crabtree (4); pnaban (5); PWSlack (1); redfred (3); SolarEagle (1); TonyS (2); xyz (6)

Previous in Forum: Electric Arc Furnace Regulation   Next in Forum: FCMA Soft Starter

Advertisement