Motor Contribution Through Delta/Star Transformer

10/14/2014 11:22 PM

hi all

if I have a delta (primary) / star (secondary) connected transformer and experience an earth fault on the primary, will motor current feedback from the secondary side through to the primary side for that earth fault?

Similarly, for a phase fault, will motors feedback to the primary from the secondary?

I know the answer is no for the first scenario and yes for the second, but was hoping someone could explain why. I've spent hours googling for no result.

__________________
Electrical Engineer
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster #1
#1

Re: Motor contribution through delta/star transformer

10/15/2014 1:54 AM

Hi!

Based on my experience, when transformers have winding connections with Delta/Star, the motor loads won't affect much on the asymmetrical short-circuit currents. However, if a symmetrical fault like three phase short-circuit occurs, the motors will contribute to the short-circuit currents. You could check out the problem here http://www.psa-outline.com/

Register to Reply
Commentator

Join Date: Jul 2010
Posts: 92
Good Answers: 1
#2

Re: Motor Contribution Through Delta/Star Transformer

10/15/2014 8:17 AM

Thanks for the response... can anyone explain why?

__________________
Electrical Engineer
Register to Reply
4
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3
In reply to #2

Re: Motor Contribution Through Delta/Star Transformer

10/15/2014 9:22 AM

The delta side of the transformer, having no direct connection to ground (no Neutral or Wye point connected to ground) has no path for a ground fault current to flow. If no path, then no current. When the first fault to ground occurs on a phase of the primary, all that happens is that it establishes a voltage reference for all the phases, based on that one being at ground potential. It's only a second fault to ground that then completes a circuit and you have a REAL ground fault. Note that this assumes that nowhere on the delta primary feeding the transformer is there a connection to ground in the first place (such as a wye secondary on the upstream transformer feeding the delta on yours)! Otherwise the first ground would complete a circuit and fault current would flow.

That's the principle used in delta distribution systems, usually in older industrial plants. There was no direct ground connection, so the first short to ground wouldn't bring all the motors, etc., to a halt. There would be a ground detection system that lights a flasher, rings a bell, sounds a horn, or something, so that maintenance people could track down the fault before a second one happened (and the smoke came out!).

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Good Answer (Score 4)
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#4

Re: Motor Contribution Through Delta/Star Transformer

10/16/2014 1:07 AM

HOMEWORK!!

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Motor Contribution Through Delta/Star Transformer

11/03/2014 9:34 AM

The first earth fault on the primary will establish the voltage reference for the other two primary phases. The second earth fault on the primary will take out the overcurrent protection devices, at which point the secondary will de-energise as well.

All clear?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); brich (1); PeterT (1); polerz (1); PWSlack (1)

Previous in Forum: What Caused This Damage?   Next in Forum: Parallel Operation Of DG

Advertisement