Parallel Operation Of DG

10/15/2014 12:44 AM

Can we operate 2 or more dg(desile genrator) of different rating in parallal. what are the condition for parllal operation of DG ?

Register to Reply
Pathfinder Tags: DG operation
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: Oct 2014
Posts: 14
#1

Re: parallal operaion of dg

10/15/2014 12:59 AM

Ofcourse it is possible.

In order to connect DG in parrallel the following should be checked:

  1. Phase Sequence
  2. Voltage Magnitude
  3. Frequency
  4. Phase Angle

Regards,

Hisham

Register to Reply
Active Contributor

Join Date: Sep 2010
Location: India
Posts: 11
#2
In reply to #1

Re: parallal operaion of dg

10/15/2014 6:51 AM

I this case how they contribute power .

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3
In reply to #2

Re: parallal operaion of dg

10/15/2014 9:00 AM

You will need to learn the basics of power system operation by reviewing an elementary textbook on AC circuits. Here's the short course: increasing fuel causes increasing real power flow, increasing excitation/field current causes increasing reactive power flow. If you do not understand or know this already then follow the instructions in the first sentence.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#4
In reply to #2

Re: parallal operaion of dg

10/15/2014 10:46 AM

This subject has been discussed previously on this site. Try searching and then come back with a specific question.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#8
In reply to #1

Re: parallal operaion of dg

10/16/2014 4:05 AM

Dear Mr.hisham.i,

I want to supplement to your reply.

In addition to the points referred by you, the following conditions also should be matched for proper load sharing.

1. The SPEED DROOP CHARACTER for the engine should be considered, the Engine Governor plays a major role.

2. The VOLTAGE DROOP CHARACTER to be considered.

The above two points will decide the LOAD SHARING of the DG Sets. The higher the Droop from NO-LOAD to FULL-LOAD, LESSER WILL BE THE LOAD SHARED and ViseVersa.

For example, If one Generator has 6.0% Droop and the other one has 4.0% droop, the SET with 4.0% will share more load than the other set with 6% droop. and it will be in the ratio of 60% and 40%

DHAYANANDHAN.S

Register to Reply
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: Aug 2007
Location: Australia
Posts: 1630
Good Answers: 20
#9
In reply to #8

Re: parallal operaion of dg

10/16/2014 8:54 AM

I am sorry, but I do not agree with your figures you used in explanation of droop for gen sets. Before the advent of electronic governing, hydraulic governors for any gen set that I ever worked on was between 1% - 1,5%, probably closer to 1,25% on the high end of the droop. Main propulsion systems were in the order of 9% droop.

If you had anywhere near 6% droop on a gen set you would have big problems with any electrical equipment that required steady voltages or Hertz, they would be forever tripping out.

__________________
TO BE. or NOT TO BE. That is the question!! The Bard
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5

Re: Parallel Operation Of DG

10/15/2014 1:11 PM

No. It cannot be done. More accurately it should not be done by you until you get properly trained in AC power distribution. There are many more ways to damage you, your diesel generator or the grid than there are correct ways to connect.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User

Join Date: Oct 2014
Posts: 143
Good Answers: 4
#6
In reply to #5

Re: Parallel Operation Of DG

10/15/2014 8:34 PM

It can be done if the genset control system is designed to manage correctly the load sharing among several generators. In modern systems it's mostly done by interconnecting each genset controller using a fielbus or Ethernet.

If the gensets controls are not designed for appropriate load sharing it can't be done as all sorts of problems will occur.

I'd suggest to read some Woodward or Deif literature which can be downloaded freely (Woodward requires a registration but acccess is immediate after registering), especially Woodward features some general documents and white papers.

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#7

Re: Parallel Operation Of DG

10/16/2014 3:19 AM

apart from other factors mentioned you have to ensure load sharing is in proportion to the machine ratings

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#10

Re: Parallel Operation Of DG

10/16/2014 9:36 AM

"Can we operate 2 or more dg(desile genrator) of different rating in parallal."

Theoretically, anything is possible if properly designed.

"what are the condition for parllal operation of DG ?"

The conditions are to have a trained Electrical Engineer design the system that will take in power from the two generators, harmonize them with each other, and provide the combined power out to the load.

Please note that asking vague, open-ended questions on a semi-anonymous forum does NOT count as 'having a trained Electrical Engineer design the system.' You will know you have had a trained EE design the system when you have the design prints in your hand, SIGNED by the EE who is staking his license, reputation, and possibly his freedom, on those plans being correct and accurate.

Once you have gotten the plans, you will need to have an EE (the same one who drew up the plans or another EE, it does not matter) oversee the construction installation and testing of the equipment.

---

If this is for a temporary or small-scale setup, it might be easier and safer to set up the generators completely independent of and isolated from each other, so Generator A supplies power to all the equipment over in section A, on the West side of the camp/village, and Generator B supplies power to the East side. Neither generator is connected to the other in any way, except possibly for them both being hooked up to the same tank of diesel fuel to run off of.

---

Also Welcome to CR4, you will find a lot of helpful advice here. For example, you will notice that the advice you are getting on this question is all shades of 'Your question shows that you do not understand the project you are proposing, you should get a trained, qualified person to design and build the project for you.'

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Power-User

Join Date: Oct 2014
Posts: 143
Good Answers: 4
#11

Re: Parallel Operation Of DG

10/16/2014 1:10 PM

One more detail: if operating several emergency gensets in parallel the required time for a conventional synchronization is not sufficient to meet code requirements. In such case the gensets are started simultaneously and breakers close so common voltage ramping is possible and gensets are forced in "synchronicity" (don't know if it's the correct English word). Of course it must be made sure that if one genset prime mover doesn't start correctly it won't end driven by its generator (see multi-stage reverse power threshold and delay settings and other careful startup alarms inhibition settings).

Of course I only referred to synchronous generators. Gensets with other types of 3-phase AC generators are a joke.

Register to Reply
Register to Reply 11 comments

"Almost" Good Answers: