NEC S.C. Rating

10/18/2014 8:44 AM

Hi Gentlemens,

Can any one tell which standard stands for Short circuit calculation in NEC.

Whether for 10KVA load 25KA S.C. will ok for the panel in NEC.

Need ans for that to close out the doc.

Thanks,

Prabakar

__________________
Prabakar
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: Jun 2014
Posts: 19
Good Answers: 1
#1

Re: NEC S.C. Rating

10/18/2014 11:43 AM

Hi,

I don't know exactly what you're getting at but I guess you're asking whether or not short-time short circuit rating of 25KA is OK at an electrical panel to which a load of 10KVA is connected(??).

Short circuit rating at a panel is not related to the connected load per se but to the fault current that will flow in the event of a short circuit occurring at the panel. This prospective short circuit current is dependent on the capacity of the electricity supply transformer, it's p.u. impedance and the impedance due to cables between the transformer and the point of fault. Having said this, however, rotating electrical machinery downstream of the point of fault do contribute to the prospective fault current.

Regards

Register to Reply Score 1 for Good Answer
Anonymous Poster #1
#2

Re: NEC S.C. Rating

10/18/2014 12:39 PM

I dont think that you can close out the document even if somebody tell you .

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: NEC S.C. Rating

10/18/2014 2:57 PM

The 2014 NFPA 70®: NEC® is the standard/document you need.

Are you really qualified to close this document out, if you don't have a copy of the code?

I think not.

Register to Reply
Associate

Join Date: Jan 2012
Location: chennai.
Posts: 27
#10
In reply to #3

Re: NEC S.C. Rating

10/19/2014 11:49 PM

Thanks i will check it out the NFPA 70.

__________________
Prabakar
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: NEC S.C. Rating

10/18/2014 6:44 PM

Non of the figures given make any sense what so ever. 25KA MPFC where the rated load is only 10KVA

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5
In reply to #4

Re: NEC S.C. Rating

10/18/2014 10:53 PM

Addendum:

25KA MPFC I would associate with somewhere around 1000KVA at 433V.

One hell of a miscalculation if this is to close a document of any standing.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#6

Re: NEC S.C. Rating

10/19/2014 8:48 PM

sprabakar22,

More information will help! What type of document are you trying to close out? Do I assume this is for equipment subject to NEC rules (you are in India and I am unaware of the NEC being the law there)?

Also, as others have said, the S.C. amps is really dependent on the characteristics of the power source, and not the actual equipment load.

If this is a piece of equipment you are working on, for sale, then you can specify that it must be connected to a source circuit with a maximum S.C. amps. Doing this requires you to ensure that all the components will withstand a fault current of that magnitude (or a lower magnitude if downstream of a current-limiting device). After doing this, the customer and installer now assumes the responsibility for supplying the power with the proper S.C. rating.

--John M.

Register to Reply
Associate

Join Date: Jan 2012
Location: chennai.
Posts: 27
#8
In reply to #6

Re: NEC S.C. Rating

10/19/2014 11:30 PM

Dear Mr. John M,

Thanks for the Reply. Not for the India project its for project in Europe. Yes this equipment is subject to NEC Rules.

And to find out the upstream contractor and the person and the supporting docs will be very difficult. The Scope we are having here is very small only stuck with the NEC rules i already checked with the Max assumption of calculation with IEC 60909 its comptiable.

Only thing is need rules for supporting doc. like any previous project r Rules In NEC.

IF i have the supporting doc from NEC rules for short circuit its easy.

Thanks,

Prabakar

__________________
Prabakar
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#11
In reply to #8

Re: NEC S.C. Rating

10/20/2014 2:10 AM

Mr. Prakabar,

The NEC (NFPA 70) is a document that lists the conditions or specifications that a completed electrical project must meet. It does not tell the electrician how to do the work. If includes phrases such as telling you that all equipment must be installed in accordance with the manufacturer's instructions and any instructions or requirements that are part of its listing.

That word "listing" has a special meaning--it is the certification by an independent agency that a component has been tested to perform according to a published standard. In the USA this is often by Underwriters Laboratories (UL) or Factory Mutual (FM). In Europe there are many, but two come to mind (TUV and DIN).

I'm wondering if the information you have been given has confused the need for a UL type of listing with the installation requirements that should comply with the NEC. I worked for a number of years for a UL panel-building shop. We did custom panels. Each one had to be built with materials and methods that complied with the UL requirements. The completed panel was then given a UL label. With this label on the panel, it could go to any customer's location and be installed without any further worry about an inspector's or customer's wondering if the panel was acceptable.

Also, look back to the last part of my earlier post. If the customer has already told you what the available S.C. fault current is, then you must use components that can safely handle or interrupt a short circuit of this magnitude. Many people can confuse the S.C. fault current with the much lower currents that may typically flow during an overload. A fuse or breaker may be rated to open with a downstream overload current of 30 amps, but it has to be built to withstand the stresses and heat produced when a downstream short circuit current of 1000, or 6000, or 12000, or possibly even 35000 amps is momentarily flowing through it.

If your customer has specified the available fault current, then you have to build to handle it. If all that your customer has given is the available S.C. fault current at some point upstream from your equipment, there are programs available via free download that will calculate the fault current at the line lugs on your equipment. To do that, however, you need a number of details (wire size, wire length, conduit type, number of wires in parallel, system voltage, incoming available fault current). If a transformer is there, you need the impedance. If you have equipment nearby with a large motor or a capacitor bank, these will increase the available fault current in the circuit. The process of doing this sort of calculation is not easy.

--John M.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#7

Re: NEC S.C. Rating

10/19/2014 11:04 PM

I am also from Chennai, India. In this part of world, the panel building has become cottage industry. Any body and every body makes panels here without knowing technical importance. Many people here believe in providing 35 kA MCCB for incomer and 25 kA/16kA MCCB for outgoing irrespective of the location these panels in the Electrical distribution system.

May be the person who posted the query is end user or certifying agency for acceptance.

This is how things are happening here. No scientific and systematic approach for any issues. No designers are involved in Electrical systems design ,people simply copy drawings and specifications from other projects without really and deeply going into the details of requirement for the new Project.

This is one of the reasons for major failures like building collapse recently happened here .

Some thoughts came to my mind and I am recording here .

If this continues , even one day there will be major failure in Electrical Installation also.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Associate

Join Date: Jan 2012
Location: chennai.
Posts: 27
#9
In reply to #7

Re: NEC S.C. Rating

10/19/2014 11:48 PM

For your kind information im from chennai but im not working over there.

Dont belive that other side of the person will not be technically sound, If he also from your place.

IF you found panel manufacturing company is not capable in chennai Pull them to court or compalint about them in Association or the Report to them who certified.

__________________
Prabakar
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#12

Re: NEC S.C. Rating

10/26/2014 7:41 AM

In my opinion, NEC does not indicate any way to calculate the short-circuit current the cable

will withstand. The cable cross section area is chosen only according to continuous load [and the overload protection setting. The grounding conductor cross section area is chosen according to ungrounded conductor[s].

However, in art. 240.4 Protection of Conductors it is an informational note:

Informational Note: See ICEA P-32-382-2007 for information

on allowable short-circuit currents for insulated copper and aluminum conductors.

In General Cable SPEC F125/ January, 2010 -see:

http://www.generalcable.com/NR/rdonlyres/D60F2C04-B580-4C2C-A4DC-07B638A1DA02/0/SpecF125.pdf

it is shown how to verify the short-circuit withstand current for copper and aluminum conductors

insulated with XLPE or EPR.

__________________
Julius
Register to Reply
Register to Reply 12 comments

"Almost" Good Answers: