How to determine the size of cables correctly and efficiently?
User-tagged by 2 users
Re: How to choose correct cross-section of cables
10/23/2014 11:46 PM
Refer BS 7671 or manufacturer's literature.
pnaban
Good Answers: 109
10/23/2014 11:51 PM
Calculate it!
10/23/2014 11:51 PM
CR4 ADMIN: Deleted Post
Spam
: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.
Reply Score 2 for Off Topic
10/23/2014 11:56 PM
Don't be a spam maggot.
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member
10/24/2014 12:01 AM
If you dont know....You shouldn't be asking here... Look at your text books or you really shouldn't be playing with these things!
It's all about the Boom! - MythBusters
10/24/2014 12:05 AM
It's a spammer.
10/24/2014 6:33 AM
Consult someone other than you.
10/24/2014 9:26 AM
Are you measuring them or selecting them? Measurement can be done using length measuring tools. Selecting them is something a qualified Electrician does using your national standard.
Good moaning!
Good Answers: 181
Re: How to Choose Correct Cross-Section of Cables
10/24/2014 10:10 AM
Reported
Good Answers: 181
10/25/2014 11:02 AM
But nothings been done about it.
10/24/2014 11:32 AM
What's to calculate or determine. Contact the cable manufacturer with the part number and look up the outer dimension in their catalog.
10/24/2014 11:32 AM
From first principles, following British Standards:
1. Cables serve electrical loads, therefore, cable ampacity Iz shall commensurate with design load current, Ib at least; Therefore, know your design load for a start.
2. Current flow causes voltage drop, Vd, mV per Ampere per unit length of cable - cable impedance may be obtained from cable manufacturers/design codes
Voltage drop shall not be greater than that stated in the design code.
3. Faults may occur so cables shall be protected against overcurrents - In (nominal rating of overcurrent protection device - OCPD)
4. Tabulated cable ampacity, It varies with cable types, and in accordance to factors that affect heat transfer to/from cable - C, correction/adjustment factors, eg.
  • Ca - ambient temperature
  • Cg - grouping of cables
  • Ct - thermal insulation, etc. (refer design code)
Iz = It x C
Select your cable type, method of installation, etc. Refer to tabulated cable ampacity, cable impedance & correction factors
5. Therefore, size your cables as follows:
Iz ≥ In ≥ Ib ;
Vd ≤ max volt drop in design code.
In addition where OCPD affords protection against overload, I2 operating current of overload protection device ≤ 1.45 Iz
Rgds.
10/25/2014 12:25 AM
Select the correct size of the cable considering the following
1)continuous current rating
2)Max. voltage drop permissible
3)short cct rating of the cable checking the system fault level
4)Cable laying condtions
5)max ambient Temperature
6)Single core or Multi Core
7)Earthed cable or unearthed cable
The cable manufacturer's catalogue will provide all the details for the above points
V.Natarajan
Anonymous Poster #2
10/25/2014 6:42 AM
Use the Force. Just as everyone here has done!
Good Answers: 42
10/25/2014 11:01 AM
Usually one has to choose the cable according to a national electric code-NEC, BS, VDE and so on. You may chose the insulation material-as PVC, XLPE EPR and other- and so to limit the conductor maximum permissible temperatures-for continuous load, short time emergency load and short-circuit. You may chose the conductor-usually copper or aluminum. You have to increase the cross section conductor area if the voltage drop-for continuous load or starting-will require, and you have to check if the cable withstand the presumed short-circuit current[you may use IEC 60949 for non-adiabatic phenomenon to increase a bit the withstand current].
But this in case in which the cable cost is your interest.If you are worrying about losses cost in this cable you have a further increasing of the cross section area up to the point where the total cost of the cable and the losses cost is the minimum.
Julius
10/29/2014 5:51 PM
Dear Mr. dhayanandhan, I appreciated your post giving links with much info but leaving the responsibility to do some studying up to the OP. I think what bugs many on this forum is the questions some ask reveal such a lack of understanding of the subject it seems unbelievable that they are really going to get involved in something so far over their head. If all 4 posts today by AP#1 are from the same person I would not want my name (or pseudonym) associated with this person. His/her lack of competence is way past dangerous. It could by criminal and if he/she is charging for his/her work it is dishonest. Leads back to the question of whether AP's should be allowed. -- JHF
Reply Off Topic (Score 4)
10/25/2014 9:12 PM
As I expected, people are again focusing on solely the cross sectional area of the presumably copper conductors without any understanding of where or how these cables will be used. Nothing about any attribute of the insulating material is being considered at all. Nothing about the thermal conductivity of the insulation or media the cable rests in matters one iota to this forum. The difference between continuous, peak, or even fault mode operation parameters cannot come into the conversation. Suspended cable across the Sahel is considered identical to cable submerged under Puget Sound. Nobody ever worries about any loading effects until a fly-back and reflection of a load triples the supply voltage at one point causing repeated insulation breakdown at just one point in a transmission line.
Did I rant about the unknown frequency of the current? No. Frequency! Frequency! Frequency! Duty cycle! Frequency! Skin effect! Frequency!!!
Good Answers: 42
10/26/2014 1:00 AM
You are right to be red Fred. But slow down a bit. The open post asks how to choose the "size" of a cable "correctly and efficiently". Nothing more. Correctly: see the Code- or calculate it if the Code does not answer. Efficiently: the total cost could be involved: installation and losses.
Usually one cannot state the cable raceway but it is dictated. For most of the cases the Code has an answer.
Julius
10/26/2014 10:49 AM
Dear Mr.redfred,
I appreciate your views and I feel, the topics referred by you is not receieving due attention.
What I want to mention is that at least one third or half of the points expressed by you is taken care to extent in my Reply (Refer Post No.16 above) in the 1st Web-Link http://www.electrical-installation.org/enwiki/General_method_for_cable_sizing has 6 sub-topics which takes care for Temp.Rise, Installation method, with several of cables, in Trenches, Cable Trays Earthing Resistance etc.
Perhaps, the PERFECTION which you expect has to (or will) come by PERSEVERANCE and continued efforts, by the ENGINEERS in the days to come.