Electrical Troubleshooting

11/09/2014 12:23 PM

Speed of mud pump don't increases in our ac scr drilling rig (e-1400-xi, BHEL MAKE) --possible reasons and how to approach for the troubleshooting

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: electrical troubleshooting

11/09/2014 12:36 PM

First, identify what type of electric motor (induction, universal, stepping, etc.) you are using. This will identify which electrical parameter should effect the rotational speed.

Second, identify if any intended or accidental mechanical governor mechanism is regulating the speed. (Is something stuck?)

Third, identify if the scr driver for this motor is actually modulating the needed parameter.

Correct the problem accordingly.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Active Contributor

Join Date: Jul 2013
Posts: 15
#3
In reply to #1

Re: electrical troubleshooting

11/09/2014 3:05 PM

Thanks. Mud pump motor is DC motor, speed control is done through motor armature voltage control from 0 to 750 volt DC. The voltage variations is done through Dc module. The dc voltage is generated from ac voltage by the help of controlled scr operation through ac module. Further there is no obstacle to prevent speed increase.

The driller in the Derrick floor uses hand throttle to to vary the speed. I just want to know how to find out the root cause where is the problem for non increasing the speed

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#5
In reply to #3

Re: electrical troubleshooting

11/09/2014 4:38 PM

measure the voltage at the motor! if you have voltage but no pumping you have hydraulic issues

Register to Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#6
In reply to #3

Re: electrical troubleshooting

11/09/2014 6:41 PM

Like other guys advice, measure output of the dc module if it is responsive to the variation of speed you want to have correspondingly. It could be the problem here. Knowing the results you should replace your dc module if voltage does not vary at all.

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#7
In reply to #3

Re: electrical troubleshooting

11/09/2014 8:06 PM

OK. You started down the path I described. It appears that my description of the initial steps were insufficient information for you to complete the rest of the steps. Exciting the armature field alone with a DC current will not cause motor rotation at all to happen. What creates the stator magnetic field? This will determine what kind of motor you have. This will then determine if the frequency of a field or the current of a field will modulate the motor speed.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #3

Re: electrical troubleshooting

11/10/2014 6:57 AM

There. All the information needed to fix it was to hand in the first place. If a competent Maintenance Technician is not on-board locally, then hire someone.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Dec 2013
Posts: 10
#13
In reply to #1

Re: electrical troubleshooting

11/10/2014 11:51 PM

this is correct, i agree!!!

Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#2

Re: electrical troubleshooting

11/09/2014 1:53 PM

maybe its plugged with mud

Register to Reply
Power-User

Join Date: Oct 2014
Posts: 143
Good Answers: 4
#4

Re: Electrical Troubleshooting

11/09/2014 3:51 PM

Pelase first check the voltage and current of both the armature and field. Those can usually be read from the drive display but it's also a good idea to measure them using a DC (or TRMS AC which measures down to DC) clamp amperemeter (regular clamp meters only measure AC).

Also check the rating plate of the motor.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#8

Re: Electrical Troubleshooting

11/10/2014 3:04 AM

Dear Mr.dks,

You have not indicated the Type of Motor. If it is DC MOTOR, there again whether the field is in series or shunt, the problem is with main armature, or field winding.

If it is VFD there some thing related to TORQUE issue.

If it is AC conventional motor, the capacity of the motor is insufficient.

Pl. check and inform to this Forum.

DHAYANANDHAN.S

Register to Reply Score 1 for Off Topic
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#10

Re: Electrical Troubleshooting

11/10/2014 7:12 AM

First I would check the driller control. Most pots are mechanical and can wear out. Simple check of the input voltage change as the driller adjust the pot.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Power-User

Join Date: Oct 2014
Posts: 143
Good Answers: 4
#11

Re: Electrical Troubleshooting

11/10/2014 5:02 PM

For testing purposes, if safety requirements are met, it should be possible to control the DC drive using the local control panel (usually provided and mounted on the drive or sometimes on the door).

But you require the drive documentation and some basic knowldedge about DC drives. Unless it's a really old or basic DC drive or if the OEM has locked the panel or if the drive control panel hasn't been supplied. It will also allow you to check motor currents and voltages as well analog I/O values and digital I/O statuses.

Be aware that running motors using the drive control panel must be done very carefully as some safety systems may be bypassed (depends on the control design). For many non-servo applications, which by definition are not extremely dynamic by definition, it's possible to run carefully manually for testing purposes (if required set up temporarily an additional Emergency Stop pushbutton box). In case of running the DC drive in a regenerative quadrant avoid switching off the grid power unless absolutely required as it can blow fuses or even damage hardware.

Which DC drive model do you use?

Register to Reply
3
Participant

Join Date: Nov 2014
Location: TEXAS
Posts: 1
Good Answers: 1
#12

Re: Electrical Troubleshooting

11/10/2014 8:17 PM

Hey brother,

try this:

Check the "Speed control" circuit at the SCR control.

If you have appropriate signals there.

Check at the Drillers control.

If you have the appropriate signal there.

Check the output of the SCR control to the motor (with the motor connected).

Read the armature VDC at the SCR control and check for variability in proper response to the selected speed at the Driller control.

If the armature voltage is not varying proportional to the speed control setting.

Remove the motor armature leads. and connect (6) 130 V incandescent lamps in series across the armature circuit and check for varying intensity of light output through the series circuit.

I would advise NOT setting at the maximum setting.

If the lights work, but the motor doesn't.

It's in the motor.

If the lights don't vary, it's your SCR control.

If your Field circuit fails the motor will try to run away with itself with no speed control.

Without the field circuit through the motor, there is no counter EMF to offset the rotation of the armature.

Hope this helps.

HAPPY DRILING

__________________
OLD DRILLER, OLD ELECTRICIAN, (MAYBE) JUST OLD
Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: Jul 2013
Posts: 15
#15
In reply to #12

Re: Electrical Troubleshooting

01/31/2015 11:02 AM

hello Drilldog brother, Due to various operation problem I could not reply in time. with regards to problem, expert came checked , found problem lies in the DC module, replaced the module and tested OK- all this was done in a hurry, so I did not get the clue. Anyway problem resolved. Thanks for your very good reply anyway.

But I need your help further. The various step you had given, kindly expand a little bit. For example you said "Check the "Speed control" circuit at the SCR control" -- how to do this , please tell me the steps if it is OK with you

regards

Register to Reply
Active Contributor

Join Date: Jul 2013
Posts: 15
#16
In reply to #12

Re: Electrical Troubleshooting

03/27/2015 2:04 AM

HELLO SIR, THIS IS A BELATED RESPONSE FROM MY SIDE. I REGRET FOR THAT. YOU HAVE GIVEN A GREAT EXPLANATION TO SOLUTION OF MU PROBLEM. BUT BEING NEW IN THIS FIELD I AM UNABLE TO DO THE FOLLOWINGS :-

(1) How to Check the "Speed control" circuit at the SCR control. hat should be its input and output.

(2) also tell me how to Check at the Drillers control and what is the input and output of the driller's control panel

regards

dks

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#14

Re: Electrical Troubleshooting

11/11/2014 9:30 AM

I have no practical experience with high pressure mud pumps. I have only theoretical suppositions.

I think it is a series dc motor. In my opinion, two problems could be: control problem [overspeed control limited] or short-circuit in excitation pole coil. For general information see:

http://www.iaeng.org/publication/IMECS2012/IMECS2012_pp1052-1054.pdf

__________________
Julius
Register to Reply
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (1); Apol (1); dhayanandhan (1); dks (3); DRILLDOG (1); Fredski (2); Noudge79 (1); ozzb (1); Plimos (2); PWSlack (1); redfred (2)