Electrical Grounding

11/17/2014 6:39 AM

Is there special MEGGER (Insulation tester) available for hazardous and intrinsically safe areas?

Register to Reply
Pathfinder Tags: megger for hazardous area
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: electrical grounding

11/17/2014 7:10 AM

There is no such thing as an intrinsically safe area.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#5
In reply to #1

Re: electrical grounding

11/17/2014 8:46 AM

its safe in a text book but once you enter the real world all bets are off

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #1

Re: electrical grounding

11/17/2014 8:56 AM

Even a relatively safe area can be rendered hazardous by the untrained and unknowing.

OP needs some competent assistance, by someone close by.

Register to Reply
Commentator

Join Date: Oct 2013
Posts: 62
Good Answers: 3
#15
In reply to #6

Re: electrical grounding

11/18/2014 8:20 AM

Maybe I need to step back a little from my position about forum replies after seeing this post.

Register to Reply
Power-User

Join Date: Oct 2014
Posts: 143
Good Answers: 4
#2

Re: electrical grounding

11/17/2014 8:10 AM

LOL Yeah, one which guarantees intrinsically safe sparks after the "ia" Zener barrier.

Are you in charge of the ATEX compliance of your plant?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: electrical grounding

11/17/2014 8:24 AM

Wouldn't that be something.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #2

Re: electrical grounding

11/17/2014 8:26 AM

Want a laugh?

Look back at our friend's history.

Some of his questions are a real hoot!

Register to Reply Off Topic (Score 5)
3
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#7

Re: Electrical Grounding

11/17/2014 1:24 PM

No, because the Insulation tester test energy is higher than the intrinsically safe limits.

__________________
jack of all trades
Register to Reply Good Answer (Score 3)
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#8
In reply to #7

Re: Electrical Grounding

11/17/2014 5:33 PM

...and would therefore blow the fuse inside the isolation barrier...

__________________
Good moaning!
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#10
In reply to #8

Re: Electrical Grounding

11/17/2014 7:15 PM

Not necessarily, as unlike your standard intrinsically safe barriers equipped with fuses and limiting resistors intrinsically safe circuits can be protected by electronics alone that limit the current, voltage and power to safe levels. Certified intrinsically safe galvanic isolators are an example of this.

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#9

Re: Electrical Grounding

11/17/2014 5:39 PM

Are you serious? What on earth (pun intended) are you trying to do? Cause an explosion or something?

__________________
Good moaning!
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#11

Re: Electrical Grounding

11/17/2014 10:53 PM

Garuda777,

As I hope you know, all wiring within a hazardous/classified area must be installed in a manner that prevents it from starting a fire or explosion in that area. Intrinsically safe circuits are designed to limit the available circuit energy to levels that are too low to cause ignition. Circuit components have to be selected so they are incapable of temperatures that would exceed the ignition temperature of the explosive or flammable materials in that area (whether dusts, vapors, liquids, etc.) Wiring devices must be selected and installed so that any explosion or fire that starts within them cannot rupture the enclosure and any hot gases or vapors are cooled to a temperature below the atmosphere's ignition temperature as they vent out of the enclosure.

That being said, I hope you have read the posts that tell you a megohmmeter cannot be used on an intrinsically safe circuit. Any meter with a battery or other power source, used within the classified area, has the real risk of causing a fire/explosion. A megohmmeter used outside the classified area on a circuit that enters the classified area should be OK as long as the circuit's wiring in the area complies fully with code rules.

--JMM

Register to Reply
Power-User

Join Date: Oct 2014
Posts: 143
Good Answers: 4
#12

Re: Electrical Grounding

11/17/2014 11:27 PM

Indeed there is a limited choice of expensive ATEX measuring instruments like multimeters, calibrators,... but for sure no Megger. Also when working in dangerous zones it's by far not only about the electrical devices, it goes much further and requires to follow extremely strict rules which include the use appropriate equipment, clothing, PSA, etc. and to not carry anything which could cause sparks, even when falling. Appropriate training is an absolute must.

Some posters, me included, were obviously when replying kidding because the OP's question is close to asking if there are ATEX flame throwers available.

Register to Reply
Power-User

Join Date: Apr 2007
Posts: 273
Good Answers: 12
#13

Re: Electrical Grounding

11/17/2014 11:37 PM

Not intrinsically safe, but there are devices that are designed to test insulation in motors and generators at their normal operating voltage. Current is limited to a very low value. These things are designed for in-plant use.

http://www.megalert.com/index-2.html

Register to Reply
Commentator

Join Date: Nov 2007
Location: Calcutta
Posts: 87
#14

Re: Electrical Grounding

11/18/2014 1:40 AM

I think you want to know if there is any intrinsically safe Megger (Insulation Tester) for hazardous area like in coal mines etc .

If that is so , then there is intrinsically safe Insulation Testers certified for use in Mines where current passing thru the circuit is less than 10mA.There are other features also which make such instruments safe for areas where there are ignitable gasses like in mines .

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#16

Re: Electrical Grounding

11/18/2014 10:02 AM

There are Megohm meters such as the Fluke 1507 tester that are offered by several manufacturers all of which are capable of insulation testing at voltage values of 50 volts which will not damage the conductors used in intrinsically safe circuitry.

A search for megohm meters at Dranitz, Fluke, Ideal, etc. websites will reveal all that is available.

If you need technical help contact your favorite test meter sales rep and they will answer any questions or concerns you may have as well as recommend the correct meter for your test application.

Most wiring and cables used today are rated for a minimum of 300V which is well above the 50V meter test voltage.

You must first determine the maximum voltage rating of each and every conductor/wire being tested then select the appropriate tester.

You must determine the operating voltage of the circuit being tested.

All wiring and cables that are going to be tested must be de-energized and disconnected from the circuit terminals at both ends before and during testing.

Be sure that the applied meter test voltage does not exceed the conductor insulation voltage rating.

(Failure to do this can cause severe damage to the equipment and/or malfunction of the circuitry.)

Performing this type of testing in an energized cabinet is hazardous and can be fatal so be sure to properly isolate, de-energize, and protect all wiring and terminals from inadvertent contact with test personnel.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#18
In reply to #16

Re: Electrical Grounding

11/18/2014 2:10 PM

What happens when the insulation cannot withstand the applied test voltage?

__________________
Good moaning!
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#17

Re: Electrical Grounding

11/18/2014 10:16 AM

In order to illuminate the shady areas of your knowledge,here is a thin ray of light:

Read and learn.

https://www.instrumart.com/assets/Megger-insulationtester.pdf

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Anonymous Poster #1
#19

Re: Electrical Grounding

11/18/2014 4:40 PM
Register to Reply
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); arunavamukerji (1); Crabtree (3); Fredski (1); HiTekRedNek (1); jack of all trades (2); jmueller (1); lyn (2); Plimos (2); PWSlack (2); roeblinggrid (1); SHOCKHISCAN (1); steve45 (1)