HT Cable and HVAC Ducts

11/24/2014 5:26 AM

Hello All,

I want to know whether any IS standard prohibits laying HT cable trays below HVAC ducts. Or is it convention that all HT cables should be above among, ducts, LT cables, Pipes etc.

regards'

Jithin James

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: HT Cable and HVAC Ducts

11/24/2014 8:36 AM

below or attached to the underside?

Register to Reply
Member

Join Date: Jul 2014
Posts: 9
#4
In reply to #1

Re: HT Cable and HVAC Ducts

11/25/2014 12:28 AM

It's in a cable tray underneath the HVAC duct, and it doesnt touch, but the clearance is shown very minimum, around 100 mm.

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#2

Re: HT Cable and HVAC Ducts

11/24/2014 9:40 AM

It depends on the application and local codes.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3

Re: HT Cable and HVAC Ducts

11/25/2014 12:25 AM

Ask the Consultant to give a sketch.

__________________
pnaban
Register to Reply
Member

Join Date: Jul 2014
Posts: 9
#5
In reply to #3

Re: HT Cable and HVAC Ducts

11/25/2014 12:32 AM

The consultant has already given a sketch, we are bit skeptical on that , hence the doubt!

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#6
In reply to #5

Re: HT Cable and HVAC Ducts

11/25/2014 1:46 AM

Could you post here?.

__________________
pnaban
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#7

Re: HT Cable and HVAC Ducts

11/25/2014 10:19 AM

Suppose the skin of the HVAC duct is non-insulated and below dew point with the HT tray below it. Do you really want conductive water dripping on that? Do you want the tray supporting the HT to corrode? Are you serious? This is a complete no brainer.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Jun 2011
Location: Mossel Bay, SA
Posts: 777
Good Answers: 21
#8

Re: HT Cable and HVAC Ducts

11/26/2014 1:51 AM

I think you have loosely used the descriptor "IS".

The question posed has nothing to do with IS as understood in Electrical Theory.

IS has to do with apparatus capable of generating sufficient energy under fault conditions to ignite a surrounding flammable/ explosive atmospere.

Perhaps there is another meaning for IS (other than Intrinsic Safety) that I am too dim to latch onto , on this otherwise fine day ?

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#9
In reply to #8

Re: HT Cable and HVAC Ducts

11/26/2014 10:52 AM

Maybe meant short hand for "International Standard". Usually referred to as ISO?

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Jun 2011
Location: Mossel Bay, SA
Posts: 777
Good Answers: 21
#12
In reply to #9

Re: HT Cable and HVAC Ducts

11/27/2014 1:26 AM

Aaah..there you go... I stand corrected, thank you!

The years are starting to haul me in.

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#10

Re: HT Cable and HVAC Ducts

11/26/2014 2:00 PM

IEEE Std 525-1992, IEEE Guide for the Design and Installation of Cable Systems in Substations.

ch.12.3.2 Tray system design

  1. In general, vertical spacing for cable trays should be 12 in (30.5 cm), measured from the bottom of the upper tray to the top of the lower tray. A minimum clearance of 9 in (22.9 cm) should be maintained between the top of a tray and beams, piping, etc., to facilitate installation of cables in the tray.
  2. Cables installed in stacked cable trays should be arranged by descending voltage levels, with the higher voltage at the top.

That means-if "etc." =ventilation duct also-it is permissible to install a cable tray for medium voltage cables below the duct if the clearance of 9 inches is provided.

__________________
Julius
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#11
In reply to #10

Re: HT Cable and HVAC Ducts

11/26/2014 9:51 PM

when buried in earth does the same rule apply?.

__________________
pnaban
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#13
In reply to #11

Re: HT Cable and HVAC Ducts

11/29/2014 4:52 AM

For underground installation: in NESC Rule 353 and 354 minimum radial separation required it is 300 mm [12 inches].However, adequate vertical separation shall be maintained to permit access to and maintenance of either facility without damage to the other cables.

__________________
Julius
Register to Reply
Member

Join Date: Jul 2014
Posts: 9
#14
In reply to #10

Re: HT Cable and HVAC Ducts

11/29/2014 5:04 AM

Thank you Sir!

Register to Reply