Earthing Calculations

12/05/2014 12:03 AM

Meshed electrodes are generally designed as a grid of strips placed horizontally in the ground; however, the resistance to earth of a meshed earth electrode and the resistance to earth of a strip earth electrode are different from each other.

Why is the formula used to calculate the resistance to earth of a meshed earth electrode different from the formula to calculate the resistance to earth of a strip earth electrod, while meshed earh electrodes are also basically strip earth electrodes?

Thanks in advanced.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#1

Re: Earthing Calculations

12/05/2014 12:51 AM
__________________
Common Sense Dictates
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Earthing Calculations

12/05/2014 8:22 AM

Different shapes, different formulas. How not?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#3

Re: Earthing Calculations

12/06/2014 12:00 PM

The single electrode formula is calculated starting with a differential equation

See [for instance]:

http://admin.copperalliance.eu/docs/librariesprovider5/power-quality-and-utilisation-guide/631-earthing-systems-fundamentals-of-calculation.pdf?sfvrsn=6&sfvrsn=6

or IEEE 80/1986 [not IEEE 80/2000].

But the area ground resistance started from round plate formula-also single electrode-and further it was developed experimentally.

__________________
Julius
Register to Reply
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#4

Re: Earthing Calculations

12/06/2014 12:47 PM

Single conductor earths or grounding rods or strips perform quite differently from grids. The use of a grid is normally only to retain a ground in a given area to maintain the same potential. While they will provide some grounding, it is much more limited. The same way a vertical ground rod will provide much more grounding than the same rod placed horizontally in the ground. The reason if you study the theory in depth is that the rod, strip or grid is making contact with only a small portion of the earth which really has poor surface conduction. The radiant lines of energy go out quite a ways and the resultant resistance can be quite low. One test that shows the difference in how the conduction works in the earth is to drive 3 ground rods (set A) 1 foot apart and 3 more ground rods (set B) 10 feet apart. Measure the resistance of one single rod, then compare that to set A and you will find that A is not much improvement, but compare it with B and you will find a really, really large improvement. From this you should deduce how a grid and a strip or vertical rod should all behave differently and have different formulas.

All that being said, the earth is not a homogeneous item and varies a lot, even in the same location, so formulas are only a starting point, and a proper ground test is essential to providing a good earth or ground connection.

Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

4wsilver (1); 7anoter4 (1); IdeaSmith (1); Tornado (1)

Previous in Forum: DC Current Applied to the Temple Increases IQ   Next in Forum: Changes in Lighting Products

Advertisement