Unbalance Power Factor at No Load on 3-Phase Motor

12/06/2014 6:58 PM

I measured 3-phase induction motor 45 kW , 4-pole , 400 V / 50 Hz in condition at no load

The result for each phase is:

voltages:

399,86 V

399,92 V

399,83 V

phase currents

16,1 A

15,7 A

15,8 A

input powers

252,6 W

194,7 W

334,5 W

power factors

0,0378

0,0298

0,0509

I don't understand a big discrepancy in power factor for each phase when voltages and currents are practically symmetrical .

What can be reason for it ?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#1

Re: unbalance power factor at no load on 3-phase motor

12/06/2014 8:33 PM

At so low power factors, the slightest difference between each phase armature Q factor, usually caused by tiny core inconsistencies, makes a major power consumption difference, i.e. any, even perfectly acceptable differences between phases on motor construction are exaggerated. But that is not a sign of bad quality or any motor problem whatsoever. The figures you give are those of a top quality motor. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Participant

Join Date: Dec 2014
Posts: 3
#6
In reply to #1

Re: unbalance power factor at no load on 3-phase motor

12/07/2014 2:11 AM

Thank you for your answer. Can you write more about "tiny core inconsistencies" ?

Is it possible that here can be influence a little air-gap excentricity (static / dynamic ? ) or asymmetrical winding too ?

Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#11
In reply to #6

Re: unbalance power factor at no load on 3-phase motor

12/08/2014 9:37 AM

Yes, that kind of inconsistencies I'm talking about. You can't expect all three winding sets and cores to be geometrically and electrically identical, actually, on some winding schemes, this is totally impossible for obvious geometric reasons. An idling motor on normal grid (not VFD, there can be differences there) draws enough current (out of phase of course, but still high enough) for those differences to show, etc etc. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: unbalance power factor at no load on 3-phase motor

12/06/2014 8:35 PM

Why do you care what the power factor is at no load?

Register to Reply
Participant

Join Date: Dec 2014
Posts: 3
#7
In reply to #2

Re: unbalance power factor at no load on 3-phase motor

12/07/2014 2:15 AM

I think that no load test is quality index for each motor.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#12
In reply to #7

Re: unbalance power factor at no load on 3-phase motor

12/08/2014 2:46 PM

Oh. Nothing to do with single-phase loads connected elsewhere on the supply, then?

__________________
Good moaning!
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#3

Re: unbalance power factor at no load on 3-phase motor

12/06/2014 10:40 PM

I would compare your deviations to the full power draw when mechanically loaded and not unloaded. At this low of a power factor a simple quantizing error of one LSB can appear as a huge error.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4

Re: Unbalance Power Factor at No Load on 3-Phase Motor

12/07/2014 12:33 AM

Did you record PQ and pf at full load?.

__________________
pnaban
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Unbalance Power Factor at No Load on 3-Phase Motor

12/07/2014 12:34 AM

Multimeters are such nice little toys. Digital GIGO in some cases.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#8

Re: Unbalance Power Factor at No Load on 3-Phase Motor

12/07/2014 2:29 AM

If motor manufacturer give on name plate the current,pf,noise,vibration,losses etc both at no-load and at full load it would be useful to test after repairs.

__________________
pnaban
Register to Reply
Power-User
United Kingdom - Member - Not quite retired Member

Join Date: Aug 2012
Location: Up an araucaria araucana tree, South London, United Kingdom
Posts: 132
Good Answers: 7
#9

Re: Unbalance Power Factor at No Load on 3-Phase Motor

12/08/2014 4:01 AM

How are you measuring power?

Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#10

Re: Unbalance Power Factor at No Load on 3-Phase Motor

12/08/2014 8:34 AM

Your meter readings might show equal values but in fact they do not occur at the same instant of time.

If you used an oscilloscope you would see this.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#13

Re: Unbalance Power Factor at No Load on 3-Phase Motor

12/11/2014 5:14 AM

In my opinion, the stress exercised differently on a part of magnetic core -mainly in stator teeth region, I think- it could cause a change in core properties. Losses could be different for the same magnetic flux density in different parts of the core.

__________________
Julius
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#14
In reply to #13

Re: Unbalance Power Factor at No Load on 3-Phase Motor

12/11/2014 5:39 AM

If this was observed after rewinding burnt motor winding,due to unbalanced heating of windings in 3phases damaged/overheated core or rotor rotor bars can result in unbalanced noload current

__________________
pnaban
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#15
In reply to #14

Re: Unbalance Power Factor at No Load on 3-Phase Motor

12/18/2014 1:56 PM

At the beginning no-one measured the no-load losses-it is not an usual test -but the no-load currents. Since Rfe is big [here 300-500 ohm] and Xm is small [25 ohm] the common impedance will be equal to Xm [approx.].

And then, the current depends almost on Xm. Xm=2*pi()*frq*L The inductance L is almost zero in laminate and is concentrated in the gap. As the gap is the same for al phases [if the rotor moves] the Xm is the same in all phases [more or less].And, in conclusion, the absolute value of the currents will be the same in all phases [if no winding issue occurred].

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#16
In reply to #15

Re: Unbalance Power Factor at No Load on 3-Phase Motor

12/18/2014 3:04 PM

Actually, the magnetic field [intensity] is small in the laminate and elevated in the gap. The the magnetomotive force [ H*leng] is concentrated in the gap then, and the inductance depends on it.

__________________
Julius
Register to Reply
Register to Reply 16 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (3); Alcyon (2); Crabtree (1); Geoffrey36 (1); horace40 (1); lyn (1); pnaban (3); redfred (1); SimpleMind (2); Tornado (1)

Previous in Forum: High Voltage S/d of Generator Due to Mist   Next in Forum: Remember Me? The "Iceberg In Fukushima" Guy?

Advertisement