Measuring the Online Conductivity of Condensate Water for Boiler

01/07/2015 1:05 AM

please help me for right option to choosing the type of conductivity transmitter/ meter for condesate water line fron condensate tank to deareator tank of boiler the transmitter should have 4~20mA output signal for control, also suggest for installation of this sensor.

__________________
with best regards
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: measuring the on-line conductivity of condensate water for boiler

01/07/2015 2:48 AM

Learn how to use a search engine!

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: measuring the on-line conductivity of condensate water for boiler

01/07/2015 3:07 AM

Please supply details of the application and a list of the options under consideration.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Jan 2015
Location: pakistan
Posts: 13
#3
In reply to #2

Re: measuring the on-line conductivity of condensate water for boiler

01/07/2015 4:23 AM

i m working in a sugar mill, you know that in sugar process the steam circuit is a closed circuit, we use steam pressure for running the steam turbines for power generation and mills roller driving, and we are using exhaust steam of turbine for process house, like evaporaters pan stations and then the condensate of steam use for condensate water as feed water for boiler. there was risk of leakage of cane juice in evaporaters pains and juice heaters tube, so for safety for condensate contamination we need to install conductivity sensor on 6'' line of condensate water that was going in deareator tank of boiler having pressure 1.5 to 3bar and temperature 95C to 110C, so please suggest the right sensor and installation place, i also check through search engine, but needs more and practical information of experts

__________________
with best regards
Register to Reply
Guru

Join Date: Aug 2008
Location: England & Ireland
Posts: 1063
Good Answers: 61
#5
In reply to #3

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/07/2015 6:31 AM

I don't understand how measuring the conductivity of your condensate water will tell you if you have picked up cane juice contamination. Surely the juice compounds are non-ionic species that will not affect the conductivity of the condensate? Unless of course there are some ionic species present in the juice that can act as a "tracer." More information needed!

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#19
In reply to #3

Re: measuring the on-line conductivity of condensate water for boiler

01/08/2015 2:18 PM

You might also want to invest in a controlled sample cooler for that conductivity, as your temperature is rather high, and can damage some probes from certain vendors. Sample conditioning modules are usually set up with an overtemp switch to block sample flow when the temp is too high to continue. Swan makes hands down the best online water measurement/analysis instrumentation for the plant environment, and since it is Swiss manufacturing, they guarantee product support for 10 years beyond the announced obsolete date of the model. You will not find that kind of support for anything American, much less Japanese.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Active Contributor

Join Date: Jan 2015
Location: pakistan
Posts: 13
#4

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/07/2015 5:42 AM

please note the 6'' line pressure of condensate water is 1.5 bar to 3 bar and temperature is 95 to 110C,

__________________
with best regards
Register to Reply
2
Member

Join Date: Jan 2015
Posts: 5
Good Answers: 1
#6

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/07/2015 7:48 AM

Believe it : Sugar in return condensate from Evaporator station has conductivity .

TDS = non specific. Turbine Exhaust steam is used to evaporate excess water from the original mixed juice ( +/- 12 to 14 Brix) to a concentration of around 68Brix for further treatment in the vacuum pan station.

If there is a tube leak in the Evap station, then it is immediately seen in the condensate return to the boiler feedwater storage tank.

I used Flame Photometers to provide ONLY sugar detection ( as Conductivity, although a good guide, is non specific).

The question of equipment to be used : any reliable toroidal ( in preference to amperometric) system can be used. Mail me if you want a complete system design. I do not charge for on-line consulting.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Aug 2008
Location: England & Ireland
Posts: 1063
Good Answers: 61
#7
In reply to #6

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/07/2015 5:12 PM

"Sugar in return condensate from Evaporator station has conductivity."

Why?

Register to Reply
Member

Join Date: Jan 2015
Posts: 5
Good Answers: 1
#10
In reply to #7

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/07/2015 11:14 PM

Because sugar in solution certain impurities that are conductive and allow the passage of electricity ( Conductivity, if you read the theory and understand it, depends on any free ions in a solution to carry current)

If you can't accept this, please do some Chemistry / electricity research

Register to Reply
Guru

Join Date: Aug 2008
Location: England & Ireland
Posts: 1063
Good Answers: 61
#14
In reply to #10

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/08/2015 4:42 AM

Gosh, thanks for the lecture. FYI I have a B.Sc. in Chemistry and relevant to this question, spent 2 years working on the electrodeposition of aqueous polymer solutions and 2 years research on H2/O2 fuel cells and Zn/Air batteries. So please feel free to fill me in on why a non-electrolyte such as sugar, conducts electricity. What are these "impurities" and from where do they arise? Thanks.

Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#15
In reply to #14

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/08/2015 9:35 AM

Just a shot in the dark here, but since:

  1. cane sugar is extracted from sugar cane, and
  2. sugar cane is a plant, which during its growing phase is a living organism, and
  3. living organisms have biological processes, and
  4. biological processes frequently rely on ion transfers.

Would it not make sense to find some of the ion carriers, such as NaCl, as trace contaminants within the 'cane sap'/cane syrup?

I don't mean to step on any toes, however, the curriculum vitae you provided shows a strong affinity for 'inorganic' chemistry (polymers may or may not be 'organic' in the chemical sense, that is, containing at least one carbon atom, but except for a few cases would polymers be involved in biology) and the situations you have been working in are, for all intents and purposes 'spotlessly clean.' Biology, on the other hand, is very dirty and messy, and you're always dealing with contaminants. 'Pure' blood plasma is plasma with a parts per ml count of red blood cells, white blood cells, platelets, etc below the 'threshold value' where they are considered enough to provoke an immune reaction from the recipient, 'pure' cane syrup still has bits of the cells from the sugar cane that was mashed up/shredded to extract the syrup, and you do not want to know how much rat butt meat is allowed in a hot dog by the FDA. (even kosher hot dogs may contain small amounts of rat, which is non-kosher, simply because it's too small to detect with the current methods, and the poor shlamiel who was running the grinder turned his back on the process because he had to sneeze, and while avoiding contaminating the meat with his own biology, didn't see the one rat who fell off the overhead rafter into the machine.)

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Guru

Join Date: Aug 2008
Location: England & Ireland
Posts: 1063
Good Answers: 61
#16
In reply to #15

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/08/2015 12:55 PM

There may well be ionic contaminants in impure sugar - that's what I'm trying to find out. As for your rat rant - the mind boggles.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#21
In reply to #16

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/08/2015 3:48 PM

I may have gone a little over-the-top with the hot dog analogy.

That's one problem with growing up in the Theatre, I can never be sure when I'm being ... (goes into a Hamlet 'alas, poor Yorric' pose) ... overly dramatic in conversation.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#25
In reply to #21

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/08/2015 5:03 PM

rat butt meat? Really. That is just beyond the pail. I thought we were talking condensate, not I gotta unvisualize rat butt meat.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#31
In reply to #25

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/09/2015 11:06 AM

Okay, I did go too far into hyperbole there, I apologize.

Minor quibble, though, the term is 'beyond the pale' not pail.

http://en.wikipedia.org/wiki/Beyond_the_Pale

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Member

Join Date: Jan 2015
Posts: 5
Good Answers: 1
#17
In reply to #14

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/08/2015 1:30 PM

So when are you going to complete your "education"?

You hold a Bsc degree in Chemistry , right?

Just so you are in the frame, so to speak ( I never like to quote my stats) I hold 2 x Doctor of Philosophy Degrees: Engineering Instrumentation and Engineering Management. I also have an Mba in project management and a 2nd Mba in International Business Management. These are irrelevant to the, 'hands on' 30 years' experience in Sugar Milling Instrumentation out of a total of a 50 years in C&I. ( Boilers, powerplant, analyzers etc etc are my fields of activity.

I have designed , implemented and commissioned sugar mill Instrumentation in several countries using Stand alone Micro-processor, PLC and DCS systems.

I lecture in some 8 countries here in Africa ( OK so you live in the "real" world)and all course compilation and presentation I do myself.

Your whining about Chemistry when you have virtually NO practical field experience is embarrassing to your image. Do some honest to God research into the science of Sugar Milling and then ask some relevant questions.

Regarding the furtherment of your 'career' : My first suggestion to you would be to take a course in Humility. When you are done with this,perhaps you will have learned that respect is earned, not some piece of paper you so glibly brag about.

Sorry, but you asked for this.

Register to Reply
Guru

Join Date: Aug 2008
Location: England & Ireland
Posts: 1063
Good Answers: 61
#20
In reply to #17

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/08/2015 2:52 PM

I'm 73 years old and retired so will not be furthering my formal education, but thanks for your suggestion. I'm not going to give you my life story, but they include water treatment chemical sales and service, x-ray, NMR, IR and optical emission spectroscopy sales and marketing. I find your remarks rude and offensive and have reported them to CR4 Management. As a newcomer to CR4 I don't think throwing your weight around will make you many friends.

P.S. You still haven't answered my question about why sugar solutions have a conductivity.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#22
In reply to #17

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/08/2015 4:09 PM

Speaking of humility, and earning respect, you might not want to com on so strong with your early posts. You may be internationally recognized as a genius and miracle worker, but until we get to know you better here, all we have is the tone of your posts to go on for determing what sort of personality you have. Are you sure you want to present yourself as a Charls Emmerson Winchester III sort of character?

I think I waited until I was about a hundred comments in before I started wisecracking and letting my slightly off-center sense of humor show. By then people had gotten used to me, and I had a GA or two under my belt, so I felt more comfortable with saying things that some people might take as grandstanding or offensive. I had already shown that I was able to 'play well' with the other people here, so I could risk hurting feelings since I knew the people here would see my apologies were sincere.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#33
In reply to #22

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/09/2015 11:16 AM

And to the person who gave me a GA for this:

Thank you, I try my best to be helpful and informative here, and baring that, I at least try to be entertaining and to ask questions that will help those who know more than I on a subject to work out the answers.

It's a team effort, and deep down inside we're all just fellow nerds (To some degree or another, I literally cannot conceive on anyone with no trace of nerdiness ever being attracted to Engineering, No cheerleader or athlete would look at a motor, watch or electronic gizmo and say 'Cool, I wonder how it works,' they'd be too busy 'being popular' to think about anything else.), I do what I can to help.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#23
In reply to #17

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/08/2015 4:15 PM

Well, at the risk of being shunned because I have no formal degree (though considerable time in several different colleges and 45 years in various industries) I'll have to go with energyconversion on two counts.

1. A solution of pure water and sugar will not, by themselves, conduct electricity.

2. CVs don't mean much here. A track record with some history behind it is worth far more to the members. Manners will help, although I have none and make no excuses for that.

3. Newcomers should show a little deference to established members when first entering the murky waters of a new forum. They'll find the swimming more pleasant later on.

I know, that's 3. But, who's counting?

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#24
In reply to #23

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/08/2015 4:22 PM

"Manners will help, although I have none and make no excuses for that."

You've got more manners than you realize. You may be bluntly honest, but you don't go around insulting and offending people just for kicks. I'd give some recent examples of 'people with no manners here' that I found, but those people have had all their threads and posts deleted, so the examples are gone.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#26
In reply to #23

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/08/2015 5:07 PM

But we are not mixing pure water with "pure" sugar here now are we? I was under the impression the OP was talking about a sugar mill, cane juice, etc. Cane juice does include some electrolytes.

OP needs to get an auto-ranging transmitter with at least one output loop, and probably a couple of output relays to alert operators when things are not right. There is a learning curve for his process, and it is up to him to get on the horsey and ride it. Not us.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#27
In reply to #26

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/08/2015 5:38 PM

I quote the brash newcomer, "Sugar in return condensate from Evaporator station has conductivity"

Well, show me your sugar ions and I'll be quiet.

IF said newcomer had said, "condensate from Evaporator station has conductivity" I'd never have waded into this cesspool of ignorance, and arrogance.

First, the OP is ignorant in so many ways. No knowledge of the processes involved. no knowledge of the instrumentation required to test the condensate for conductivity, nor any idea of where or how to install the equipment if it dropped into his lap.

Then there's our collective arrogance of ignoring the fundamental question, as lame as it is, and verbally dueling over things so far above the OP's head as to be in orbit around the sun.

OP doesn't have a clue about any of this.

How he got this job in the first place would make interesting reading.

Register to Reply Good Answer (Score 2)
2
Guru

Join Date: Aug 2008
Location: England & Ireland
Posts: 1063
Good Answers: 61
#28
In reply to #27

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/08/2015 5:52 PM

I've just been reading up on "Why some people leave CR4." Look no further than this thread for several answers.

Register to Reply Good Answer (Score 2)
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#32
In reply to #27

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/09/2015 11:11 AM

I will agree that sugar itself is non-ionic. That is a non-brainer. However, sucrose sugar breaks down to fructose and glucose, and aldoses as those are known as "reducing" sugars susceptible to oxidation. Once oxidized, the end group is now a carboxylic acid, and depending on the pH, it will be present as a carboxylate ion. I agree we are bit touchy about the wording, and the devil is in the details.

Sugar mills represent anything but a pure chemistry situation, so there must always be impurities in the process that are very undesirable in the steam circuit. I think conductivity monitoring is a good idea, or every Oxidation-Reduction Potential (ORP) might be of some use.

What I don't get is why people get all huffy about the confusion of wording when we are all just trying to "feel the elephant to see it."

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#34
In reply to #32

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/09/2015 11:33 AM

Just repeating what the new guy with, "2 x Doctor of Philosophy Degrees: Engineering Instrumentation and Engineering Management. I also have an Mba in project management and a 2nd Mba in International Business Management", and who took offense at being called a "brash newcomer" said.

Me? I don't know from nothin'.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#35
In reply to #32

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/09/2015 12:05 PM

[ What I don't get is why people get all huffy about the confusion of wording when we are all just trying to "feel the elephant to see it." ]

Perhaps it's just that people are concerned that they'll be the ones to feel that area below the part that feels 'like a little rope.'

I'm going to stop the analogy there, I do NOT want to be the next person to step onto a metaphorical 'land mine.'

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#36
In reply to #35

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/10/2015 2:10 PM

Unintentional palpation is never a pleasant experience. Nevertheless, it is precisely what science is built upon. So probe deeply, my friend, you may discover something up there. It may not be what you were seeking, but it may find its uses.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Commentator

Join Date: Aug 2014
Posts: 66
Good Answers: 2
#37
In reply to #17

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/10/2015 4:10 PM

Well good for you.

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#18
In reply to #14

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/08/2015 2:11 PM

All plant juices contain small quantities of electrolyte, certainly not as much as blood serum, but you can find sodium, potassium, etc. and also some small amount of chloride. Plant juices also contain not insignificant amounts of organics compounds such as organic acids and some nitrogen compounds that may be ionized at various pH conditions.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Commentator

Join Date: Aug 2014
Posts: 66
Good Answers: 2
#8

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/07/2015 9:00 PM

Do you know what range you can expect to see? For very low conductivity (like under 1 uS), look for a "resistivity " meter for example. Most any instrument will have a 4-20 mA loop for conductivity and maybe one for temperature.

You may want to talk to a salesman. Hach is one company, Knick is another...two of many.

Bob the water geek

Register to Reply
Power-User

Join Date: Jul 2010
Posts: 136
Good Answers: 19
#9

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/07/2015 10:00 PM

Honeywell does conductivity. Its 4973 insertion probe is rated to 140 DegC up to 16 bar. There are a couple different transmitter/ analyzer/controller options. They're industrial, not lab designs and priced accordingly.

Register to Reply Score 1 for Good Answer
Member

Join Date: Jan 2015
Posts: 5
Good Answers: 1
#11
In reply to #9

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/07/2015 11:26 PM

If you wish to use what I consider, "Best in Class" then opt for the new Yokogawa system.

It has unique features such as multi solution temperature compensation.

If this is confusing, please accept the fact that temperature compensation relies on what is called the Beta factor; it is normally based on an NaCl solution as a reference. There is a simple methodology for determining this. Google it and read how.

However, plant chemical fundis might not find this ( NaCl) to be close enough to the solution under measurement. Yok offers 2 solution alternatives.

It is also programmable via a sealed touch screen display in 6 languages. Couple this with a toroidal (or doughnut ) probe and the unit can be calibrated in Micro. milli Siemens as well as BRIX. ( Which for Molasses blow up tank application is perfect as it has 2 x 4-20mA outputs, the 2nd being temperature. Great as it allows Brix and temperature control from a single , but multi output sensor

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Aug 2014
Posts: 66
Good Answers: 2
#12
In reply to #11

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/08/2015 12:25 AM

Actually, all this is fairly standard. Electrodeless conductivity may not a good choice unless his process has a fouling component. It depends on what his conductivity range is, and we don't know that yet.

Register to Reply
Guru

Join Date: Jun 2011
Location: Mossel Bay, SA
Posts: 777
Good Answers: 21
#13

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/08/2015 2:09 AM

I agree fully with #1...Yours is a somewhat pathetic request.

Register to Reply
Member

Join Date: Jan 2015
Posts: 5
Good Answers: 1
#29

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/08/2015 11:55 PM

Ok, after all the BS, perhaps the original questioner and perhaps others may wish some meaningful observations on why and how to measure the presence of sugar contaminant in boiler return condesate. There could naturally be others, but in the vast majority, only trace sugar with its impurities are checked.

Firstly thre choice and location of the probe : Amperometric is simpler to install with a hot tap feature, making on-line cleaning and maintenance easier). It does suffer from mold infestation hwever and requires a weekly PM to clean.

Location : The idea of sensing a tube leak or other source of impurities in the feedwater, is to be able to divert the condensate to a holding tank before the charge pump delivers it to the Hotwell. So a ground floor collection point with say 5 or more condensate return streams collects these in a tank. Each has a dump valve allowing immediate switching to bypass and drain. This is the COARSE measurement and is normally effected with an Instrument range of 0 to 100 micro Siemens, setpoint around 40. ( Of course if the tube leak is severe, the conductivity could skyrocket to 1500 Micro Siemens or more)

This lower tank offers the ability of diluting a small leak with pure condensate from the remaining streams of integrity. However anything in excess of 12micro Siemens will cause major problems in the boiler tubes, where caramelization will lower tube heat transfer coefficient ( OK, so there are many chemical supply company that will treat boiler feedwater to minimize this.

Getting back to the measurement : Again, on the ground floor, I us a Marius Flame Photometer with a Potassium flame and filter. 766nM ( burns almost identically to the same color as a mild sugar solution) This unit has a 1/32nd" samping line making dead time almost zero and with a simple solenoid switching a dump valve some 25 meters verticaly mounted in the line, any and all impurities are dumped to a holding tank.This is not wasted, but are-analyzed by the plant process staff in order to see if it can be diluted to a successfully low figure, say 1 to 10 micro Siemens.

I hope this clears up some of the reasons why condensate in the sugar milling industry is monitored, how it is achieved and what and where to mount the equipment.

BTW, to all of you who rather arrogantly refer to me as "Brash newcomer" I say, weel done. You sure are on the right track here. Amazing how just one person originally from this continent has F******* up your American Pie.

But that was YOUR choice so live with it.

I will now take the broad hint about why people leave this forum. I learn every day, but some of the input here is just so crap, that I would much rather spend my time in a more meaningful way. To anyone who just MAY have appreciated my input, sorry, but the vast swell op opinion says I'm OUT.

Cheers.

Register to Reply Off Topic (Score 3)
Guru

Join Date: Aug 2008
Location: England & Ireland
Posts: 1063
Good Answers: 61
#30
In reply to #29

Re: Measuring the Online Conductivity of Condensate Water for Boiler

01/09/2015 4:55 AM

Please close the door after you. Thanks.

Register to Reply Score 2 for Off Topic
Register to Reply 37 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

adreasler (7); badbob (3); Bud (1); Charles101143 (5); energyconversion (7); Hilton (1); James Stewart (6); lyn (4); PWSlack (1); rao73 (2)

Previous in Forum: Difference Between Purge Panel & Flameproof Panel   Next in Forum: Orifice Calculater Software

Advertisement