Bus Duct

01/16/2015 2:03 AM

Why are we using bus duct between generator and transformer in place of simple cable?

Register to Reply
Pathfinder Tags: .
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#1

Re: Bus Duct

01/16/2015 5:21 AM

Do you mean "between generator and step-up transformer"? From the step-up transformer to High voltage Switchgear or overhead line we use cables, indeed.

Usually from generator to step-up transformer -or to and from generator breaker-you could use cables and terminations but many cables in parallel. Let's say for a 300-700 MVA generator at 20 kV the rated current is 8-20 kA. Ampacity of a 1000 MCM copper cable in a cable tray-10 ft. wide- is 580-600 A. Then you need 15 up to 35 parallel cables per phase [up to 100 single-core cables] provided with 200 terminations and terminals and so on.

__________________
Julius
Register to Reply Good Answer (Score 2)
3
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2

Re: Bus Duct

01/16/2015 3:08 PM

Because "simple cable" is too simple for something as complex as the interconnection of a generator to the grid. First there's the reliability question, whenever there are multiple terminations per phase of paralleled cables there's the problem of a poorly made connection causing an unbalanced current flow through the other connections/cables.

This is a degenerative situation which can lead to cascading failures as others now have to pick up excess current, which in turn leads to overheating/failure of the next poorest joint, things can degrade very rapidly from there and lead to a unit outage.

Another not so simple consideration is how to balance the current flow through all those cables given the physical spacing required to arrange and keep cool all those conductors.

But the real reason is revealed when a professional performs a FMEA (Failure Mode and Effects Analysis) and considers what happens when there is a fault, particularly a short circuit on the circuit between the generator terminals and the GSU (Generator Step-Up) transformer. The mechanical forces on those conductors and their supports are tremendous, leading to mechanical stresses that can permanently distort the conductors and/or break them free from their supports.

Parallel conductor systems are particularly vulnerable to conductor "galloping" whereby the magnetic forces due to a fault cause the unrestrained cables to break free and whip around ferociously for the duration of the fault. A properly designed bus duct system is mechanically robust to withstand those forces and keep the phases from contacting each other or ground and causing additional faults, it also has provisions for normal cooling and containing any arc products from causing any further damage to other equipment and/or personnel.

Which would you rather sign-off on, a pretested assembly with 6 bolted connections, or one with say 6 cables per phase for a total of 36 crimps and 36 bolted connections?

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 3)
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#4

Re: Bus Duct

01/19/2015 9:22 AM

Because the electrical code says so?

Because the insurance company underwriting the facility wants it to follow the code or they will refuse to pay out for any 'accidents'?

Because the engineer who designed it has a basic respect for human life and does not want people to be killed needlessly by electrocution?

Because the engineer who designed it has a basic understanding of liability laws and does not wont to go to prison from someone being electrocuted by a poorly-designed system he signed off on as safe?

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

7anoter4 (1); adreasler (1); dhayanandhan (1); RAMConsult (1)

Previous in Forum: Earth Leakage Current   Next in Forum: Protection of an Under-Rated Switchgear

Advertisement