Anonymous Poster #1

Excessive Arcing of Controller Magnetic Contacts

02/03/2015 11:15 AM

The motor voltage is 460 and I can see 412V of the controller during operation. At first go, the magnetic contacts had excessive arcing and burned out. After replacement of magnetics, the problem still occurs. I can not find the solution. Please help me out!! Thank you in advance.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Excessive arcing of controller magnetic contacts

02/03/2015 11:18 AM

Call an electrician. He can help you out.

Reply
Anonymous Poster #1
#2
In reply to #1

Re: Excessive arcing of controller magnetic contacts

02/03/2015 11:21 AM

Thank you for your reply but he told me you might google it...;;

Reply Score 1 for Good Answer
Anonymous Poster #2
#3
In reply to #2

Re: Excessive arcing of controller magnetic contacts

02/03/2015 11:53 AM

Sounds like the technically "blinder" being lead by the technically blind.

There's no helping your sort. Best thing that can happen is a big fire that destroys all the equipment. Much safer that way.

Reply Off Topic (Score 3)
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#6
In reply to #2

Re: Excessive arcing of controller magnetic contacts

02/03/2015 1:45 PM

Your electrician told you to ask 'Lyn' on CR4 to supply a google search for your answer?

Really.

__________________
jack of all trades
Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #2

Re: Excessive arcing of controller magnetic contacts

02/03/2015 2:30 PM

There is no point in asking lyn to do it; it is better to do these things oneself so as to save time.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #1
#9
In reply to #2

Re: Excessive arcing of controller magnetic contacts

02/03/2015 2:49 PM

#2 reply: I don't want there to be any misunderstanding.

I contacted my technician and asked for helping me in this issue but he told me it was because of power supply issue and you might google it because it was common issue. I just wanted to hear other advice in this forum. Thank you for sharing your opinions.

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Excessive arcing of controller magnetic contacts

02/03/2015 12:41 PM

Are you in North America and you have 480V available, or are you in some other part of the world where you use some other voltage, such as 415V? Because that would explain why you are reading 412V right there.

If you have 415V available and the motor is rated for 460V, it can posdibly still work, but not if the machine needs the full kW of the motor, because the difference in frequency will lower the kW capacity of the motor, even though torque will posdibly remain the same. Most machines work on torque, not power, but we have no idea what your machine is.

The arcing you show in that picture does not appear on the outset to be excessive. All contacts arc when they open (and a little when they close). But are these welding shut? That would be a problem.

If you want real help, you will have to do a more thorough job of describing everything about your system and issues. Otherwise you can expect further abuse.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Anonymous Poster #1
#8
In reply to #4

Re: Excessive arcing of controller magnetic contacts

02/03/2015 2:38 PM

Thank you for your reply.Our normal specific voltage rating is 460 V, 3 phases, 60 Hz.When we do not run our electric driven fire pump, it has 440V but after running it with load, the voltage dropped to 402 or 412V.The controller provides 400A magnetic so we consider that the capacity of current is not sufficient. We use wye-delta controllers at site. we installed motor connections as I attached(According to guidelines). Can this connection be an issue of arching matter?

Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#10
In reply to #8

Re: Excessive arcing of controller magnetic contacts

02/03/2015 3:20 PM

You need to get an Electrician involved. Someone who can look at it and find out what's wrong.

__________________
Good moaning!
Reply
Guru

Join Date: Jun 2010
Posts: 1296
Good Answers: 104
#12
In reply to #8

Re: Excessive arcing of controller magnetic contacts

02/03/2015 5:17 PM

Is this a new problem, or has it occurred for an extended time? Is there a mechanical interlock between your wye and delta starters? What is this motor driving? Is it starting unloaded? Which starter is arcing - wye, delta, both? (This is really not my area of expertise.)

Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#13
In reply to #8

Re: Excessive arcing of controller magnetic contacts

02/03/2015 5:21 PM

If you have a 480V service and it is dropping to 412V when this pump runs, your service is likely too small for the load. But it should be noted that since this is a FIRE PUMP, that may be an issue. In general, Fire Pumps only run when there is a fire, at which time everything else would (should) be shut down. So it's entirely possible that you are running your Fire Pump while the rest of the plant is running and creating too much of a voltage drop, which might be contributing to the problem.

But Wye Delta starting, although a notoriously cheap way to satisfy utility starting power restrictions, is exceptionally nasty when it comes to the contacts and contactors, ESPECIALLY what is called "open transition" Wye-Delta starting as you have here. When the starter has to transition from Wye to Delta, all 3 contactors must be open. This allows the motor to slow down just a bit, then when it reconnects, it is out of phase with the line supply and there is a resulting huge spike in current and voltage, which has a nasty habit of burning contacts on the contactors (among other things). With your voltage being low to begin with, then dropping lower when you add the Fire Pump load, that problem is made even worse, because most likely your pump motor is not at the right speed even for a normal transfer yet. Generally, Fire Pump starters that use Wye-Delta starting would use a "closed transition" version that adds a 4th contactor and a set of transition resistors that keep energy on the motor during transition so that this doesn't happen. Those are more expensive though.

So why are you running the Fire Pump? Testing? If so, the evidence of the severe voltage drop indicates that you should only be doing the testing when the rest of the plant is mostly shut down.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 3)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#17
In reply to #13

Re: Excessive arcing of controller magnetic contacts

02/04/2015 5:12 AM

Fire pumps, depending on the design, are often running 24/7, simply to maintain water pressure on a fire main piping in say a building, or even onboard a ship or possibly on a large area for a factory.

It is possibly not just simply switched on an off when needed.....in my experience......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#21
In reply to #17

Re: Excessive arcing of controller magnetic contacts

02/04/2015 4:45 PM

I am not saying your comment is in error, but, in my 39 years of experience, I have never seen a fire pump ran 24/7 to keep pressure on a sprinkler system. I have seen lots of "jockey pumps" (small 1-2 HP motors) used to maintain pressure levels but never have I seen a main fire pump ran that way, sure would be expensive on the power bill.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#24
In reply to #21

Re: Excessive arcing of controller magnetic contacts

02/04/2015 9:10 PM

On ships, there would be at least one full sized pump running 24/7 to keep the fire main ready for instant usage...

Alarms would alert the engineers to any pressure loss immediately.....

The OP has not told us if its a 24/7 or not or whether its on land, sea or even air!!

We are just left guessing....and covering all bases!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#25
In reply to #24

Re: Excessive arcing of controller magnetic contacts

02/05/2015 12:19 PM

Never looked at fire fighting systems on ships so I will defer to your knowledge. Seems like a waste of energy to me though.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#26
In reply to #25

Re: Excessive arcing of controller magnetic contacts

02/05/2015 10:17 PM

Must have been a military vessel, because we all know, energy is free on a military vessel...

All kidding aside I agree with you on the Jockey Pump issue, but this might also be a semantics issue as well. On a ship, the fire pump may have been one of many smaller pumps, cordoned off into sections of the ship separated by bulkheads in case they were sealed off, as opposed to a land building fire pump system where you have one large 200HP fire pump for the entire building and a small jockey pump to maintain pressure. So if instead the ship has 20 x 10HP zone fire pumps all tied into a common header, it doesn't make sense to add a 21st pump as a jockey pump, you just use the fire pumps themselves as jockey pumps and alternate them.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#27
In reply to #26

Re: Excessive arcing of controller magnetic contacts

02/06/2015 7:48 AM

I can understand that, it was a good explanation, thanks.

On ships the firemain pumps that are run (in my day) are the "Big Boys".......maybe nowadays there have been redesigns.

My next question to the OP is does this contactor supply the Jockey or the main pump? If its the main pump, surely it is hardly ever in use? Fires every day? I think not!!

We need more info....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#20
In reply to #13

Re: Excessive arcing of controller magnetic contacts

02/04/2015 9:05 AM

JRaef,

I apologize for more or less repeating what you stated in your post. By the time I had composed mine, you had already posted, with much more detail.

One detail not mentioned so far, is the ability of a contactor to maintain hold under voltage drop. There are contactors that can do this.

__________________
CRTL-Z
Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#14
In reply to #8

Re: Excessive arcing of controller magnetic contacts

02/03/2015 5:23 PM

If time based, the transition from star to delta could be miss-timed.

__________________
CRTL-Z
Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#16
In reply to #8

Re: Excessive arcing of controller magnetic contacts

02/04/2015 5:08 AM

What I would do:-

The contacts are definitely over heating badly....maybe not just in "starting", but also in "running" mode.....I assume that the motor has been checked out carefully for shorts and unbalanced fields?

Assuming that the motor is OK, this post suggests to me that there is too much resistance in possibly the cabling and definitely the contactor contacts.

Voltage is dropping and the motor is therefore taking more current....

With your present set up, even the motor is possibly in the danger zone of over heating as well.....have you checked that out?

Do not take this problem lightly.....it could become very costly and a fire that destroys everything is a distinct possibility....as I believe someone has already mentioned, Lyn maybe?

May I suggest that the cabling size be doubled (you neglected to mention what you have at this time) and the contactor contact current ratings should also be doubled to say an 800 amp. version.

Fusing/circuit breakers to be correct for the motor and load in use.....not increased.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5

Re: Excessive Arcing of Controller Magnetic Contacts

02/03/2015 1:43 PM

Check the motor starting current through the contactor, you may find it exceeds the contactor rating in which case you may need to upgrade the contactor and/or add a soft starter to the motor to limit the starting current.

Also, your supply voltage under load appears a little too low (check your local standards for the actual allowed voltage drop) so you may possibly need to talk with your power board (or whoever is responsible in what ever part of the world you are in) and get a transformer upgrade (excessive voltage sag is not good for motors or switchgear). If this excessive voltage drop is only during starting then a soft starter should fix the problem.

Let us know what you find.

__________________
jack of all trades
Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#11

Re: Excessive Arcing of Controller Magnetic Contacts

02/03/2015 4:11 PM

nice heaters though

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#15

Re: Excessive Arcing of Controller Magnetic Contacts

02/04/2015 12:01 AM

Is your powersupply(KVA) capacity enough,did you check for loose connections,is the cable size enough?. For fire fighting starter should not be star-delta(delay) but DOL.

__________________
pnaban
Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#18

Re: Excessive Arcing of Controller Magnetic Contacts

02/04/2015 8:39 AM

The load current is higher than the contactor is designed to interrupt.

Either the contactor is undersized or there is a downstream fault that is causing the current to exceed the contactor rating.

If this contactor is servicing the fire pump; Keep in mind that the interruption rating of the contactor is the most important factor and contactor selection should not be based on motor full load amperage alone.

Worst case conditions during interruption events need to be considered such as motor locked rotor amperage and the maximum current that can be developed in the circuit during a bolted-fault condition.

I agree with JREF in that if the system voltage is low the motor will pull excessive amperage during starting as well as when running.

If the contactor services more than just the fire pump; It is required that you determine the total load on the contactor and factor the interruption capacity accordingly.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply
Power-User

Join Date: May 2007
Location: Hurst, Texas
Posts: 178
Good Answers: 4
#19

Re: Excessive Arcing of Controller Magnetic Contacts

02/04/2015 8:59 AM

If you have R-C network snubbers make sure they are ok. If you don't have any, get an industrial version. Also add Mov's . All of them need to be across the motor windings because the collapsing magnetic fields are what generates the excess voltages.

Just from the pictures, I'd say the contactors are undersized. Some I have seen are okay in light duty, but in your case I think you need a larger margin.

You may need to parallel multiple Mov's to adsorb all the excess energy released, but you will know this if they cook or explode!

http://en.wikipedia.org/wiki/Varistor

http://www.taitroncomponents.com/catalog/PDF/Passive/MOV%20Selection%20Guide%20&%20How%20to%20Order.pdf

Good luck!

__________________
Bill H.
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#22

Re: Excessive Arcing of Controller Magnetic Contacts

02/04/2015 4:48 PM

Is this contactor in a factory built and certified Fire Pump Controller? If so... While there may or may not be a problem in this system that needs to be fixed, please, do not modify this fire pump controller in any way.

Doing so will void its certification and have a negative impact on your insurance situation should something happen.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#23

Re: Excessive Arcing of Controller Magnetic Contacts

02/04/2015 5:21 PM

Call Someone More Qualified To Troubleshoot The Problem. PERIOD!!!!!!!

Reply
Reply to Forum Thread 27 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (4); Anonymous Poster (4); bigg (1); Bill H. (1); Crabtree (1); Fredski (1); jack of all trades (2); JRaef (3); lyn (1); Munster (1); North of 60 (3); pnaban (1); PWSlack (1); SHOCKHISCAN (1); Unredundant (2)