Power to Drive Fans in Series

02/04/2015 2:33 PM

Hi folks,

I request anyone with a fan background to help me get over this. Suppose I have 3 axial fans in series and they need to be driven at a given RPM . Said fans belong to a horizontal air cooled heat exchanger. How do I calculate the input power to drive multiple fans in series? On first instance, it sounded to me like if I knew the power required for one fan, then it would be thrice that value to drive 3 fans. But I'm probably thinking this convenient answer isn't quite right. Please help, thanks!

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Power to drive fans in series

02/04/2015 2:49 PM

I take it the air flow of said fans is in series, not the electric motors (which should be wired in parallel through a single our multiple control contactors or variable speed drives)?

__________________
jack of all trades
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#2

Re: Power to drive fans in series

02/04/2015 3:10 PM

If the fans are drawing equal power then yes it would be three times that power.

Don't know why they would be in series. Electrical or flow makes no sense.

One fails they all do if electrical. And stacking them for flow would only see maybe minor improvement in flow.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#3

Re: Power to Drive Fans in Series

02/04/2015 7:04 PM

What do you mean by series? Does the same air flow through all three fans, or the same current flow through the three fan motors? If it's the former, then it would obviously require less power as each fan would be "helped" by the other two. If they are electrically in series, then I don't see why the total power would not be three times the power required by one fan.

Register to Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#4

Re: Power to Drive Fans in Series

02/04/2015 10:45 PM

This sounds very familiar . . .

http://cr4.globalspec.com/thread/81836/Fans-in-Series

I'm thinking you're right. It isn't that convenient an answer unless you are also tripling the pressure differential.

Register to Reply
Power-User
Hobbies - Musician - New Member

Join Date: Dec 2014
Posts: 418
Good Answers: 3
#5

Re: Power to Drive Fans in Series

02/05/2015 6:28 AM

First things first. Compute at the source- your hydraulic parameters

Fans in series would have the same Q -flow capacity but ΔP across it is definitely increase to some extent.

Hydraulic Power = ρgQH = Q*ΔP, all you need to do is divide it by 3, then check if motor rating of each fan is greater than the result. If so that it is greater, then no problem. That would be your maximum hydraulic power requirement for the fans, --no overloading with the motor rating. If hydraulic power is greater than motor rating -- then it wont work well and safe.

Q and delta P should be a design value as intended for the heat transfer capacity of the heat exchanger.

__________________
"When I thought I exceeded to be wise but wisdom was far from me" -King Solomon
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Power to Drive Fans in Series

02/05/2015 10:45 AM

Surely a simple telephone call to the fan supplier would answer this question? <sigh>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 5)
Associate

Join Date: Jan 2008
Posts: 33
Good Answers: 1
#8
In reply to #6

Re: Power to Drive Fans in Series

02/06/2015 10:25 AM

Hi PWSlack

Funny you say that, because that's what I did. Got a software tool from the fan vendor and it does all the math for you. With 3 fans, contrary to what I thought, the power remained pretty low. So it wasn't 3 times the power to drive one fan.

Register to Reply
Associate

Join Date: Jan 2008
Posts: 33
Good Answers: 1
#7

Re: Power to Drive Fans in Series

02/06/2015 10:24 AM

Thank you all. I think Rixter's answer hit the lightbulb in my head. No I don't mean to say electrically wired in series, the fans are stacked one behind the other on the same drive shaft. They are the same in design, so each fan has 6 blades and other similar geometry.

Register to Reply
Active Contributor

Join Date: Jan 2015
Location: Mumbai, Maharashtra, India
Posts: 16
Good Answers: 1
#9

Re: Power to Drive Fans in Series

02/12/2015 2:20 AM

You should call it multistage series fan arrangement, When the output of first is input for the second and output of second is input for third the output, overall output will be different from each single fan output. Using even number of blades may not be acoustic and may cross the limits of db. Power will also be different for all three, ip/op, load rpm, fan load [even with same type of blades].

Multistage arrangements can be series or parallel, power calculation will differ in both the cases same way as in water pumps. If you have assess to either theory you can get answers easily. You can select either arrangement after deciding what you want more volume or pressure.

__________________
Ajay Sanghrajka
Register to Reply
Register to Reply 9 comments

"Almost" Good Answers: