Density of an Insulation

02/04/2015 2:09 PM

is there a formula to calculate the density of a fiberglass insulation as per the middle east condition.I have installed fiberglass pipe insulation with 64 Kg/m3 density and 3 inch thickness for outdoor pipe.But now the consultant insists to change and increase the density to 80 Kg/m3.I need to show a calculation to proove that the installed density and thickness will achieve the desired properties.

The datas are

pipe internal temperature 5 degree centigrade

External temperature 45 degree centigrade

Relative humidity 75%

Thermal conductivity of insulation 0.032 at 24 degree centigrade

Pipe dia 50 mm

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Density of an insulation

02/04/2015 2:15 PM

How about compressing and adding 25% more insulation into the same pipe?

80/64 = 1.25 = 125% of installed insulation.

Fibreglass insulation is compressible right?

__________________
jack of all trades
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2
In reply to #1

Re: Density of an insulation

02/04/2015 2:20 PM

Yeah, that's the idea. Pack it as tight as possible to get more R in the box.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#3
In reply to #2

Re: Density of an insulation

02/04/2015 2:45 PM

No problem then, unless perhaps something has to pass through said pipe.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#4
In reply to #1

Re: Density of an insulation

02/04/2015 3:56 PM
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: Density of an Insulation

02/04/2015 4:49 PM

I'm curious to know how you arrived at 64 Kg/m3 density and 3 inch thickness if you don't know how to calculate the necessary insulation required in the first place?

You want to defend an indefensible decision on your part, now that it has been questioned.

Desperation on your part does not instill urgency on ours.

Search the internet for a solution and remember this next time you take a WAG that may be questioned later.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6
In reply to #5

Re: Density of an Insulation

02/04/2015 4:58 PM

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #6

Re: Density of an Insulation

02/04/2015 5:18 PM

Just had a chuckle. Went back and looked at the OP's past requests for help.

Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#8

Re: Density of an Insulation

02/04/2015 11:24 PM

Please check the thickness as mentioned in the agreed contract technical specification . If the consultant is insisting on particular thickness he must have designed the system based on certain K value and thickness.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9

Re: Density of an Insulation

02/05/2015 12:43 AM

Fiberglass isn't particularly well suited for insulating cold pipes. Much better is expanded polystyrene or polyurethane foam, probably about 1.5 inch thickness in this case, and covered with a high-quality vapor barrier.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Jun 2014
Posts: 623
Good Answers: 33
#10

Re: Density of an Insulation

02/05/2015 7:00 AM

Too bad you are not located in New York or New Jersey: you could just hand the 'consultant' 5 $100 bills and say "are you sure? It looks fine to me"

__________________
Hey Isaac, catch! ...oops, that's gonna leave a mark...
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#11
In reply to #10

Re: Density of an Insulation

02/05/2015 8:38 AM

Good idea, except I'd guess he hand the "consultant" 308749.47 Rupees.

Register to Reply
Power-User
Hobbies - Musician - New Member

Join Date: Dec 2014
Posts: 418
Good Answers: 3
#12

Re: Density of an Insulation

02/05/2015 9:54 AM

It actually means you are cheating the right specification and not reading the contract-but you may. This literally means change the under specs installation.--that is your fault if you are not complying as per contract.

Now if it's the other way around, this is a variation order and additional labor and materials for reworks is chargeable to the owner,--which is a good thing to you, bad for the consultant and engineers(owner side).

__________________
"When I thought I exceeded to be wise but wisdom was far from me" -King Solomon
Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#13

Re: Density of an Insulation

02/05/2015 10:47 AM

You don't say if the new insulation is also fiberglass. The insulating value of most insulating materials is due to trapping air and preventing circulation of that air. A higher density insulation of the same material will contain more of that material and less air. If I'm not mistaken, a higher density insulation of the same material and thickness will transfer MORE heat than the lower density insulation.

To get better insulation, you need either a better material or greater thickness.

Since you are trying to keep heat OUT, a reflective coating such as aluminum foil on the outside of the existing insulation can help significantly.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#14
In reply to #13

Re: Density of an Insulation

02/05/2015 1:18 PM

That's right, you beat me to it. OP hasn't said why the consultant wants higher density, perhaps he's under the impression it will improve insulation, or some other reason.

__________________
Give masochists a fair crack of the whip
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#15
In reply to #14

Re: Density of an Insulation

02/05/2015 1:28 PM

It could also be for abrasion resistance.

Lets see if we can get to a hundred different plausible reasons before the OP comes back.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Member

Join Date: Nov 2011
Posts: 9
#17
In reply to #15

Re: Density of an Insulation

02/07/2015 3:10 PM

Thanks for all the reply. The specification was 80 Kg/M3 Density Fiberglass pipe insulation. The mistake had happened from the site engineer. It was my responsibility too cross check. So we are all responsible. Now it is installed and all vapor barriers like foster coatings are applied. We had realized our mistake at the time of inspection. To remove and to new installation is not feasible as the material, cost and more over we will all be responsible.

Any advice….

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#18
In reply to #17

Re: Density of an Insulation

02/09/2015 1:24 PM

You still have not said whether the thickness of the installed insulation is the same as the specified thickness, nor what that value of thickness is.

If I understand correctly, you have some thickness of 64kg/m3 fiberglass insulation, while the original specification was that same thickness of 80kg/m3 fiberglass insulation.

If that is correct, then I believe that the installed insulation will provide better heat rejection than the 80kg/m3 fiberglass insulation would have provided, but it will be somewhat more susceptible to physical damage from accidental impact/force.

"Thermal conductivity of insulation 0.032 at 24 degree centigrade" 0.032 in what units?

Without knowing the thickness of the insulation and the total length of pipe, there is no way to calculate even a rough estimate of the heat gain of the cold material.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Member

Join Date: Nov 2011
Posts: 9
#19
In reply to #18

Re: Density of an Insulation

02/10/2015 2:53 PM

It is 3 inch thickness.What i have installed is 64Kg/m3 Density with 3 inch thickness and the specification was calling for 80 Kg/m3 Density with 3" Thickness.Thermal conductivity is 0.032 Watt per meter per celsius degree (W/m-°C).Length of each pipe is 1.2 meter.

Register to Reply
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#20
In reply to #19

Re: Density of an Insulation

02/13/2015 2:21 AM

Thank you.

Now, in my limited experience, the term 'thermal conductivity' is a property of a material, as illustrated by the following sample

(from the Physics Hypertextbook 12/8/11):

"

Thermal Conductivity for Selected Materials
(~300 K except where otherwise indicated)
materialk (W/m K)
air, sea level0.025
air, 10,000 m0.02
aluminum237
asbestos0.05-0.15
asphalt0.15-0.52
brass (273 K)120
brick0.18
bronze (273 K)110
carbon, diamond895

"

The suppliers of your fiberglass should be able to provide values of thermal conductivity for both densities. As I have stated previously, I'm almost certain that the higher density material will have a higher thermal conductivity, and thus a greater heat ingress.

I suspect that your value of 0.032 W/m-°C is a maximum permissible heat gain for the 1.2 m length of pipe. That is not a thermal conductivity. If English is not your first language, we may have had some misunderstandings due to translation...

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#16

Re: Density of an Insulation

02/05/2015 2:55 PM

You haven't stated what the "desired properties" are.

__________________
An obstacle is something you see when you take your eyes off the goal.