Unbeatable Wire Pull

02/09/2015 2:10 AM

Hello all,

We have a three inch rigid conduit in the slab.

Old cloth wrapped, (non asbestos) 4/0 conductors.

there were four. now three,

Unfortunately the insulation has stripped off in the pipe and we believe it is creating a wedge in the pipe.

We have had fingers pull off, broke two socks, and have used a tugger at 8,000-10,000 lbs.

we have dumped about a gallon of soap in the pipe.

We think it is binding at the 90 about five feet from the panel.

I broke one of the wires on the last pull at 9,000 lbs.

PS we have pull all conductors out from the other end.

Is there a heavier duty tugger than the Greenlee Ultra tugger 8?

Or a way to auger the conduit and wire.

Thanks

Yes, using barricades, 70E, and plywood over equipment.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Jul 2014
Location: Savannah, GA. The post office decided to change my address again.
Posts: 253
Good Answers: 19
#1

Re: unbeatable wire pull

02/09/2015 2:31 AM

If I read correctly you are trying to get the old insulation out only as the conductors have been pulled from the other end.

Might try high volume air blow back from the pull end, plumbers may have a solution for you they clear some pretty nasty clogs.

Heavier tugger? if it is a vertical pull try a high capacity forklift they can generate considerable force but be forewarned that they can also pull they conduit right out of the concrete.

__________________
Never seem more learned than the people you are with. Wear your learning like a pocket watch and keep it hidden. Do not pull it out to count the hours, but give the time when you are asked.(Lord Chesterfield)
Register to Reply
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: Unbeatable Wire Pull

02/09/2015 9:33 AM

If you pull on it hard enough you will break something. The only way one can guarantee breaking what one wants broken will be if everything can be seen. I would first consider a bore scope to identify the situation before going blindly for more power.

If this wire run is so old that it has cloth insulation then the conduit is also that old. Replace the conduit with the old wires inside.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#4
In reply to #2

Re: Unbeatable Wire Pull

02/09/2015 12:01 PM

"If you pull on it hard enough you will break something." Agreed.

Title of the thread is Unbeatable Wire Pull. This sort of sounds like the irresistible force. Our OP is already breaking wires. I sort of doubt the Tim Allen technique is called for here.

When the unshared information regarding the wire pipe and cables is used in a wire pull calculator or conduit fill calculator, what does the calculator tell you?

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#5
In reply to #4

Re: Unbeatable Wire Pull

02/09/2015 12:16 PM

Oh I don't know. Every time Tim went for more power and failed spectacularly, Al looked better and better. I've found that sometimes it is better to let them fail. It often helps to clear their ear canals.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#20
In reply to #5

Re: Unbeatable Wire Pull

02/10/2015 12:07 AM

It was always funny to watch!

__________________
"Real Bass Players" do not use picks
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#3

Re: Unbeatable Wire Pull

02/09/2015 9:50 AM

What is the complete length of the conduit?

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#6

Re: Unbeatable Wire Pull

02/09/2015 12:34 PM

You might try a plumber's snake, the kind with a helical coil on the end with a sharp point to snag the blockage. I would think pulling is far preferable to pushing because pulling would relieve the blockage, whereas pushing would tend to cram it tighter.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Optical Engineering - Member Engineering Fields - Engineering Physics - Member Engineering Fields - Systems Engineering - Member

Join Date: Apr 2010
Location: Trantor
Posts: 5363
Good Answers: 647
#7

Re: Unbeatable Wire Pull

02/09/2015 12:52 PM

I'm confused. You said you had 4 conductors in the conduit, but now you have three. You also said you've pulled out all the conductors from the other end. So are there still conductors in the conduit or not? If so, try pulling the remaining conductors from the other end. At this point they may be damaged and will have to be replaced anyway.

You poured soap into the pipe (as a lubricant?), but did you use a shopvac to force the soap into and then beyond the clog? It may not be getting to where it is needed.

__________________
Whiskey, women -- and astrophysics. Because sometimes a problem can't be solved with just whiskey and women.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#8

Re: Unbeatable Wire Pull

02/09/2015 3:48 PM

The insulation has peeled off the wire and wedged itself in there, that when combined with the friction of the copper on the conduit, has created a perfect storm of a wedge of copper cemented in place with the dried up cotton swelled up with the lube.

Abandon the old conduit in place or jack hammer it out and replace it with new materials, cheaper and less time consuming.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Power-User
Hobbies - Target Shooting - New Member Hobbies - Model Rocketry - New Member Safety - ESD - New Member

Join Date: Jan 2008
Location: here
Posts: 109
Good Answers: 5
#10
In reply to #8

Re: Unbeatable Wire Pull

02/09/2015 4:40 PM

That is exactly what happened. This is one of the four cables we were able to pull out.

The other three are wedged at the 90 below the panel. we have to shutdown the building to access the panel.

The total run is about 175ft to the middle of the first floor panel.

If a new conduit is run, it would probably cost around 30-60K.

Just looking for ideas.

Thanks

All the wires have been pulled in about 35ft. So no pulling back the other way.

Register to Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#11
In reply to #10

Re: Unbeatable Wire Pull

02/09/2015 5:09 PM

Well, I don't know about anyone else but this isn't what I thought you were asking about. This is, I'm afraid, worse than I thought, and I thought it was sort of bad to begin with.

To dig up and replace is an excessive amount of $$$. I suppose you've considered the easy alternative: abandon existing wireway and go overhead in lieu of underslab.

Where is that Tesla guy with his wireless energy transmission when you need him?

__________________
Semper Ubi Sub Ubi
Register to Reply
Guru
Engineering Fields - Optical Engineering - Member Engineering Fields - Engineering Physics - Member Engineering Fields - Systems Engineering - Member

Join Date: Apr 2010
Location: Trantor
Posts: 5363
Good Answers: 647
#12
In reply to #10

Re: Unbeatable Wire Pull

02/09/2015 8:36 PM

Two more ideas: 1) Vibration. If the jammed conduit isn't too deep below the concrete surface, and if you have a pretty good idea where the clog is, rent a vibration machine and send waves of vibration into the clog to see if you can shake it loose.

2) Jackhammer. Break through the concrete at the point of the clog and chop it out. Then pull out the rest of the cables, repair the conduit, fish new cables through it, and then patch the concrete.

__________________
Whiskey, women -- and astrophysics. Because sometimes a problem can't be solved with just whiskey and women.
Register to Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#22
In reply to #12

Re: Unbeatable Wire Pull

02/10/2015 12:25 AM

I do like the idea of using an electric motor driven compactor.

__________________
"Real Bass Players" do not use picks
Register to Reply
Power-User

Join Date: Aug 2008
Location: Melbourne, Australia
Posts: 476
Good Answers: 32
#13
In reply to #10

Re: Unbeatable Wire Pull

02/09/2015 10:31 PM

Could you clean out the soap sludge and poor in some acid (say hydrochloric acid - dilute form such as that used for cleaning bricks - maybe a tad stronger), to dissolve the insulation - leave it there a while? Then flush thoroughly. Assumes that the conduit can handle it and you won't leave puddles in it.

Just an idea - maybe too dangerous.

__________________
johny451
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#15
In reply to #10

Re: Unbeatable Wire Pull

02/09/2015 11:09 PM

One solution may be to find a suitable solvent that will dissolve the cloth and which then can all be flushed out of the pipe. This will depend on the conduit material, local environmental concerns etc., but it's another possibility.

Other than that, you are going to have to get into the conduit at the point where it is clogged.

That will entail a bit of concrete cutting and you will want to be at the right spot if you go that way

Consider connecting a wire tracer such as the Ampro 4000T or similar to the still in place wires so that you can find where they go under the slab. You can also find where the wires actually end with one of these devices. Another option is to push a metal snake in as far as it will go and connect the tracer to that to find the route of the conduit

Alternatively, employ a concrete radar scanner to find the conduit route.

The jam up is likely to be at a bend, so that would be the place to start, but a simple measure of the length that you have out will give you an idea of where the problem is greatest.

In any event, getting into the pipe somewhere in the middle will ease the burden, and it shouldn't be too hard to re-establish the integrity of the conduit afterwards.

Register to Reply
Guru
Australia - Member - New Member

Join Date: Jun 2011
Location: Thailand
Posts: 631
Good Answers: 3
#18
In reply to #10

Re: Unbeatable Wire Pull

02/09/2015 11:38 PM

Is the 90 5 feet below the panel? or horizontal? A 90 in a conduit w/o inspection point is bad design in any case, but if absolutely necessary, it should have a good radius on it.

__________________
Floss or die!
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#23
In reply to #10

Re: Unbeatable Wire Pull

02/10/2015 1:57 AM

I would take out the section of the elbow, pull the rest of the wire straight out, replace the elbow section, and run the new wires....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#24
In reply to #23

Re: Unbeatable Wire Pull

02/10/2015 2:19 AM

Ahh...but is there only one elbow?

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#34
In reply to #24

Re: Unbeatable Wire Pull

02/10/2015 11:20 AM

Who cares? cut 'em all out....

If you had started with one of these you'd be done by now....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#37
In reply to #34

Re: Unbeatable Wire Pull

02/10/2015 12:14 PM

That guys hard hat kept falling off and smashing his toes...

__________________
CRTL-Z
Register to Reply Off Topic (Score 5)
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#9

Re: Unbeatable Wire Pull

02/09/2015 3:54 PM

Go see the local plumbing experts and borrow/hire the services of a pipeline inspection camera that will fit the conduit. Most have 50ft cables but often they will have some with 150ft leads.

That will allow you to base your direction on observation rather than guess.

Some of these cameras are self driven, while others are pushed by operators into position.

If it's so important that the surface no be disturbed, then there are pipe bursting options to run a new conduit through the track of the previous one.

__________________
Just an Engineer from the land down under.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Aug 2009
Posts: 17
#14

Re: Unbeatable Wire Pull

02/09/2015 11:06 PM

At the vacant end of the conduit extend it to connect a tee fitting with ball valves to each branch of the tee. On one branch connect a pump on the other branch a vacuum source. With with the vacuum ball valve closed pump in a solvent/lubricant. WD40 comes to mind. Then close the pump valve and open the vacuum valve. Vacuum. Repeat this process a number of times. Give the copper another tug.

Register to Reply
Guru

Join Date: Aug 2010
Location: Melbourne, Australia
Posts: 740
Good Answers: 24
#16

Re: Unbeatable Wire Pull

02/09/2015 11:24 PM

I would suggest using some of the available plumbing tools - camera to see what is going on and auger to clear it.

Perhaps try calling in a plumber..... they are familiar with this sort of problem.

Register to Reply
Guru

Join Date: Jun 2009
Location: Ontario Canada
Posts: 930
Good Answers: 31
#30
In reply to #16

Re: Unbeatable Wire Pull

02/10/2015 8:57 AM

The camera is a very good idea that way you may get a visual of the issues..a little technology will usually help in the diagnosis. Possibly a roto rooter device will clean the bore possibly with some compressed air at same time to clear the debris.

__________________
The fine line between cuddling and holding one down to prevent escape must be learned
Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#17

Re: Unbeatable Wire Pull

02/09/2015 11:25 PM

If the other end is empty (all pulled 35 feet or so), then you can access that end of the wires using plumbers equipment and recover them from that end.

Usually we would have had a pull through rope/wire attached so that we could install the replacement cables. Wasn't there something like that on the end?

Good luck!

__________________
Just an Engineer from the land down under.
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#19

Re: Unbeatable Wire Pull

02/09/2015 11:50 PM

Any chemical that eats away the paper will also attack the conduit. It may also corrode the copper wire.

Pull the wires back out through the panel and put them neatly aside. This will make easier pulling later.

Get a substantial plumbers snake, the kind that uses connectable lengths of wire/spring sections. That way you can make the snake as long as you need it. Put a grabber head on it, spiral wound spring with a open end on the leading end. It look sort of like a cork screw. (This is the type that you would snake out a 3" drain pipe with). Temporarily fasten a piece of 3" conduit with appropriate bends to the panel end of the conduit. Put the snake through the temporary guide which is there to keep the snake from kinking. Rotate and advance the snake through until you catch the plug. While rotating in the same direction pull the snake and the plug or part of the plug out. If the whole plug doesn't come out repeat this until all is out.

Just treat the paper plug as you would a large plug of paper and shxt in a drain pipe.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#21

Re: Unbeatable Wire Pull

02/10/2015 12:10 AM

Pull it all out and start over. Lube from the start to finish. Best to use XLPE though.

__________________
"Real Bass Players" do not use picks
Register to Reply
2
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#25

Re: Unbeatable Wire Pull

02/10/2015 2:32 AM

The only surefire way of removing the cable for little or no cost is to contact a couple local tweakers and schedule the removal between 12midnight and 3am. You'll be amazed at their motivation

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply Good Answer (Score 2)
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Jun 2014
Posts: 623
Good Answers: 33
#26

Re: Unbeatable Wire Pull

02/10/2015 6:29 AM

If you don't get the other three conductors out of the conduit, you are kind of torqued.

At this time, you can only pull the conductors in one direction.

So you have 3 more chances to get another conductor out in one piece.

If you get one more out, hopefully the remaining two will be easier.

At this point you have limited options: you either have to clear the conduit or install a new one.

I would consider borrowing somebody's jeep or truck with a winch on it and pull on one conductor at a time or at least for the first one, the other two may pull out together which would be better to clean out the conduit of leftover debris.

If the winch does not work, turn the vehicle around...get the idea?

I think pulling one at a time would be easier at this point but you could barrow two more vehicles with winches if available.

Just be careful if you have to turn the vehicles around for dual/trio pull, you do not the vehicles to contact each other.

I cannot believe I am recommending this, it sounds like something from Red Neck Island TV show.

But you sound like you are approaching the point of no return, they are wedged now and if you don't get them out you rent a compressor and jackhammer....

That box: "I want to post anonymously" looks more appropriate somehow right now.

__________________
Hey Isaac, catch! ...oops, that's gonna leave a mark...
Register to Reply
Power-User

Join Date: Nov 2011
Location: NASA-Glenn Research Center, Cleveland Ohio
Posts: 389
Good Answers: 17
#27

Re: Unbeatable Wire Pull

02/10/2015 8:05 AM

how about pouring some drano (sodium hydroxide) down the pipe (mix with water first and follow safety). it will eat the organic material (cloth insulation).

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#28

Re: Unbeatable Wire Pull

02/10/2015 8:43 AM

A high pressure water cutter can be used to clear the pipe as a last resort.

Are you sure that you do not have a junction box or other device such as a splice box in the pipe? If so you will have to locate it and dig it up in order to clear the restriction.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#29

Re: Unbeatable Wire Pull

02/10/2015 8:49 AM

I agree with Wwwheaty.

Use more soap, possibly diluted a bit with water and then pour into the conduit and use a vacuum to pull it through the cloth insulation.

You can essentially flood the conduit with a soapy solution and get the other wires out then use a plumbers snake with an auger tip to retrieve the insulation.

After the conduit is cleared of any obstructions, rinse the conduit out with clear water and pull new wires.

One more question,

Is there dirt on the wire you were able to remove. If so, the conduit may be corroded through and open to the earth below the slab?

Good luck

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#31

Re: Unbeatable Wire Pull

02/10/2015 9:18 AM

Everyone seems to be assuming that this cloth is what is causing the binding. What if the pipe is partially collapsed and/or now root infested. The bunched up cloth from the pulled cable was just getting caught on the obstruction that has to be cleared.

There comes a point in every project where the initial plan must be modified to complete the task.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#32

Re: Unbeatable Wire Pull

02/10/2015 9:34 AM

Houston, you have a problem.

As I see it, you have three possible solutions.

1. Remove the wire, You might try flexible drill extensions like these (you might have to chain a few together) and a short auger bit like this. Once the wire/insulation is chewed up, you may be able to remove it.

2. Jackhammer up the elbow and replace it (and hope this is where the problem is).

3. Abandon the conduit in place, and run an overhead replacement.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Power-User
Hobbies - Target Shooting - New Member Hobbies - Model Rocketry - New Member Safety - ESD - New Member

Join Date: Jan 2008
Location: here
Posts: 109
Good Answers: 5
#33

Re: Unbeatable Wire Pull

02/10/2015 10:22 AM

Good morning and thanks for all the tips.

The conduit is in the basement of a two story building on a hill.

The panel we pulled the wire out of is in the center of the building first floor, about 175ft away. All underground fed from a 2000A panel, that we can only shutdown for a day and to penetrate the slab we almost need an act of Congress.

It is in a government building.

Here is a picture of the ONE cable we pulled out.

Register to Reply
Power-User

Join Date: Nov 2011
Location: NASA-Glenn Research Center, Cleveland Ohio
Posts: 389
Good Answers: 17
#36
In reply to #33

Re: Unbeatable Wire Pull

02/10/2015 11:33 AM

call roto-rooter (and dont dismiss the sodium hydroxide, it will disintergrate the cotton)

Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#38
In reply to #33

Re: Unbeatable Wire Pull

02/10/2015 12:54 PM

Accessible ceilings?

In Canada we would abandon the old conduit and run some teck cable, probably along the wall or attached to the ceiling (is the ceiling available?).

In the US they are fond of rigid. So make your choice and get on with it

Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#42
In reply to #33

Re: Unbeatable Wire Pull

02/10/2015 4:16 PM

Would it be possible to provide a rough sketch including the position of the wire for this installation?

__________________
CRTL-Z
Register to Reply
Participant

Join Date: Feb 2013
Posts: 4
#35

Re: Unbeatable Wire Pull

02/10/2015 11:22 AM

Yes I also work in a similar situation. The extensive job off temporary feeding loads so that power shut down can last until the job is complete, may be the only choice you have. I did not catch the reason for pulling out this cable other than it was old. If this feeder shorted inside the conduit, it may have welded itself to the conduit. Another thing that wire pullers do not think about. We call it wire pulling so as to confuse the general public. What you really want to do is draw the cable from the conduit. A drawn cable pull is one that an equal amount of force is pushed at the conduit as is pulled from it. If this is not possible, the results are often catastrophic. As far as a stronger tugger goes, I have used as many as three tuggers in tandem to increase the pulling capacity. Again this will present possible catastrophic results if not properly done. If the ends of your cables are long enough to use the strands of the wire to hook to pulling rope, rather than using a sock or finger. I would try to pull the remainder the cables all at the same time. Good Luck!!! but I'm sure you're screwed.

Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#39

Re: Unbeatable Wire Pull

02/10/2015 1:56 PM

As it is cloth insulation, perhaps you could put some moths in the conduit.

Seriously, those tuggers use nylon rope if I remember correctly (based on my dad almost losing a thumb when the drum catch failed) is there room and a solid anchor point to use a come along?

__________________
CRTL-Z
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#40

Re: Unbeatable Wire Pull

02/10/2015 2:33 PM

What about running a directional drill line parallel to the old pipe and just run the new wires through that. Leave the old wires where they want to stay.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User
Hobbies - Target Shooting - New Member Hobbies - Model Rocketry - New Member Safety - ESD - New Member

Join Date: Jan 2008
Location: here
Posts: 109
Good Answers: 5
#41

Re: Unbeatable Wire Pull

02/10/2015 2:59 PM

Largest Greenlee tugger made.

Sleeve over conduit with guide pulley.

Register to Reply
Guru

Join Date: Oct 2014
Location: Hemet, Land of milk and honey.
Posts: 2365
Good Answers: 36
#43

Re: Unbeatable Wire Pull

02/10/2015 4:28 PM

My idea.

1. Look at building plans and see how conduit was routed, this will tell you length of straight runs and where 90's are at. You said you pulled 35 ft. from on end, subtract 35 from that end to approx its position.

2. Everywhere there is a 90^, there can be a jam, consider cutting thru concrete at (these) points.

3. No plans ? The gas meter man came to my house recently to trace the pipe, he had this gizmo that looked like a box attached to a handle, he traced the pipe no problem thru the slab and under the soil.

Years ago, a customer of mine needed to replace a light on their swimming pool, the wire was cloth backed 12/2 , an old man ( I was a young punk) suggested I tie a wire puller to both ends, this way I could work wire back and forth to loosen it up and use lubricating oil to lubricate the inside of the conduit ( I thought of using soapy water but he said that would cause the cloth to swell) , as I stood on a tall ladder using a funnel and a clear piece of tubing, I poured the oil into the conduit, he worked the wire back and forth and coaxed the wire out of the conduit.

Note: the picture of the guy with the concrete saw reminds me of bikers who run around with skid lids hooked to helmet locks.

As for the" act of congress " thing, somebody in the white house has been doing a lot of stuff recently without paying them no never mind.

Register to Reply
Participant

Join Date: Feb 2015
Posts: 1
#44

Re: Unbeatable Wire Pull

02/10/2015 8:47 PM

Is there some sort of corrosive liquid you can pour in the conduit to reduce the of the insulation debris that remains in the conduit. Let is set over night it might loosen it enough to come out. I am unsure of what would eat the fabric with out generating a lot of hazmat.

Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#45
In reply to #44

Re: Unbeatable Wire Pull

02/10/2015 11:18 PM

Anything that will eat up the insulation will eat up the conduit and wire even faster. Couplings on rigid metal conduit are supposed to be watertight but most aren't unless a special conductive lube is used. The corrosive material will then leak out and eat away the concrete the conduit is encased in. With copper wire, plastic or rubber insulation, galvanized conduit or paper insulation the order of being eaten by the corrosive material would probably be copper wire, galvanized conduit or paper insulation and finally the plastic and rubber insulations. Solvents, especially chlorinated, will most likely make the insulation swell making the job even harder.

Unfortunately the old saying "What goes in must come out" is very true in this case. If it jammed while being pulled in one direction the most likely solution is to pull it out in the opposite direction, just with more pull. There are "split wire pulling grips" that can be put on the wires to accommodate pulling the wires out with extremely forceful effort. https://www.mcmaster.com/#standard-cable-pullers/=vuul4y http://www.cooperindustries.com/content/dam/public/wiringdevices/BuyersGuides/AHBG/N/AHBG-N-27.pdf These are only the most common types. Much stronger ones are also available for this purpose or pulling high voltage wire between towers.

Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#46

Re: Unbeatable Wire Pull

02/10/2015 11:24 PM

Double rig the cable at the wire end with another pulley.This will double the pull of the existing puller.(Like a block and tackle principle).

Good luck!

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Jun 2014
Posts: 623
Good Answers: 33
#47

Re: Unbeatable Wire Pull

02/11/2015 3:42 PM

Well, did you get it out or not?? Hopefully no one got hurt.

__________________
Hey Isaac, catch! ...oops, that's gonna leave a mark...
Register to Reply Score 1 for Good Answer
Power-User
Hobbies - Target Shooting - New Member Hobbies - Model Rocketry - New Member Safety - ESD - New Member

Join Date: Jan 2008
Location: here
Posts: 109
Good Answers: 5
#48

Re: Unbeatable Wire Pull

02/11/2015 5:12 PM

We are going to abandon in place.

Wish I had better news.

Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#49
In reply to #48

Re: Unbeatable Wire Pull

02/11/2015 5:17 PM

Oh well...

Will there be a memorial service?

__________________
CRTL-Z
Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#51
In reply to #48

Re: Unbeatable Wire Pull

02/11/2015 9:46 PM

I think you should still hire a couple of local tweekers. In this video, seems they got pass the elbows in this guy's conduit with no problem!

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru

Join Date: Aug 2010
Location: Melbourne, Australia
Posts: 740
Good Answers: 24
#52
In reply to #48

Re: Unbeatable Wire Pull

02/12/2015 5:06 PM

Something like this:

http://www.alibaba.com/product-detail/Mini10m-USB-Endoscope-Inspection-Camera-Waterproof_1897742586.html

would show you what is going on.....

Register to Reply
Associate

Join Date: Jan 2009
Posts: 37
Good Answers: 1
#53
In reply to #48

Re: Unbeatable Wire Pull

02/16/2015 11:08 AM

"We are going to abandon in place."

Prolly the simplest course of action.

However...it would have been interesting to knock this out.Most likely,based on what you have already removed,the conductors & insulation moved independently causing the cloth/rubber insulation to bunch up & wedge in tight against the conduit.

A formidable union (bridges are held together with this form of mechanical connection)!

The only solution is to 'undo' the joint.

Possibly a plumber's snake could be utilized to push back (WITHOUT ROTATING),if only slightly, the bundle enough to get the conductors & insulation unwedged or at least reduce the PSI of the wedged bundle.

Pump in some lube.Pumping will be required due to the now restricted access between the conductors.

Some vibration.Use the snake,Again WITHOUT ROTATION to alternately push and pull the bundle.Some vibration applied directly to the conduit could not hurt.

If the lube pump PSI could be monitored & maintained during these processes a clue might be had as to how the bundle is behaving (moving,separating from each other etc.).

If there is any success with the above then re-attaching the snake to an individual conductor,repeating the above processes & then slightly rotating the individual conductor could get you free.

Rinse & repeat as req'd.

I suspect that any kind of camera will show a blob of insulation.

Introducing Any kind of caustic will jeopardize the future conductors as well as anyone working on this project.

J

Register to Reply
Guru
Hobbies - CNC - New Member

Join Date: Jul 2013
Location: Lost Wages Nevada
Posts: 1578
Good Answers: 55
#50

Re: Unbeatable Wire Pull

02/11/2015 6:30 PM

Wise decision. Good luck with the next one.

__________________
Though it does seem he frequently has a Swiss Army knife or Leatherman and a roll of duct tape with him.
Register to Reply
Register to Reply 53 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dj95401 (2); Doorman (2); EV1guy2004 (4); GW (1); HiTekRedNek (1); Jimh77 (3); Johny451 (1); Just an Engineer (2); Massey (2); Mr Fixit (1); MRC (1); old salt (2); Original_Macgyver (3); PapaJohn (1); RAMConsult (1); redfred (4); Rixter (1); roy hammy (1); setlock77 (2); SHOCKHISCAN (1); SolarEagle (2); spades (2); Stuart21 (1); tonyhemet (1); Unredundant (4); Usbport (2); WAWAUS (2); WJMFIRE (1); Wrench twirler (1); Wwwheaty (1)

Previous in Forum: HP Consumed by a Hydraulic Pump   Next in Forum: Nice Film for Mechanical Engineer

Advertisement