Maximum Power Consumption Of PLC Modules Mounted On DIN Rail

02/10/2015 2:42 AM

I want to know about Maximum power consumption of PLC modules mounted on DIN Rail. Currently I am using Siemens S7-200 PLC.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Maximum power consumption of PLC modules mounted on DIN Rail

02/10/2015 5:02 AM

The manufacturer's documentation should give details. If not (or you cannot find it), contact Siemens directly. http://w3.siemens.co.uk/home/uk/en/Pages/ContactUs.aspx

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Score 1 for Good Answer
Power-User

Join Date: May 2008
Posts: 136
Good Answers: 2
#2

Re: Maximum power consumption of PLC modules mounted on DIN Rail

02/10/2015 5:49 AM

The consumed power depends on the industrial process required to be achieved by the PLC , I mean the number and kind of both sensors & actuators used in that process,... and accordingly, you can determine the Siemens brand to use... As you know there are a number of Siemens' PLCs.
Hope this helps. ,

__________________
Just live and .. Learn!!
Register to Reply
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#3

Re: Maximum power consumption of PLC modules mounted on DIN Rail

02/10/2015 6:16 AM

Alternatively measure current and voltage over time. Thats at least how I think that works most of the time.

__________________
Common Sense Dictates
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Maximum Power Consumption Of PLC Modules Mounted On DIN Rail

02/10/2015 8:54 AM

How did you find this forum??

Use whatever skills that you posses to find the web site of the maker of the device and look at the specs.

Tips to Effective Internet Searching - Hannon Library

Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5

Re: Maximum Power Consumption Of PLC Modules Mounted On DIN Rail

02/10/2015 10:02 AM

Everything on an S7-200 works off of a 24VDC power supply. So if you are attempting to determine the correct size of power supply to run your configured PLC, you must get the data sheets of each module, which will tell you the peak power consumption of that module. Add them all together and your 24VDC PSU capacity must equal or exceed that value. Anything else connected to the I/O modules is not consuming power separately.

And by the way, the DIN rail has nothing to do with it, it is just the mounting form factor. The S7-200 has little ribbon cable connectors for each module which connect in series to build a back-plane bus as you go, and that bus is what you are feeding with the 24VDC PSU.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#7
In reply to #5

Re: Maximum Power Consumption Of PLC Modules Mounted On DIN Rail

02/10/2015 12:37 PM

I agree with JRaef. With the variety of input and output modules, the total power consumed and controlled is going to be a function of the overall system layout.

If you are trying to size a 24 VDC power supply, take care that you are not stingy. That is to say it is much better to have plenty of capacity in the DC power supply than to try to come close to the actual needs.

If the power supply capacity is too close to the required power, the PLC may start flipping out and reboot over and over. Be generous. You never know when you will want to add a few more bells and whistles on that 24 VDC buss.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Power-User
Hobbies - Musician - New Member

Join Date: Dec 2014
Posts: 418
Good Answers: 3
#8
In reply to #7

Re: Maximum Power Consumption Of PLC Modules Mounted On DIN Rail

02/10/2015 10:57 PM

Just add dedicated power supply separatety just for CPU.

__________________
"When I thought I exceeded to be wise but wisdom was far from me" -King Solomon
Register to Reply
Power-User
Hobbies - Musician - New Member

Join Date: Dec 2014
Posts: 418
Good Answers: 3
#6

Re: Maximum Power Consumption Of PLC Modules Mounted On DIN Rail

02/10/2015 10:23 AM

Get a multimeter, get voltage and current reading and multiply it--this is the actual power.

If you want the rated Wattage, look at the back or at the side of your power module, a specification data sheet/label should be there, and read what it is rated. Done.

__________________
"When I thought I exceeded to be wise but wisdom was far from me" -King Solomon
Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ali18 (1); IdeaSmith (1); JohnDG (1); JRaef (1); Kulas (2); lyn (1); NotUrOrdinaryJoe (1)

Previous in Forum: 3 Phase VFD Feeding a 2 Phase Capacitor Run Motor   Next in Forum: Boiler Water pH & TDS

Advertisement