Cables in Conduit

02/13/2015 9:41 AM

I have an existing 1" PVC conduit running underground. It is 30' long. I had planned to use the conduit for running 10 gauge stranded wire to power a planned shop in the back yard. I now need to run 75 OHM coaxial video/power cable for my video surveillance camera. Is it acceptable to run the coax with the 10 gauge wires? I was concerned about electrical interference with the coax.

Thanks,

Don

__________________
The only people who don't make mistakes are those who don't try.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Cables in conduit

02/13/2015 11:26 AM

Why not just try it and see? If you see a blizzard, it didn't work.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Electrical Engineering - New Member

Join Date: Oct 2007
Location: Sour Lake, TX 30°08'59.68"N 94°19'42.81"W
Posts: 675
Good Answers: 13
#2

Re: Cables in conduit

02/13/2015 12:57 PM

Use double braided coax cable

__________________
Bridge rule #1: Nobody is as good as he thinks about himself nor as dumb, as his partner thinks...
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#3

Re: Cables in conduit

02/13/2015 2:25 PM

What type of wire are you using for your underground run?

It must be rated for wet locations even though it is in conduit, because it is underground. My recommendation is direct burial cable or THWN.

In either case, as long as the insulation is rated for the voltages applied, there is no code reason you cannot do this.

You should not have any crosstalk issues.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Power-User

Join Date: May 2009
Location: S. Louisiana
Posts: 284
Good Answers: 3
#4
In reply to #3

Re: Cables in conduit

02/13/2015 3:17 PM

I was planning on using braided THWN (I believe that is the correct designation for heat and moisture resistance). I already have the coax, although not double braided. I wanted to keep the cross section of the bundle as small as possible. I'll just try it on dry land in a length of conduit, see if it works and go from there.

Thanks.

__________________
The only people who don't make mistakes are those who don't try.
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5

Re: Cables in conduit

02/13/2015 3:26 PM

It might depend on the load, and what equipment is running....in any case it should be quite minimal....which would then depend on the application running...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Power-User

Join Date: May 2009
Location: S. Louisiana
Posts: 284
Good Answers: 3
#6
In reply to #5

Re: Cables in conduit

02/13/2015 3:41 PM

"It might depend on the load, and what equipment is running....in any case it should be quite minimal....which would then depend on the application running..."

Yea, of course, you are right. I plan to run about 60 ft., and I don't think (you know how that goes) I'll use any more than 20 amps/120V at one time. I'll split the service into 240V to have it just in case, and 120V which is all I plan to use in the foreseeable future.

__________________
The only people who don't make mistakes are those who don't try.
Register to Reply
2
Guru
Popular Science - Weaponology - New Member Fans of Old Computers - PDP 11 - New Member Technical Fields - Architecture - New Member Hobbies - HAM Radio - New Member

Join Date: Oct 2009
Location: Maine, USA
Posts: 2168
Good Answers: 71
#7

Re: Cables in conduit

02/13/2015 4:32 PM

If you use a good quality RG6-CATV Coax that's triple shielded you should be OK.

I have two coax like this, along with my main power feed to the house, and several other power feeds in a conduit. Every time we have tested the signal quality on the coax it's been excellent.

__________________
Tom - "Hoping my ship will come in before the dock rots!"
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#8

Re: Cables in conduit

02/13/2015 10:52 PM

For the A/C use a UF or USE rated wiring.Use a 10/3 with ground.

Try to spiral the power as you install it in the conduit.This will help reduce noise.

For the coax,use RG6 gel-filled coax.

This is moisture resistant.

Noise should not be a problem with 60 Hz.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#13
In reply to #8

Re: Cables in conduit

02/14/2015 10:20 AM

I'm not sure about the ground.

He should drive a ground rod at the shop and use that as his ground.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Power-User

Join Date: Apr 2007
Posts: 273
Good Answers: 12
#9

Re: Cables in conduit

02/13/2015 11:37 PM

10 AWG wire seems pretty small for a shop, but that's another matter.

I built a combination outdoor kitchen-bar / swimming pool pump house and ran 4 AWG wire and plain old coax cable for TV. 60 foot run in PVC conduit. Works just fine, no interference.

I haven't tried using it for a computer modem or telephone modem, however.

Register to Reply
Guru
Hobbies - Target Shooting - New Member

Join Date: Jan 2011
Location: Indiana
Posts: 558
Good Answers: 14
#10

Re: Cables in conduit

02/14/2015 8:03 AM

This reminds me of a job, we were running an access control system in a airport shipping hanger. We were putting in a system to cover 10 doors with power and communication cable for the card readers. All of our cabling was rated for what we were doing and worked fine. we had ran all of the wiring for 7 doors and left pull strings for the other 3 doors. Since the customer could not make up their mind on the other 3 doors we completed the job with the understanding of returning later to finish the rest of the doors as soon as they got authorization to do so from home office. Well that lasted for about a month and we got a call that the doors were working sporadically. low and behold what do I find when I get there but a lot of ac on our lines since our equipment was all dc lo-voltage where were we getting the ac. So I trace our cabling to see if some one had crossed our lines with ac and I did not find any thing crossing any of our equipment that was causing the problem. Now I am really wondering what has happened so I start tracing the conduit and what do I see but an extra junction box that we had not installed tied to our system and inside was three 8 gauge wires an (electrician) and I use that term loosely, had used our conduit and our pull strings to do his job of wiring all of the overhead lighting. his wire ran to the end of our conduit where he installed a sub panel. Where it was connected to the lighting that was connected to use as needed to save energy the lights had PIR (passive infer red) controllers on them and sensed you walking in the lanes on the shipping storage floor, as you walked down the aisle it turned on mercury vapor or metal halide lights I don't know which but it was more then the shielding we were using could handle. Needless to say he had to make a return trip to do his job the second time and re-pull the three pull cables we were to install the next month. He was not happy nor was his company management.That was why it was an intermittent issue as it only happened when some one was on the floor. It was enough to drive you to drinking but since I don't drink it drove me to women oh yea the wife wasn't happy nor was my head since her favorite frying pan landed upside of my head maybe I should not check out other women when she is around, you think I would have learned that by now. *(;p)

__________________
Four boxes keep America Free The soap box, The ballot box, The jury box, & The cartridge box.
Register to Reply Off Topic (Score 5)
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#14
In reply to #10

Re: Cables in conduit

02/14/2015 11:34 PM

OK, I've got a worse situation. One of our engineers went for a startup of a new steel mill in Spain. Everything went well and the equipment tested fine and was running at above rated production and then they brought in the owners personel. The production slowed drastically and motors started tripping at ramdom. Checking the system they found that after the electrical equipment was installed, the plumbers had connected the drains from the bathrooms into the electrical conduits because the design called for a short vertical riser from the 90's into the motor to make the pulling of the wire easier. The waste was being piped right into the junction boxes of the motors under the restrooms. I am willing to bet that the electricians who had to clean up did not say nice things about plumbers.

Register to Reply Off Topic (Score 5)
Power-User

Join Date: May 2013
Posts: 351
Good Answers: 22
#11

Re: Cables in conduit

02/14/2015 8:13 AM

I see 2 problems. One is the code requirements. Most jurisdictions will not allow Power cables and LV electronics cables in the same conduit. If you are going to have an inspection, you should review local requirements. Second is that if you have a failure of the AC line within the conduit it will most likely destroy all electronics connected to the coax at each end.

However, it should work just fine because the intent of coax is to shield out the interference and the frequencies that shop tools produce are easy to shield.

Calculate that the fill factor is adequate (check code). Don't just put the conductors in the conduit to check. If there are any bends the conductors will bind if you exceed the recommended fill. If there are bends be sure to allow the individual wires to slip against each other. (As in do not tape them together) Use 2 people, one to pull and one to guide the wires in carefully. Go slow and steady. Use lots of proper lube.

Register to Reply
Power-User

Join Date: May 2009
Location: S. Louisiana
Posts: 284
Good Answers: 3
#12
In reply to #11

Re: Cables in conduit

02/14/2015 8:45 AM

Thanks to all of you for your constructive comments.

I already have my permit for the garage/shop and there should be no inspection since I am providing power from my existing system. That's just how it works here. I may go ahead and use 8/3 service instead of 10/3. The largest power user may be from hand power tools and possibly a small-scale biodiesel lab.

Permits and inspections are a little tougher then in years past. For the last house I built in 1984, in a rural area, the only requirement was that I had to have a percolation test for my septic system. I built all of the plumbing and electrical systems myself, although I did have friends in the trade perform informal inspections. And, there were some minor adjustments I had to make.

Inspections and code requirements can be a pain but sometimes they save us from ourselves, and neighbors.

Thanks again,

Don

__________________
The only people who don't make mistakes are those who don't try.
Register to Reply
Commentator
United States - Member - VT

Join Date: Jun 2014
Posts: 59
Good Answers: 4
#17
In reply to #12

Re: Cables in conduit

02/16/2015 8:21 AM

Good luck pulling 10-3 UF in a 1" pipe, much less 8-3. Those are a flat cable and you can't just go by the conductor count/ conduit fill tables. I ran 1-1/4" conduit out to a shed for 10-3 UF, and even then I made absolutely sure the cable fed into the pipe without twisting. If you want a larger wire size in 1" conduit, you will be using individual conductors (THHN, etc), and you do want a ground rod at the far end as well.

__________________
Teach your cat to write
Register to Reply
Power-User

Join Date: May 2009
Location: S. Louisiana
Posts: 284
Good Answers: 3
#18
In reply to #17

Re: Cables in conduit

02/16/2015 11:00 AM

I was actually planning to use individual braided wires in the conduit. I know that would be a lot easier than pulling the UF. I've done the same with 12/3 in 3/4" conduit.

FWI: I connected three 100' and one 65' coax cables (total 365') to my surveillance camera it works fine. It's the Defender system that I purchased from Home Depot on line.

Thanks,

Don

__________________
The only people who don't make mistakes are those who don't try.
Register to Reply
Guru
Canada - Member - New Member

Join Date: Jul 2013
Location: Canada but south of 49
Posts: 895
Good Answers: 20
#19
In reply to #12

Re: Cables in conduit

02/17/2015 8:29 AM

Good choice to go with the 8/3 power cable. You never know what you may want to power up in the garage. Better to "oversize" it now than be undersized later.

__________________
Never stop learning
Register to Reply
Active Contributor

Join Date: Dec 2013
Location: Ohio, USA
Posts: 15
Good Answers: 4
#15

Re: Cables in Conduit

02/15/2015 1:21 AM

While not part of the National Electrical Code I normally deal with ... I believe the answer would be "not allowed" per §820.133(A)(1). A note to §820.133 Installation of Coaxial Cables and Equipment, in the 2014 NEC Handbook says:

  • Jackets of coaxial cable do not have sufficient construction specifications to permit them to be installed with electric light, power, Class 1, non-power-limited fire alarm circuits, and medium- and high-power network-powered broadband communications cable. Failure of the cable insulation due to a fault could lead to hazardous voltages being imposed on the Class 2 or Class 3 circuit conductors.
Register to Reply
Power-User

Join Date: May 2009
Location: S. Louisiana
Posts: 284
Good Answers: 3
#16
In reply to #15

Re: Cables in Conduit

02/15/2015 7:47 AM

Thanks Oscar!

__________________
The only people who don't make mistakes are those who don't try.
Register to Reply
Register to Reply 19 comments