Regarding MCBs Rating

02/15/2015 9:32 PM

If we have branch MCBs rating of 16A, 16A, 6A, 6A, 16A - then the rating of the main parent MCB above the branch MCB will be the sum of all of them? Or, it should be at least 20% above the sum of value of those ratings? Their sum would obviously be 60 Amps - and the next available rating is 63 Amps. So can 63 A be selected - as it is the highest available MCB rating? But as far as I know we also have MCB ratings upto 125 A. But if we allow 20% of room then - it is 60*1.2 = 72 Amps; so next higher available is 80 Amps MCB.

Regards,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Regarding MCBs Rating.

02/15/2015 9:37 PM

"...as far as I know..." if you have to ask the question you shouldn't be doing the work...

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Regarding MCBs Rating.

02/15/2015 10:14 PM

If you have to ask, find other work.

Or, buy a copy of BS 7671 or the NFPA 70: NEC®

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3

Re: Regarding MCBs Rating

02/15/2015 11:57 PM

consider discrimination between breakers as well as load and diversity factors etc

__________________
pnaban
Reply
3
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Regarding MCBs Rating

02/15/2015 11:59 PM

If diversity is taken into account, the main breaker could be somewhat less than the sum of the sub-breakers. OTOH, if future expansion is possible, it could be larger. No single answer is possible.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Good Answer (Score 3)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5

Re: Regarding MCBs Rating

02/16/2015 12:23 AM

In addition to maximum simultaneous load consider maximum starting current too.

__________________
pnaban
Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#6

Re: Regarding MCBs Rating

02/16/2015 12:55 PM

So, are all your sub-circuits' breakers all passing their rated current all the time? And, if you intend changing breakers for a higher rating, are you certain that the main feeder can take it? Your ball.

__________________
Good moaning!
Reply Score 1 for Good Answer
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #6

Re: Regarding MCBs Rating

02/16/2015 11:55 PM

If connected load increases,upgrading of MCBs is necessary. Also selecting correct type(B,C,D etc) of MCB is important.

__________________
pnaban
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#8
In reply to #7

Re: Regarding MCBs Rating

02/16/2015 11:58 PM

Bear in mind that the OP need a solution. If this arises in your work place what an engineers should do without beating round the bush.

__________________
pnaban
Reply
Power-User

Join Date: Sep 2011
Posts: 267
Good Answers: 7
#9

Re: Regarding MCBs Rating

02/17/2015 12:54 AM

If you had say a 60 A (sized properly) feed to a sub-panel, you could have a 200 A breaker in the sub panel and it would be OK.

Reply
Power-User

Join Date: Jan 2015
Location: Johannesburg, South Africa
Posts: 248
Good Answers: 3
#10

Re: Regarding MCBs Rating

02/17/2015 2:21 AM

The Main MCB max rating is a reflection of the current capacity of the feeding/supply cable from the Supplier. I will assume that you do not know how to find the rating of that cable if you do not know how to calculate combined rating. Legaly you are commiting an offence working in a db without qualifications and it is better to get a qualified person to do this. Electricity have laws because people can not see the danger you expose them to doing things you know nothing of. The regulations is to protect the people arround you and the buildings you can fry/burn down with the workers inside. Be responcible and stand back untill you finish your education and apprentice period. If you are in training or an apprentice you will be reporting to somebody with the answers and dtailed explinations.t

__________________
Tragedy for Engineers is thinking they know so much that they can not learn from any body else.
Reply Off Topic (Score 5)
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#11

Re: Regarding MCBs Rating

02/17/2015 2:47 AM

Breakers are sized to protect the conductors.

Your main breaker should have a rating that suits your feed cable/drop line size.

__________________
Difficulty is not an obstacle it is merely an attribute.
Reply Score 1 for Good Answer
2
Power-User

Join Date: Nov 2011
Posts: 286
Good Answers: 15
#12

Re: Regarding MCBs Rating

02/17/2015 3:10 AM

No. THe breakers are sized to protect the wiring and installation not each other. It is useful to get discrimination between the breakers and as you say a 6A should trip before a 10A. There are tables and curves from which you can determine this. Agree with the other posters - there are too many questions you have not asked to be able to continue with this safely. Suggest handing this over to someone else. Good if this someone else isn't the fire brigade.

Reply Good Answer (Score 2)
Reply to Forum Thread 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (1); KeepItSimpleStupid (1); lyn (1); Oomborrie (1); pnaban (4); RAMConsult (1); silverfox (1); Tornado (1); Wal (1)

Previous in Forum: Level Transmitter   Next in Forum: What is the Most Important Logic Gate?

Advertisement