Previous in Forum: Can Fire Hydrants Run in Floors (with False Ceilings) Above Cable Trays?   Next in Forum: Earth Drill Machine for Earth Rod
10 comments
Enquiry
03/04/2015 3:57 PM
Hello fellow engineers, please can you help me with some type of tests that are conducted on current transformers.
Thank you
Re: Enquiry
03/04/2015 4:12 PM
Someone here may help you.
What type of transformers are you testing, and what types of tests are you wishing to perform?
If you can't answer these questions, I'll assume this is a homework (or work related) question.
Then you will be directed to a search engine to look for "transformer tests".
We don't do homework here. Here's a hint: C57.154-2012 - The IEEE Standards Association
Re: Enquiry
03/07/2015 8:37 AM
I want to test a current transformer. To confim if its turns ratio (4000/5 amps ) is okay and also a test that will help indicate the polarity of the Current transformer and grounding
Re: Enquiry
03/07/2015 9:42 AM
Testing the current to voltage transfer of any circuit requires test equipment capable of independently measuring current and voltage. The preferred instrument for these measurements is an oscilloscope with a clamp on current probe and the typical voltage probe that comes with any oscilloscope. If you do not have access to this instrument or if you do not understand how to use it then there is very little we can do to help you.
Re: Enquiry
03/04/2015 4:24 PM
Two related tests come immediately to my mind. VSWR measurement into an ideal load and insertion loss deviation from ideal transfer.
Re: Enquiry
03/04/2015 4:38 PM
Re: Enquiry
03/07/2015 8:57 AM
Its not an home work.Its a problem and as a young man am tasked to solve the problem.I was told the problem has been there for 25 yrs and over.I want to solve it-i wil need your views
Good Answers: 225
Re: Enquiry
03/04/2015 6:26 PM
Whichever tests that you decide to do, don't open circuit the secondary while ever there is current flowing through the primary/core.
Good Answers: 131
Re: Enquiry
03/05/2015 10:34 AM
Typical tests on CTs used for instrumentation, control, and protective relaying are a ratio test to verify how close it is to nameplate ratio, and excitation / knee voltage test to verify its saturation point. You could also do an insulation resistance ("megger") test.
Re: Enquiry
03/05/2015 11:15 AM
The current transformers are tested for lead content and a variety of other toy safety standards.
[Sorry, but I couldn't hold back any longer.]
Good Answers: 73
Re: Enquiry
03/05/2015 11:51 AM
Perhaps you are asking how to select an appropriate CT for a given signal. Some CT's are so sensitive that they distort the signal. You may also be interested in frequency response. The problem is that you must know some things about the current you want to monitor in order to select an appropriate CT.
Would you care to elaborate?
Register to Reply 10 comments