Anonymous Poster #1

Line Monitoring for Digital Output

03/15/2015 5:13 AM

Hi,

How line monitoring can be implemented for a digital output (PLC/DCS/ESD) which is providing output to field device (solenoid valve) through an interposing relay.

Regards,
Vimal

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Line monitoring for Digital output

03/15/2015 12:45 PM

Eh? Go again?

__________________
Good moaning!
Reply
2
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Line Monitoring for Digital Output

03/15/2015 6:38 PM

Reply Good Answer (Score 2)
2
Guru

Join Date: Jul 2010
Posts: 669
Good Answers: 176
#3

Re: Line Monitoring for Digital Output

03/15/2015 10:26 PM

There are redundant DO's for this SIL 2 safety app. One sourcing, one sinking.

The solenoid is the load:

Reply Good Answer (Score 2)
3
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#4

Re: Line Monitoring for Digital Output

03/16/2015 9:24 AM

A simple high-impedance indication light paralleling the load devices (interposing relay coil & solenoid) would give adequate visual verification for both.

If you need details on voltage level installing high impedance digital or analog voltage meters in parallel to the load devices (interposing relay coil & solenoid) will give visual indication.

If you need current monitoring installation of a metering shunt or current monitor relay in series with the signal to each device will work.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Reply Good Answer (Score 3)
Power-User
Hobbies - Musician - New Member

Join Date: Dec 2014
Posts: 418
Good Answers: 3
#5

Re: Line Monitoring for Digital Output

03/17/2015 12:09 PM

It needs to be decoded from digital to analog discrete i/o. You need discrete output module or you may choose solenoid valve which features off/on led status.- thats the safest. I/o Wiring of field instruments could sometimes fail and deliver wrong inputs. The same would happen if you got the signal from the controller. The safest is direct on field instrument 1step proces.

__________________
"When I thought I exceeded to be wise but wisdom was far from me" -King Solomon
Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#6

Re: Line Monitoring for Digital Output

03/17/2015 12:13 PM

It all depends on what you mean by "line monitoring". If you want a gadget like a pilot light, connect it in parallel with your solenoid.

If you want statistical data or trending data, buy a HMI software package like what you will find at www.Indusoft.com and monitor the PLC. You get 40 hours of trial and error time before the demo license shuts down.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#7

Re: Line Monitoring for Digital Output

03/24/2015 11:03 AM

Install a 110VAC light parallel to the energized solenoid, since this will not be energized except when the interposing (definite purpose contactor) relay is closed. I presume you will use a N.O. interposing relay, since this would cut down on 110 VAC power usage. If this is a critical application where you need to see the active solenoid itself on screen, then you should parallel the solenoid voltage with a suitable bridge circuit (convert to some DC voltage), then to ADC input (analog-digital converter) and then the digital version of the signal is back into the PLC/HMI. Just remember that the "more moving parts" you insert into the picture the more that can go wrong, go wrong, go wrong.....

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Reply to Forum Thread 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Crabtree (1); Iris (1); James Stewart (1); Kulas (1); lyn (1); NotUrOrdinaryJoe (1); SHOCKHISCAN (1)

Previous in Forum: Annubar Discrepancy   Next in Forum: Auto Regressive Model

Advertisement