Liquid Level Sensors

06/10/2015 10:48 AM

Hello Engineers,

I work for a company called Simple-Fill and we've been having some major problems finding a suitable level sensor/switch to utilize in the system we've been designing. The switch has to be top mounted with a 3/4" UNF or NPT port, withstand a pressure of 4500 psi, and a temperatures in the 50-90C range. We do not want to use differential pressure as the tank (12" diameter, 6' height) fills rapidly and contains a gas at a high pressure, which would lead to potential errors in such an indirect measurement. We have seen potential thermal dispersion switches, but as the temperature changes rapidly as well we fear these could lose calibration. Lastly, cost is very sensitive as we are a startup so the $4k-7k continuous sensors of companies like VEGA and Emerson are out of the question. We are better suited for a more cost effective solution, which in my research appears to be a switch. Any and all suggestions are welcome, thanks guys!

David Hakanson

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Jun 2014
Posts: 623
Good Answers: 33
#1

Re: Liquid Level Sensors

06/10/2015 10:55 AM

This link might give you some ideas you may not have considered yet, good luck!

http://www.sensorsmag.com/sensors/leak-level/a-dozen-ways-measure-fluid-level-and-how-they-work-1067

__________________
Hey Isaac, catch! ...oops, that's gonna leave a mark...
Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: Jun 2015
Posts: 14
#4
In reply to #1

Re: Liquid Level Sensors

06/10/2015 11:21 AM

Thanks for the info Massey!

Register to Reply
3
Power-User
Engineering Fields - Manufacturing Engineering - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Apr 2008
Location: USA
Posts: 113
Good Answers: 4
#2

Re: Liquid Level Sensors

06/10/2015 11:15 AM

Rather than fluid level, can you fill by weight? Previously, I worked at a facility that filled cylinders with various gases, and our best and easiest means to get an accurate and repeatable fill was by weight. An accurate digital scale should fill the requirement.

Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: Jun 2015
Posts: 14
#3
In reply to #2

Re: Liquid Level Sensors

06/10/2015 11:20 AM

Do you have any idea if we could install such a system on a particular tank? The vessel we're measuring liquid level in is part of a larger system and therefore immobile, so we would not be able to place it on a scale.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5
In reply to #3

Re: Liquid Level Sensors

06/10/2015 11:50 AM

Build in load cells that constantly monitor the weight into the support structure of the tank, no need to place it on a scale.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Active Contributor

Join Date: Jun 2015
Posts: 14
#6
In reply to #5

Re: Liquid Level Sensors

06/10/2015 11:59 AM

Do you have any recommendations of suppliers to look at? in addition, if the load cells are to be within the tank I assume they would need to be compatible with our liquid?

Register to Reply
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Jun 2014
Posts: 623
Good Answers: 33
#7
In reply to #6

Re: Liquid Level Sensors

06/10/2015 12:04 PM

Sounds like you may be a little unfamiliar with load cells. The load cells can be external the tank even under the structure supporting the tank. You can even put them under the floor that supports the structure that supports the tank.

__________________
Hey Isaac, catch! ...oops, that's gonna leave a mark...
Register to Reply
Active Contributor

Join Date: Jun 2015
Posts: 14
#8
In reply to #7

Re: Liquid Level Sensors

06/10/2015 12:28 PM

Right, I guess I should probably explain the unit in more detail; the vessel is part of a larger unit, and is suspended in the frame (about a foot or so off the ground). So, my question is, where would the load cells go? If the load cells are mounted on bottom of the vessel (externally), would they have the capacity to sense changes in weight due to filling without the vessel contacting the ground?

Thanks for all the help guys!

Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#9
In reply to #8

Re: Liquid Level Sensors

06/10/2015 12:42 PM

Load cells may be the right choice, but without knowing what else is being supported along with the tank, it could be hard to get into the right range. The most obvious placement is right under a nearby foot. Unfortunately that means that the said foot must not be bolted or welded to the floor.

I'm not sure what it takes to contain 4500 (psi?) but even some scuba divers hose is good to 3000 psi, so I guess there is some serious metal reinforcement involved in the hose. A mesh is what comes to mind, but it all depends on the inside diameter of the plumbing.

A flexible coupling capable of supporting the tank would be a good start. Then support the tank by a floating foot to the floor. Your load cell would be most accurate this way. But if that is not permitted, well then, never mind...

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Active Contributor

Join Date: Jun 2015
Posts: 14
#10
In reply to #9

Re: Liquid Level Sensors

06/10/2015 1:28 PM

The frame supports a few motors, various cooling components, a buffer tank, and a second tank identical to the one we have been discussing (we have to monitor the level in both). Therefore, the frame design is not particularly flexible, which seems to make load cells a bit impractical in this case. I will look into them though as it still appears to be an interesting option. Steel piping is typically what we use in the system, but some heavy duty CNG hose is used in places

Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#13
In reply to #9

Re: Liquid Level Sensors

06/10/2015 10:43 PM

The hoses used on firefighters SCBA's SELF CONTAINED BREATHING APPARATUS have a working press in excess of 4,000psi. They connect the cylinder on the back to the pressure regulator at the chest which feeds the air mask at about 15-20" of water. The big air cylinders used to refill them in a cascade system have a working rating of well in excess of 7,500 psi. OP should contact a hi press hose manufacturer. If no info there call Scott Safety Products (years ago was Scott Aviation for the breathing air systems used on war planes) or MSA. Ask them where they get their hi press hoses.. Also if the tank is hung load cells could be installed within the hanging gear that is suspended with. This is used sometimes in the chemical industry for the same problem as OP has. Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Active Contributor

Join Date: Jun 2015
Posts: 14
#15
In reply to #13

Re: Liquid Level Sensors

06/11/2015 12:05 AM

Thanks for the tip on contacts for hose; we had been having a bit of issues finding good hose as well. Are load cells particularly susceptible to vibrations? Since there are motors connected to the same frame, this was a worry of one of our engineers.

Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#30
In reply to #15

Re: Liquid Level Sensors

06/11/2015 8:16 PM

If not with the load cell it can be done with the electronics before the load cell display. Almost anything can e done if you are willing to pay for it or develop it. Contact a load cell scale manufacturer or supplier. If they can weigh 234,000 lbs rail cars they can handle the design you are working with. Good Luck, Old Salt

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#32
In reply to #3

Re: Liquid Level Sensors

06/12/2015 3:31 PM

Build in load cells on the tank support, silly man.

What really is this magic liquid that has a vapor pressure of greater than 4500 psig at 90C? Why is this kept so hot? Something not sitting right on this end, as this thread appears to be looking for a place to detonate. If the temperature swings as wildly as you suggest, this thing is less of a storage vessel, and more of a B.L.E.V.E. waiting to happen. I think someone has latched onto a very bad idea.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Jun 2011
Location: Mossel Bay, SA
Posts: 777
Good Answers: 21
#18
In reply to #2

Re: Liquid Level Sensors

06/11/2015 6:16 AM

GA.

I have experience with fire-suppressant gas cylinders..same thing. Nothing like a good scale!

Register to Reply
2
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#11

Re: Liquid Level Sensors

06/10/2015 5:54 PM

Something in a load cell, perhaps?

Electronic scales for suspended loads - Coop Bilanciai

Register to Reply Good Answer (Score 2)
Guru

Join Date: Jun 2011
Location: Mossel Bay, SA
Posts: 777
Good Answers: 21
#23
In reply to #11

Re: Liquid Level Sensors

06/11/2015 9:31 AM

GA and probably the cheapest and most practical solution.

Now, to find a skyhook...

Register to Reply
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#12

Re: Liquid Level Sensors

06/10/2015 7:31 PM

DP

>We do not want to use differential pressure as the tank (12" diameter, 6' height) fills rapidly and contains a gas at a high pressure, which would lead to potential errors in such an indirect measurement.

How quickly is this vessel filling? Current DPs sample from 5-10x per second.

Does the liquid vary greatly in density over the temperature range? The DP-to-level calculation assumes a given density. Any density change from the assumed density is a proportional error in level conversion.

4500 psig is near the maximum allowable working pressure, 90 Deg C near the max process temp limit, but unless the tank was filling in 2 seonds I don't see why DP wouldn't work (assuming instrument handles the process conditions).

Load cells

Weight is also subject to level change with density change. It's great as a mass measurement, X.xx pounds/Kg, but suffers like DP does with level varying with density.

Using flexible connections to the vessel is key, because rigid connections (electrical, piping, supports other than load cells) can be a source of error. with the choice tension or compression load cells, a tank can be suspended and weighed.

Nuclear

Shoot some gamma rays through the vessel. Ronan is one I spec'd once.

Register to Reply
Active Contributor

Join Date: Jun 2015
Posts: 14
#14
In reply to #12

Re: Liquid Level Sensors

06/11/2015 12:00 AM

DP

The tank fills in about 7.5 seconds, but this is not the main problem with dp; the main issue is that based on tank dimensions, we would only have around 8200in^3 of liquid. Since the pressure of the gas above the liquid maxes out at 4500psi, we are worried that the added pressure of the liquid will be insignificant in comparison, leading to erroneous readings. If this is not the case though, I'd love to hear a counter argument.

Load Cells

Due to our frame being essentially unchangeable and vibrations throughout the unit caused by the motor, we'd like to avoid this if possible.

Nuclear

We got a quote from Berthold on a gamma sensor; that bad boy was >$7000 just for point level detection!

Register to Reply
Guru

Join Date: Dec 2010
Location: North West England
Posts: 1170
Good Answers: 153
#16

Re: Liquid Level Sensors

06/11/2015 3:39 AM

Davis Instruments, 0-5000psi, SS316 wetted parts, digital display + 4-20mA output + 2x pnp digitally set switched set points, accuracy 1% of full range. $414. You will need an adaptor to fit 1/4"M NTP switch to 3/4" socket. Check on web for further details.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2015
Posts: 14
#20
In reply to #16

Re: Liquid Level Sensors

06/11/2015 9:20 AM

My worry here is that in our 6 ft tank, since the density of the fluid is very similar to water, we have about 72" WC. This is only about 3psi; 3psi is only 0.067% of 4500psi.

Register to Reply
Guru

Join Date: Jun 2011
Location: Mossel Bay, SA
Posts: 777
Good Answers: 21
#17

Re: Liquid Level Sensors

06/11/2015 6:13 AM

Try Endress & Hauser or Krone Instruments.

You give up too easy...

Register to Reply
Active Contributor

Join Date: Jun 2015
Posts: 14
#19
In reply to #17

Re: Liquid Level Sensors

06/11/2015 9:10 AM

I had long conversations with both Endress and Huaser and Krohne. From both, there were only two options, Krohne's OptiFlex and E&H's LevelFlex. I was advised by both of their engineering department to look elsewhere for fear of losing calibration due to rapidly changing conditions since both systems are GWR. You may be too quick to judge

Register to Reply
Guru

Join Date: Jun 2011
Location: Mossel Bay, SA
Posts: 777
Good Answers: 21
#25
In reply to #19

Re: Liquid Level Sensors

06/11/2015 10:26 AM

Not too quick..you only mentioned two manufacturers that you tried !

Nevertheless, I want to alert you to the fact that if you are working with a flammable gas, all your electrics will need to be certified Exd (certified flame/explosion proof).

Caution is the word here, else your start-up may well shut down at first batch.

Just for interest there are hand-held level detectors available. Look here:

www.google.co.za/webhp?sourceid=chrome-instant&rlz=1C1VFKB_enZA613ZA615&ion=1&espv=2&ie=UTF-8#q=coltraco%20portalevel

Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#34
In reply to #19

Re: Liquid Level Sensors

06/17/2015 11:27 AM

I suggest you contact all of the following vendors and get their input on what they can do for you:

Emerson Rosemount

www2.emersonprocess.com/en-us/brands/rosemountanalytical

Omar VEGA

www.vega-americas.com/en/index.htm

Siemens

www.industry.usa.siemens.com/.../level_guide_en.pdf

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Active Contributor

Join Date: Jun 2015
Posts: 14
#35
In reply to #34

Re: Liquid Level Sensors

06/17/2015 11:54 AM

These are all great companies, I contacted all of them and met with both Emerson and VEGA personally. Unfortunately they and Siemens could not provide anything under about $4500. Siemens had a capacitance switch for $2200, but the specs weren't quite up to par; Ametek Drexelbrook offered a cheaper and more robust system. However, all of these capacitance systems seem to have issues with the rapidly cycling; replacing an expensive unit like this every year is not very efficient.

Register to Reply
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Jun 2014
Posts: 623
Good Answers: 33
#22

Re: Liquid Level Sensors

06/11/2015 9:30 AM

Yea, given those internal temperatures & pressures it may be very volatile inside the tank so Weighing the tank via load cell or some other means seems like the best approach.

__________________
Hey Isaac, catch! ...oops, that's gonna leave a mark...
Register to Reply
Active Contributor

Join Date: Jun 2015
Posts: 14
#24
In reply to #22

Re: Liquid Level Sensors

06/11/2015 9:42 AM

Another issue is that similarly to DP, the weight of the tank is about 1600lbs (has to be sturdy to handle the high pressures), so unless the load cells are >=0.01% accurate, it'd be pretty tough to pick up changes in liquid level as the weight of the liquid would contribute so little to the overall weight

Register to Reply
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#26

Re: Liquid Level Sensors

06/11/2015 10:43 AM

DP

There's no reason why DP wouldn't provide a head pressure measurement.

DP is designed to 'see' relatively small differential pressures in the presence of relatively large static pressures.

An industrial DP transmitter mechanically subtracts the low side pressure (vapor) from the high side pressure (vapor + liquid head pressure) so the sensor 'sees' the differential pressure of the liquid head pressure only, which it converts to an electrical signal.

DP transmitters are sized according the range of DP that is desired. 10 feet, (120 inches of water column), is easily within the range of a typical DP cell.

You'd have to consider the MAWP though. If it were me, I'd get the 6000psi option:

But there's still the open question about the stability of the liquid density.

Load cells

Sartorious has load cells whose mounts negate the effects of vibration.

Video shows turbulence due an agitator, but the effect from external vibration is the same, which throws off load measurements that don't negate the effect:

http://tinyurl.com/lq57wvz

Davis switches

I didn't look it up, but is the medium sticky or gooey that will cause switches to 'hang' over time due to build up. Good price if the technology is compatible.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2015
Posts: 14
#27
In reply to #26

Re: Liquid Level Sensors

06/11/2015 11:05 AM

With DP, the sensors are typically 0.1-0.25% accurate, so I'll assume best case and say one we were to use is 0.1% accurate. Lets say the tank is empty, and the gas is at 4500psi. If the low side somehow gets this reading spot on (0.0% error), it will read 4500psi. If the high side reads this with say a 0.05% error, pretty good based on the maximum variance of the sensor, it will read 4502.25 psi, meaning a 2.25psi liquid head pressure, which would be about 60" WC. That's a problem; am I missing something on how these operate?

I will look into those load cells, as if they negate motor vibrations they could prove useful. once again though they are non ideal due to the frame build.

Register to Reply
3
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#28
In reply to #27

Re: Liquid Level Sensors

06/11/2015 11:52 AM

> tank is empty, and the gas is at 4500psi

Low side (vapor) = 4500 psi

high side (vapor) = 4500 psi

high side 4500 minus low side 4500; pressure applied to the sensor = 0 = empty

You are thinking that the low side and high sides are measured independently and then subtracted from one another as though one was subtracting one gauge pressure pressure reading from a second gauge pressure reading. That's not the way it works, otherwise the error would be very large (as you calculate) and people wouldn't pay for DP.

That's why my previous statement was that a DP mechanically subtracts low from high and the sensor sees only the differential pressure and that's what it reports. The sensor does not 'see' the high or low static pressures independently.

The DP accuracy spec is for the differential pressure measurement, not high side or low sides independently.

An accuracy spec of 0.1% for a DP cell is 0.1% of DP span at 120 in w.c. or 0.12" w.c.; a long way from 60"wc.

By the way, somewhere I have a note I wrote 20 years ago on why one shouldn't attempt to measure a differential pressure with two separate gauge pressure measurements, for exactly the reason you've assumed; the combined error of the gauge pressure measurements can produce a very erroneous DP, in fact in flow measurements, it could appear that there was reverse flow (depending on the polarity of combined error).

DP has been used for decades for flow measurement at high static pressure, but with relatively low DPs (100" w.c.). It can be and is used for high pressure vessel level measurement; it just isn't as common because there is less of that measurement than there is high pressure/high temperature flow measurement.

Register to Reply Good Answer (Score 3)
Active Contributor

Join Date: Jun 2015
Posts: 14
#29
In reply to #28

Re: Liquid Level Sensors

06/11/2015 11:57 AM

Fantastic explanation, this clears up the issue a lot. DP now sounds like possibly the most viable option for us. Thanks a lot Carl

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#36
In reply to #29

Re: Liquid Level Sensors

06/17/2015 12:48 PM

Yes, load cell or DP is a good answer, for pressurized vessels as this. Since you are filling the vessel so rapidly, then your system will have to be tuned for extreme rapid response.

Does the vessel remain in place, or is it filled and removed for next vessel? Is the contents of the vessel corrosive? flammable? All considerations, especially safety must be taken into account prior to final answers.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Commentator
United States - US - Statue of Liberty - How's it going?

Join Date: Oct 2012
Location: USA
Posts: 95
Good Answers: 4
#31

Re: Liquid Level Sensors

06/12/2015 9:23 AM

Try looking for rf sensors. They can be used for high pressures, temps, and various materials.

http://www.sensorsmag.com/sensors/leak-level/a-dozen-ways-measure-fluid-level-and-how-they-work-1067

This web page has some good info about different ways to measure tank levels.

It seems Massey got the link before me. Good luck.

__________________
If you can't explain it simply, you don't understand it well enough. AE
Register to Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#33

Re: Liquid Level Sensors

06/17/2015 9:29 AM

Look through K-tek Magnetostrictive Level Switches

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply
Register to Reply 36 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Carl_E (3); d.hakanson (13); Hilton (5); James Stewart (2); jhhassociates (1); lyn (1); Massey (3); North of 60 (1); NotUrOrdinaryJoe (1); Noudge79 (1); nvirciglio (1); old salt (2); SHOCKHISCAN (1); Ti QE (1)

Previous in Forum: Expensive SCADA Based Pump Scheduler For Energy Savings   Next in Forum: Astro-Med MX-8000 Series Data Acquisition

Advertisement