Pump VFD

08/01/2015 12:19 PM

If I put VFD on 50HP 460V pump and decrease speed 10%, how much do I save energy in percentage? Is it proportional or not?

__________________
ZORANDODO
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Pump vfd

08/01/2015 12:39 PM

It's not worth the effort.

The cost of the VFD and installation will never be recovered on a pump installation with a 10% speed reduction..

Trimming the impeller will be much cheaper.

Throttling the output 10% will be the easiest way to reduce power consumption.

My advice, DO NOTHING.

Talk to a pump expert.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#2

Re: Pump vfd

08/01/2015 12:56 PM

I decry it will depend on a lot of things you are not telling us.

The added losses of the VFD could eat up all running speed efficiency at the pump. A decrease in speed could also move the pump out of the most efficient speed itself. Then again if your operation requires frequent stopping and starting the higher efficiency of starting with a VFD will help greatly in the overall process. If the impeller is spinning so fast that cavitation is happening the decrease in speed to below cavitation levels will be a significant non-linear improvement. Pumping a compressible fluid will change all of the equations all together.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#3

Re: Pump vfd

08/03/2015 10:29 AM

I agree with redfred

I like to add that your process requirements should dictate your pump requirements and speed.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Pump vfd

08/03/2015 10:38 AM

By pump affinity laws, 1.00 - 0.93 = 1.00 - 0.729 = 0.271 = 27.1% savings. However, as others have noted, there may be a decrease in efficiency, so the savings probably won't be quite that high.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#5

Re: Pump VFD

08/03/2015 12:25 PM

Dear Mr ZORANDODO,

We have studied in our college days that for Pumps (or Fans) the EQUATION IS AS FOLLOWS:

1. Capacity "C" is Proportional to the SPEED - N

2. Pressure "P" is Proportional to the SQUARE of the SPEED - N^2

3. Power "POWER" is Proportinal to the CUBE of SPEED - N^3

You have stated that the speed is reduced by 10% i.e equipment is running now at 0.9 N

So "C" = 0.9 N, Pressure "P" (0.9 x N )^2 = 0.81 x P, and POWER = (0.9 x N )^3 = 0.729 x ORIGINAL POWER at Speed N

Power Saved = (Power consumed at Speed N - Power consumed at Speed 0.9) = (1-0.729) = 0.271 i.e 0.271 x100 = 27.1%

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#6

Re: Pump VFD

08/03/2015 2:55 PM

You need to look at your process requirements, first. A throttling valve will be cheaper than a VFD.

__________________
Good moaning!
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#7
In reply to #6

Re: Pump VFD

08/03/2015 3:19 PM

Agreed.

A quick look at the pump curve should give a ball park indication of power savings.

Unless he's pumping mud, 10% throttling won't over-heat anything either.

Register to Reply
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#8
In reply to #6

Re: Pump VFD

08/03/2015 6:19 PM

Assuming of course that it is a centrifugal pump.

Not a good idea to throttle the output of a PD pump, a recirculating valve would reduce the output but would do nothing for power consumption.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#9

Re: Pump VFD

08/03/2015 8:49 PM

It depends on the design and type of pump as well as the process requirements.

Measure the pump flow and electrical current on the VFD input side and on the VFD output at 100% speed.

Decrease the speed by 10% take flow and current readings at same locations then compare the differences to identify any efficiency gains realized.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (1); dhayanandhan (1); lyn (2); phoenix911 (1); redfred (1); SHOCKHISCAN (1); spades (1); Tornado (1)

Previous in Forum: Check Valve Position   Next in Forum: Radiography or Ultrasonic Testing on Pipe Supports

Advertisement