Psychrometry Test

08/22/2015 5:21 AM

If I have to measure the psychrometry condition of a room under air conditioning, is that true I have to obtain the dry bulb and wet bulb at several location in order to get the average temperature ? Please guide me.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Psychrometry Test

08/22/2015 5:25 AM

You are not only un-guideable, but helpless.

Psychrometrics - Wikipedia, the free encyclopedia

Register to Reply Off Topic (Score 3)
Anonymous Poster #1
#5
In reply to #1

Re: Psychrometry Test

08/22/2015 7:59 AM

Just give the guy the answer -this is not an initiation

Register to Reply Score 1 for Off Topic
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#11
In reply to #1

Re: Psychrometry Test

08/22/2015 11:01 PM

You are being way too harsh! I didn't read it word-buy-word, but I did scan the article of your link twice, and I didn't see any answer to the OP's question.

Clearly, a single reading may be misleading, and it is not likely that the OP needs the precision of a 1000-point matrix. somewhere in between is his answer...

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Psychrometry Test

08/22/2015 5:41 AM

Yes, you should sample several locations. It might be tricky to decide how many and what locations would produce a statiscally acceptable sample set. Don't prejudice by picking either the warmest or coldest, but try to find the most representative.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Commentator

Join Date: May 2013
Posts: 66
#3
In reply to #2

Re: Psychrometry Test

08/22/2015 6:22 AM

Normally, how many sample in practice shall be taken for a good statistic study of the psychrometry ?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #3

Re: Psychrometry Test

08/22/2015 6:31 AM

The more the better, but on rough guess maybe 10 or so. Could be fewer if they aren't prejudiced, but that might be hard to assess.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster #1
#6
In reply to #3

Re: Psychrometry Test

08/22/2015 8:06 AM

It depends on the size of room and the importance or significance of your objective.

Take note that you are measuring air. A fart could easily be dispersed in a small room- bigger room needs bigger or numerous fart to impact. See if there are ventilation or air circulation if its a bigger room.

A smaller room basically needs not to have 100 readings. Would you agree, in the first place to take a thousand of samples for a 3mx2mx2m room? - to make it more likely a representative sample?

Register to Reply
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Oct 2013
Location: Texas.Baytown
Posts: 697
Good Answers: 26
#7
In reply to #3

Re: Psychrometry Test

08/22/2015 9:13 AM

Depends on the degree of accuracy that you are aiming for.

__________________
If you want to know how well a broom works you do not ask the guy selling the broom or the guy who designed the broom, you ask the guy using the broom.
Register to Reply
2
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#8

Re: Psychrometry Test

08/22/2015 10:12 AM

these ultra high tech devices work wonders to average a rooms varied temps...

Register to Reply Good Answer (Score 2)
Power-User
Hobbies - Musician - New Member

Join Date: Dec 2014
Posts: 418
Good Answers: 3
#9
In reply to #8

Re: Psychrometry Test

08/22/2015 10:28 AM

nice, clever advice. I agree. Just run the trials using the fun, but not too near. Wind velocity at significant amount (PV=mRT), decreases temperature of the bulb, it might not be anymore representative sample of the room, might give erroneous readings.

__________________
"When I thought I exceeded to be wise but wisdom was far from me" -King Solomon
Register to Reply Score 1 for Off Topic
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#10

Re: Psychrometry Test

08/22/2015 12:48 PM

The average temperature in an air conditioned room is usually taken at the return duct inlet....the relative humidity can be sampled at a few locations around the room...the dry bulb and wet bulb are taken to determine the relative humidity not the air temperature per se....which would be equal to the dry bulb reading...

https://www.ohio.edu/mechanical/thermo/Applied/Chapt.7_11/Chapter10a.html

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#12

Re: Psychrometry Test

08/23/2015 7:57 AM

Dear Mr.cckla,

The answer for your question is Yes. You have to measure in different corners as well as at 3 different levels namely at floor level,centre and at near ceiling level.

This is on account of my personal experience about 5 years back where there was a problem in the AC ROOM for the VFD for 1000 H.P. Motors - 4 nos, and it was found that though Air-Conditioners were installed to the required numbers, there was a variation in the Temp. when we measured at different corners and levels.

This has given a lesson for us and after re-orienting the AC unit, the problem was solved.

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Oct 2009
Posts: 1460
Good Answers: 30
#13

Re: Psychrometry Test

08/23/2015 9:55 AM

Just being practical here. When you ask the question, just ask "when I measure the humidity of an air-conditioned room, do I have to make one measurement or several?" It means the same thing and is a lot easier to spell. Then you have to ask yourself "Do I need a really precise measurement? Is there likely to be a variation across the room? Does it matter if there is?" If the air-conditioning has been sensibly installed then it will generate a flow of air and mixing will occur. If all you are concerned about is user comfort, then a single sample will suffice, at most a sample at each user station. If you are wanting to sample different areas of the room for the sake of the statistical exercise, then you are going to have to decide your statistical null hypothesis. "The humidity at waist level is greater than at eye level - true or false" or "The humidity near the door is greater than that at the window - true or false" and design your sample site pattern accordingly, with at least 5 samples at each site. I would say that that would be a complete waste of time for practical purposes.

Register to Reply
Member

Join Date: Jul 2015
Posts: 7
#14

Re: Psychrometry Test

08/24/2015 4:17 AM

Psychrometric properties

Dry-bulb temperature (DBT)

The dry-bulb temperature is the temperature indicated by a thermometer exposed to the air in a place sheltered from direct solar radiation. The term dry-bulb is customarily added to temperature to distinguish it from wet-bulb and dewpoint temperature. In meteorology and psychrometrics the word temperature by itself without a prefix usually means dry-bulb temperature. Technically, the temperature registered by the dry-bulb thermometer of a psychrometer. The name implies that the sensing bulb or element is in fact dry.

Wet-bulb temperature (WBT)

The thermodynamic wet-bulb temperature is a property of a mixture of air and water vapor. The value indicated by a wet-bulb thermometer often provides an adequate approximation of the thermodynamic wet-bulb temperature.

The accuracy of a simple wet-bulb thermometer depends on how fast air passes over the bulb and how well the thermometer is shielded from the radiant temperature of its surroundings. Speeds up to 5,000 ft/min (~60 mph) are best but it may be dangerous to move a thermometer at that speed. Errors up to 15% can occur if the air movement is too slow or if there is too much radiant heat present (from sunlight, for example).

A wet bulb temperature taken with air moving at about 1-2 m/s is referred to as a screen temperature, whereas a temperature taken with air moving about 3.5 m/s or more is referred to as sling temperature.

A psychrometer is a device that includes both a dry-bulb and a wet-bulb thermometer. A sling psychrometer requires manual operation to create the airflow over the bulbs, but a powered psychrometer includes a fan for this function. Knowing both the dry-bulb temperature (DBT) and wet-bulb temperature (WBT), one can determine the relative humidity (RH) from the psychrometric chart appropriate to the air pressure.

Relative humidity

The ratio of the vapor pressure of moisture in the sample to the saturation pressure at the dry bulb temperature of the sample.

Dew point temperature

The saturation temperature of the moisture present in the sample of air, it can also be defined as the temperature at which the vapour changes into liquid (condensation). Usually the level at which water vapor changes into liquid marks the base of the cloud in the atmosphere hence called condensation level. So the temperature value that allows this process (condensation) to take place is called the 'dew point temperature'. A simplified definition is the temperature at which the water vapour turns into "dew"

Register to Reply
Active Contributor

Join Date: Jul 2015
Location: Phoenix
Posts: 22
#15

Re: Psychrometry Test

08/24/2015 11:04 AM

Rotronic has some good technical notes...

http://content.rotronic-usa.com/rs/rotronicinstrumentcorp/images/Humidity%20Definitions%20WEBa.pdf

http://content.rotronic-usa.com/psych-charts

__________________
My internal monologue is saturated anologue.
Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#16

Re: Psychrometry Test

08/24/2015 1:45 PM

You might need to take a series of readings at the same place at different times as well.

It all depends on what you want the readings for.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply Score 1 for Good Answer
Register to Reply 16 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); cckla (1); dhayanandhan (1); dkwarner (1); Fredski (1); horace40 (1); Kulas (1); lyn (1); peter grasby (1); phph001 (1); SolarEagle (1); texasron (1); Tornado (2); Vincent.Jones (1)

Previous in Forum: Pump Capacity   Next in Forum: Mechanical Seal Plan 52

Advertisement