Transformer Grounding

01/04/2016 11:51 AM

we have all 11KV/0.415KV power transformer to feed various residential loads. our transformer is pad mounted. it has a body ground point on 11KV winding side, one body ground point on 415V winding side. we want to earth the transformer neutral for a TN-C system. can we use a single grounding rod for the neutral earth as well as the two body earth points of transformer i.e. connect neutral as well as the M.V and L.V side earth points to a single rod and then use this earth point for our loads as an earth reference.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: transformer grounding

01/04/2016 11:56 AM

It is difficult to understand how any organisation can have a <...11KV/0.415KV power transformer to feed various residential loads...>, and not have anyone on the payroll who knows how to write or look after documentation that describes how to install it correctly and how to look after it.

Options:

  1. Hire someone
  2. Look for employment elsewhere
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: transformer grounding

01/04/2016 12:10 PM

The codes and standards in effect in the jurisdiction in question will clearly speak to how this system needs to be grounded and how you would go about bonding the neutral to the ground plane you create.

The interesting thing is... I bet those same codes and standards have a section in them about "un-qualified" persons.

Hire someone...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Nov 2007
Location: Eastern Arizona mountains on Route 666 about a mile from God's country
Posts: 1676
Good Answers: 122
#3

Re: transformer grounding

01/04/2016 12:27 PM

Local electrical codes on required equipment and service grounding apply.

Not sure where you are but in the USA the grounding requirements vary from state to state and also from county to county or city to city in each state.

In my area we are required to install two separate, individual ground rods a minimum of 10 feet apart with the ground connection either exposed above ground or in a ground well with a removable inspection lid.

I suggest you obtain an approved copy of the grounding requirements for the location and react accordingly.

__________________
They said; "Brain size?" I heard; "Train size?" so I said: "I'll take a small one, thank you."
Register to Reply
3
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: transformer grounding

01/04/2016 1:48 PM
__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 3)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5
In reply to #4

Re: transformer grounding

01/04/2016 2:18 PM

Hear hear!

I have also suggested that before, to no avail.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6

Re: Transformer Grounding

01/10/2016 1:56 PM

Sigh...

If one earth were enough, there would be just one connection to save cost.

Consider what happens if the one earth corrodes through ....

The capacitance between the HV windings and LV windings is enough to pass a lethal current from 13.8/12/11/10 KV, to the star point (earth to the user's home) which will be wired to all the exposed metal covering electrics.

The local standards incorporate 125 years experience of how to avoid killing people around electrics. Somewhere in the legal history, there may be cases where someone made it a different way & was judged guilty for a death.

Find out the local standards or ask the electricity distributer.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#7

Re: Transformer Grounding

01/10/2016 1:59 PM

Read the codes and standards and stop asking us how to do your job. Please. We are not doing you any favours here by helping you and you are not doing yourself (or your customers) any favours by asking an online forum for advice answers on dangerous questions.

__________________
jack of all trades
Register to Reply
Active Contributor

Join Date: Dec 2015
Posts: 11
#8

Re: Transformer Grounding

02/03/2016 1:22 AM

No. Neutral should be grounded differently with the body of the transformer. When current is unbalanced in the phases, neutral carries current which must be grounded. Sometimes neutral bears potential also. But transformer body did not carry current or have potential unless there is a fault. Hence it must be grounded separately. Dont use same grounding to neutral and transformer body.

Register to Reply
Register to Reply 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

67model (1); jack of all trades (1); johnmarsh11 (1); lyn (1); North of 60 (1); PWSlack (1); SHOCKHISCAN (1); TonyS (1)

Previous in Forum: Quick Variable DC Power Supply From 400VAC   Next in Forum: I have found the Anonymous Poster!

Advertisement