Control Transformer Sizing

01/04/2013 5:28 PM

Control transformers are used to suppy power to control ciruit i.e relay coils of a ciruit.now every transformer has a kva rating along with voltage rating.so how are we gonna find the VA rating of the transformer used to supply power to the control circuit containing relay coils and pilot lamps as main loads.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#1

Re: Control transformer sizing

01/04/2013 5:41 PM

this is a Wiki question thats rather elementary

Register to Reply Score 1 for Off Topic
Guru
Engineering Fields - Mechanical Engineering - New Member Fans of Old Computers - TRS-80 - New Member Popular Science - Weaponology - New Member Safety - Hazmat - New Member Hobbies - Fishing - Fish On! United States - Member - New Member

Join Date: Apr 2012
Location: Detroit MI, USA
Posts: 2496
Good Answers: 271
#2
In reply to #1

Re: Control transformer sizing

01/04/2013 5:56 PM

Yes it is, but it's not as fun posting them here and winding Lyn up...

__________________
How we deal with death is at least as important as how we deal with life. --CAPTAIN KIRK, Star Trek II: The Wrath of Khan
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#4
In reply to #2

Re: Control transformer sizing

01/04/2013 6:47 PM

some Ops are just plain lazy! I enjoy sharing knowledge and experience, and I try to help genuine people when I can. I started typing 1.67...and erased it!!!

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Control Transformer Sizing

01/04/2013 6:44 PM

"so how are we gonna find the VA rating of the transformer used to supply power to the control circuit containing relay coils and pilot lamps as main loads."?

Pay somebody to care.

Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8
In reply to #3

Re: Control Transformer Sizing

01/05/2013 5:30 PM

Coolyaar pay? When he can come here? Good God man, get a grasp.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Off Topic
3
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Control Transformer Sizing

01/04/2013 10:06 PM

Add up the va of all the stuff that might be simultaneously energized, and then multiply by a safety factor of say 1.25. In unusual cases, this safety factor might vary. The worst case is if many of the loads switch from off to on at the same time, which could happen on recovery from a power failure.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Good Answer (Score 3)
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#11
In reply to #5

Re: Control Transformer Sizing

01/07/2013 5:04 PM

Coolyaar & Tornado,

Actually, you should add up all the VA for the loads that are on and then separately add the inrush VA for the relays and contactors that are being closed simultaneously. The inrush VA can be as much as 3-5 times the sealed VA, so the multiplier of 1.25 may not be adequate. The manufacturers of the relays and contactors all list the inrush and sealed VA's for their equipment. After doing this, then add a safety margin for future expansion of loads. At one time I designed panels for a custom shop making them with U/L listing, and we had to go this way.

--JMM

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#12
In reply to #11

Re: Control Transformer Sizing

01/07/2013 9:44 PM

Agreed. The latter part of my post implied similarly, though not in detail.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Apr 2012
Location: Lollipop Land
Posts: 34
Good Answers: 2
#6

Re: Control Transformer Sizing

01/04/2013 10:46 PM

Take your pick:

__________________
Toto, I've a feeling we're not in Kansas anymore
Register to Reply
2
Commentator

Join Date: Dec 2011
Posts: 96
Good Answers: 2
#7

Re: Control Transformer Sizing

01/04/2013 11:58 PM

Calculate the total SEALED (steady state) VA load of your control circuit. This is done by adding the continuous VA requirements of the maximum number of "omponents that will be-sagrgized at any given time, including non-inductive as well as inductive com­ponents.

Calculate the PEAK INRUSH VA of your control circuit.

First, analyze the sequence of operation of all com­ponents. Then add together the inrush VA ratings of the components that will be energized simultaneously. Next, determine the peak - or maximum simultaneous - inrush VA load that the transformer will "see." The VA requirements :or indicating lights, timers and othernon-iriductive components which do not have an inrush VA also should be included

calculate the TRANSFORMER SELECTION INRUSH

VA. Use the following formula:

Selection Inrush VA = root of (VA Seaied)2 + (VA Inrush)2

see any control transformer manufacturers data

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Control Transformer Sizing

01/05/2013 6:18 PM

Er, by using simple arithmetic, perhaps?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Power-User

Join Date: Jun 2010
Posts: 344
Good Answers: 17
#10

Re: Control Transformer Sizing

01/06/2013 2:09 AM

I assume first that you have the transformer already. Try one or all of these:

1. Use a clamp meter to measure AC current, when control circuits powered up.

2. Look up the circuit diagram, see what exists, get current rating of each item, add.

3. Measure the cross-section dimensions of the steel through the copper windings. Then guesstimate.

These represent guesstimates only, because not all control circuits are likely to be operating at the same time.

If you don't have the transformer, try 2. above.

Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Fredski (2); jmueller (1); JPool (1); lyn (1); MagicWand (1); Phaddy (1); PWSlack (1); roykav (1); TonyS (1); Tornado (2)

Previous in Forum: Choke sizing   Next in Forum: Star-Delta Starter Tripping by Simocode

Advertisement