Paralleled Generators' Loss of Load

02/13/2016 6:39 AM

hi I just want to understand how two or more Generators in synchronism supplying a common load would behave if the load is suddenly disconnected but the gens remain connected to a common bus, in other words the gens remain in parallel. Would they oscillate against one another? Richard

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Paralleled generators' loss of load

02/13/2016 6:54 AM

They might, but various other things might also happen. The best is that they are equally tuned through the range of possible loads, so that they continue to share equally.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Jun 2015
Posts: 49
#4
In reply to #1

Re: Paralleled generators' loss of load

02/13/2016 7:44 AM

That is understood. But remember the load is suddenly disconnected leaving the gens tied to a common bus. If they were equally sharing the lost load, what happens after the load is gone?

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#2

Re: Paralleled generators' loss of load

02/13/2016 7:12 AM

The way the generators share the load (KW) is determined by the throttle settings. If the throttle is raised on one generator with respect to the other, it will assume more than its share of the load. If in this case the load is removed, this generator will tend to "motorize" the other generator. There will be power delivered from the advanced engine, through its generator to the other generator (which is acting like a motor) to the other engine.

Register to Reply Score 1 for Good Answer
Associate

Join Date: Jun 2015
Posts: 49
#3
In reply to #2

Re: Paralleled generators' loss of load

02/13/2016 7:39 AM

Thanks. What if the throttle settings are uniform such that the generators are sharing load equally?

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#6
In reply to #3

Re: Paralleled generators' loss of load

02/13/2016 10:28 AM

If they are equal under load, then they should both run unloaded when the load is removed. Neither should show any power (KW).

If you are drawing current with both generators in parallel with no load, there likely is a problem with voltage regulation. If the voltages are not set equal, there will be cross current (reactive current) between the two generators.

Register to Reply
Power-User

Join Date: Nov 2015
Posts: 335
#7
In reply to #6

Re: Paralleled generators' loss of load

02/13/2016 12:18 PM

Also phasing, most importantly, that they might not cancel out one unto another.

__________________
"And ye shall seek me, and find me, when ye shall search for me with all your heart."
Register to Reply Score 2 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#10
In reply to #7

Re: Paralleled generators' loss of load

02/13/2016 2:30 PM

If the generators are locked in synchronism they have to be in phase. If not one generator will drive the other, circulating currents will be high. "Motoring" as Rixter pointed out.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Nov 2015
Posts: 335
#8
In reply to #3

Re: Paralleled generators' loss of load

02/13/2016 12:25 PM

Do you disconnect loads manually, in your power plant? Or are your gensets do not have governors? That's odd.

Here read something about load control

__________________
"And ye shall seek me, and find me, when ye shall search for me with all your heart."
Register to Reply Off Topic (Score 3)
Associate

Join Date: Jun 2015
Posts: 49
#11
In reply to #8

Re: Paralleled generators' loss of load

02/13/2016 3:42 PM

The loads were actually disconnected when all evacuating lines were tripped by protection but the hydro gens remained paralleled on the bus. Eventually, the generators tripped on " low governor oil pressure"

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5

Re: Paralleled generators' loss of load

02/13/2016 9:59 AM

It depends on the system....I would think typically one generator would have the lead, any others would shut down on reduced load...this is a condition that is dealt with in the control strategy, which depends on type of load and conditions...

https://www.physicsforums.com/threads/paralleled-generator-protection.324929/

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#9
In reply to #5

Re: Paralleled generators' loss of load

02/13/2016 1:34 PM

The engine alternators with which I was familiar years ago had governors which had two modes, isochronous and droop, that controlled the load versus speed function. Isochronous mode maintained a constant speed (or frequency) regardless of load. Droop mode allowed the engine to slow down or speed up depending on the load.

The standard procedure was to set one engine to isochronous and set the frequency with the throttle control. Other alternators paralleled with the first had governors set to droop and were adjusted with the throttle to take their share of the load.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#12

Re: Paralleled Generators' Loss of Load

02/14/2016 4:37 AM

Dear Mr. Richard Matisco,

This topic has appeared earlier and you can use the option to search with in CR4

and you will find the following link

https://www.physicsforums.com/threads/paralleled-generator-protection.324929

and you can refer the link below.

https://www.google.co.in/search?q=*Paralleled+Generators%27+Loss+of+Load*&biw=1280&bih=636&start=20&sa=N&psj=1&bav=on.2,or.r_cp.&bvm=bv.114195076,d.c2E&ech=1&psi=wBrAVqLFBI60uAS4iqmQCA.1455430329665.7&ei=6hvAVtWULNiLuwTIhoT4Bw&emsg=NCSR&noj=1

During my college days, our Professor has taught that the generator which has got less Percentage of Voltage Droop Character will continue to work as generator and the other one tend to work as a motor.

DHAYANANDHAN.S

Register to Reply
Anonymous Poster #1
#13

Re: Paralleled Generators' Loss of Load

02/14/2016 5:20 AM

Sudden loss of load = overspeed trip

Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#14

Re: Paralleled Generators' Loss of Load

02/14/2016 10:12 AM

They will all encourage each other to go faster when the load goes off. No personal experience but I guess without speed or frequency controls they will race away - particularly if diesel driven -it has something to do with needing less fuel at higher speed on no-load (experts here can explain why. I don't know for sure).

There is plenty of evidence to show what can happen to generators that over-speed:

Here's an example:

https://nolstuijt.wordpress.com/2011/11/27/duvha-powerstation-turbine-blowup-sa/

PS: Richard - are you the Chief Engineer of this power station by any chance??

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#16
In reply to #14

Re: Paralleled Generators' Loss of Load

02/14/2016 11:34 PM

"...They will all encourage each other to go faster when the load goes off...", no they don't since properly set systems don't allow this to happen.

Similarly, the overspeed in this article does not occur in normal operation, it was a result of operator error during testing:

"...They were doing a test of the turbine overspeed protection system, and in short, the protection did not kick in..."

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#19
In reply to #16

Re: Paralleled Generators' Loss of Load

02/15/2016 6:52 AM

Sorry to disagree with you RAMconsult, but I say they will speed up. We don't know the system is properly set.

My link shows what could happen in overspeed. The reason causing the overspeed is because the controls were bypassed for the test.

The novice level of the OP question makes me think there might not be any controls to start with. Hence the warning.

I am still curious why diesel engines keep on speeding up on no load (if they do that is).

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#21
In reply to #19

Re: Paralleled Generators' Loss of Load

02/15/2016 7:06 PM

Disagreement is fine, I had exactly the same reaction when my new boss (who happened to be on an IEEE committee on Power System Dynamics) asked me the same question. In my naivete I answered that once the load was removed the turbine-generator would speed up because all the inertia in the rotating mass had to go somewhere. He smiled and said, "...and where does the accelerating torque come from if no steam is entering the turbine?"

It's no different than if you're driving up a steep hill and you shift into neutral without removing your foot from the accelerator, the engine speed pops up beyond redline. On the other hand, if you simultaneously take your foot off the gas when you shift into neutral, the engine speed will see a small rise as the remaining fuel burns off, then immediately slow down once the fuel flow has stopped.

The accident you cited was a triple contingency failure and totally avoidable, a failure of multiple humans, not a mechanical one. In the US the safety systems are routinely checked, rechecked, and checked again, to ensure that something like that doesn't happen.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: May 2007
Location: Australia.
Posts: 1642
Good Answers: 81
#22
In reply to #21

Re: Paralleled Generators' Loss of Load

02/15/2016 8:42 PM
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#23
In reply to #21

Re: Paralleled Generators' Loss of Load

02/15/2016 11:17 PM

Did your new boss figure that the control system could shut off the fuel, water, or steam instantly?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#24
In reply to #23

Re: Paralleled Generators' Loss of Load

02/16/2016 11:35 AM

No, we were a bit more sophisticated than that, especially since we were modelling the overall dynamics of the plant. We were fully aware of second and third order effects such valve stroke timing, steam chest clearance volumes, piping sizes/lengths, governor and safety system time constants/delays/inertia, relay settings/operating times/sensitivities, boiler plant/control system dynamics, variances in manufacturers' data sheets, etc., etc.

It was a multidisciplinary effort involving teams from the electrical, mechanical, controls, relaying departments, as well as station operating personnel. After we programmed it in Fortran4, we then verified the models against actual tests at a steam station.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#27
In reply to #21

Re: Paralleled Generators' Loss of Load

02/16/2016 2:13 PM

I think you were right to say the generator would speed up; unless you were told beforehand that the steam had been shut off. This seems to have been introduced into the equation afterwards. But I suppose you don't argue with your new boss.

The analogy of driving uphill is OK as an example of a load, but going into neutral is akin to disconnecting the engine - the load is still there.

I think we need two cars connected by a rigid tow-bar to simulate 'parallel' running (and maybe pulling a trailer). And then to go level or downhill to simulate no-load (or losing the trailer) - when without changing the throttle (drivers not paying attention) - they will speed up without knowing.

This is well known to zealous traffic cops who place cameras here to catch drivers before they realise they have inadvertently crept over the speed limit - a nice little earner this !

Whatever the merits of this analogy - appropriate speed/load controls are necessary to run generators in parallel - as many have said here on CR4 - without which, everything else being equal, they will speed up when the load is removed.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply Score 1 for Off Topic
Associate

Join Date: Jun 2015
Posts: 49
#29
In reply to #14

Re: Paralleled Generators' Loss of Load

02/17/2016 11:55 AM

No I am not the chief Engineer. Actually I am a protection engineer trying to comprehend the dynamics of the system resulting from the disturbance.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#30
In reply to #29

Re: Paralleled Generators' Loss of Load

02/17/2016 1:41 PM

If you're interested in dynamics then you might find "Power System Stability and Control" by P. Kundur interesting, there's even a chapter dedicated to PSS. Heavy reading though, 1,000+ pages!

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Associate

Join Date: Jun 2015
Posts: 49
#31
In reply to #30

Re: Paralleled Generators' Loss of Load

02/17/2016 2:56 PM

Thank you

Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#32
In reply to #29

Re: Paralleled Generators' Loss of Load

02/17/2016 6:05 PM

"...No I am not the chief Engineer....."

..good to know....but I never did think you were. Just my odd sense of humour creeping in. Apart from thinking the generators will speed up when the load is removed - for reasons given, I am not the expert here.

It looks as though RAMconsult and others have pointed you in the right direction.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
4
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#15

Re: Paralleled Generators' Loss of Load

02/14/2016 11:31 AM

The exact reaction will be a function of a lot of information that you have not provided. In the simplest case of two identical units supplying an isolated load (no grid connection) equal to the combined ratings of the generators whose controls are properly set, the initial reaction of both machines will be to overspeed slightly as the remaining fuel/steam/gas/water clears the prime mover, then the governors will hold the speed constant. Properly set governors will sense the loss of load and immediately back the input to zero to prevent an overspeed trip and allow the units to settle back to idle/synchronous speed.

Here's the big "if", if they are set up as Master/Slave then the Master will provide the speed signal to synchronous frequency while the Slave follows, so they stay locked in speed after the transients have died out. If they are both Masters (usual case in less sophisticated governors) then you have violated a basic tenet of control theory that says you can't have two controllers attempting to control the same point that they are both sensing, and they will oscillate (aka hunting) around the setpoint. The magnitude of the oscillations will be a function of the gain, and the frequency a function of the time constants, of the governors.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 4)
Associate

Join Date: Jun 2015
Posts: 49
#25
In reply to #15

Re: Paralleled Generators' Loss of Load

02/16/2016 12:11 PM

I think RAMConsult has answered it. What you have explained is just what happened: oscillations, then a 'governor oil pressure low' trip. Possibly the oscillations were not 'damped' and the governors struggled with them until the trip. In your view, could a power system stabilizer have made a difference?

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#26
In reply to #25

Re: Paralleled Generators' Loss of Load

02/16/2016 1:44 PM

Thanks for the feedback! Unfortunately despite its name, a Power System Stabilizer (PSS) is not the panacea that many think it is. Its primary use is to reduce a phenomenom known as SubSynchronous Resonance (SSR) that can be problematic in large geographically diverse power systems. Unless you're experiencing SSR and/or routinely snapping 24" shafts between the turbine and the generator, a PSS is not for you.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Jun 2015
Posts: 49
#28
In reply to #26

Re: Paralleled Generators' Loss of Load

02/16/2016 2:28 PM

Thanks. This is useful information!

Register to Reply
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: May 2007
Location: Australia.
Posts: 1642
Good Answers: 81
#17

Re: Paralleled Generators' Loss of Load

02/15/2016 12:56 AM

If one of the generators is motor driven by the other unit then it will disconnect from the system on a reverse power relay trip.

Register to Reply
2
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#18
In reply to #17

Re: Paralleled Generators' Loss of Load

02/15/2016 6:39 AM

Only in theory, not in practice. From GE: "... it is strongly suggested that these devices (Reverse Power Relays or RPR) always be used in conjunction with some kind of a time-delay relay. This will prevent undesired operations during system disturbances which may momentarily cause the power flow to be reversed from its normal direction of flow..."

In addition to the time delay, these RPRs also have varying sensitivities and deadbands to reduce spurious operation. A quick look at the chart on page 13 may surprise those not familiar with the amount of power that the different types of prime movers will tolerate before the relay needs to operate. For example, at the low end of conventional steam turbines a typical setting is 1 percent (0.01 per unit) of the machine's rating; therefore a RPR on a 500MW unit will not even pick-up and start the timer before 5MW of power is flowing into the machine.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: May 2007
Location: Australia.
Posts: 1642
Good Answers: 81
#20
In reply to #18

Re: Paralleled Generators' Loss of Load

02/15/2016 4:51 PM

Yes I agree, GA.

Register to Reply
Register to Reply 32 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard