Anonymous Poster #1

50HZ VS 60HZ

02/12/2016 1:23 AM

What happen to a bus duct with 50HZ if supplied by 60hz power?And the should output power be 60hZ??

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#1

Re: 50HZ VS 60HZ

02/12/2016 1:44 AM

Ha, this is a trick question!

If there is 50 Hz on the duct and you supply 60Hz it will be 55 Hz as well as 50 Hz as well as 60 Hz, not? Not sure what it should be but usually if you replace 50 Hz and supply 60 Hz you will get ....

.... oh wait its coffee time. I'll come back later to see if you refined the question.....

__________________
Common Sense Dictates
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2
In reply to #1

Re: 50HZ VS 60HZ

02/12/2016 2:07 AM

Everything that branches off the bus will then run at 60Hz, unless there are VFDs or other frequency converters involved. Most AC motors will run 1.2 times as fast as on 50Hz.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3
In reply to #1

Re: 50HZ VS 60HZ

02/12/2016 4:26 AM

I've just tried superimposing 60Hz on to a 50Hz waveform.

I've got a headache now!

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Oct 2013
Location: Texas.Baytown
Posts: 697
Good Answers: 26
#8
In reply to #3

Re: 50HZ VS 60HZ

02/12/2016 10:56 AM

Hertz dont it?

__________________
If you want to know how well a broom works you do not ask the guy selling the broom or the guy who designed the broom, you ask the guy using the broom.
Reply
Power-User

Join Date: Nov 2011
Location: Philippines
Posts: 105
Good Answers: 7
#20
In reply to #8

Re: 50HZ VS 60HZ

02/14/2016 5:54 AM

A U.S. transformer maker said to me "60 Cycles but 50 Hertz". Hmm!

Reply Off Topic (Score 5)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4

Re: 50HZ VS 60HZ

02/12/2016 7:53 AM

The bus does not care which power distribution frequency gets applied to it. Depending on the nature of the load(s) attached to this bus the loads may work fine, burst into flames, or any of a number of other unpleasant scenarios.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
2
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#5

Re: 50HZ VS 60HZ

02/12/2016 9:39 AM

The bus duct is simply a conductor. It cares not if you supply 60Hz or even military 400Hz. For that matter, it would be just fine and dandy with DC as well.

What about the equipment attached to said duct? Care to offer information on those devices?

__________________
Remember when reading my post: (-1)^½ m (2)^½
Reply Good Answer (Score 2)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6
In reply to #5

Re: 50HZ VS 60HZ

02/12/2016 10:44 AM

But it would need to be three phase DC, correct? ;-)

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#7
In reply to #6

Re: 50HZ VS 60HZ

02/12/2016 10:50 AM

Not really - positive, common, and either a spare or ground. Or if we are working with OP amps we can have positive, ground, negative. Works for this argument.

Actually, the OP never did say it was 3 phase - we are just assuming that, which is the point - too little information once again.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#9
In reply to #7

Re: 50HZ VS 60HZ

02/12/2016 12:38 PM

It was an attempt at humour.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#10
In reply to #9

Re: 50HZ VS 60HZ

02/12/2016 1:06 PM

Unfortunately, so were my poor responses.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Reply
Power-User

Join Date: Dec 2007
Posts: 177
Good Answers: 6
#11
In reply to #6

Re: 50HZ VS 60HZ

02/12/2016 2:29 PM

do I hear a bid for 4 phase dc?????

Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#19
In reply to #11

Re: 50HZ VS 60HZ

02/13/2016 6:08 AM

Seen it done. Separate 220V and 440V three wire systems with a common neutral.

They were supposed to be separate systems, somewhere in the mists of time the neutrals got connected together. It didn't cause problems and I couldn't be bothered to look for it.

__________________
The reports of my death are greatly exaggerated.
Reply
Power-User

Join Date: Nov 2011
Location: New Hampshire
Posts: 406
Good Answers: 3
#26
In reply to #6

Re: 50HZ VS 60HZ

02/16/2016 3:35 PM

Only on one side.

Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#24
In reply to #5

Re: 50HZ VS 60HZ

02/15/2016 9:45 PM

Phys,

I have to disagree with you on this one. Although some could humorously argue that a bus duct doesn't care because an inanimate object can't have emotions, the users should care. As the frequency goes up from DC to 400Hz, the current flowing in the individual bus bars is increasingly forced onto the surface, instead of flowing equally throughout the entire cross-section of the conductor. This requires a decrease in the ampacity of the bus bars. This decrease is not uniformly proportional to the change in frequency, but depends in a complex manner on the cross section as well as the frequency. There are a few good articles that discuss this (unfortunately, I don't have their references right now). The 400/60 Hz ampacity ratio varies from 1.0 in very small conductors to less than 0.7 in large ones.

--JMM

Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#25
In reply to #24

Re: 50HZ VS 60HZ

02/16/2016 8:02 AM

This may help http://chemandy.com/calculators/skin-effect-calculator.htm

__________________
The reports of my death are greatly exaggerated.
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#27
In reply to #5

Re: 50HZ VS 60HZ

02/17/2016 9:47 PM

I agree with you : the busbar is a conductor. So, skin effect and proximity effect will be involved. The resistance will grow and so the losses. The temperature will rise. If it will be over the limits-it depends on insulators type, also-you have to oversize a bit.

__________________
Julius
Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#30
In reply to #27

Re: 50HZ VS 60HZ

02/22/2016 8:47 AM

For skin and proximity effect see[for information]:

http://www.aluminum.org/sites/default/files/aecd13.pdf

[pages 13-12 up to 13-16]

Note: usually from 50 to 60 Hz the resistance increases with about 3-4%[so the losses do].

__________________
Julius
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#12

Re: 50HZ VS 60HZ

02/12/2016 3:42 PM

You will have to change the core material from Iron to Kryptonite, unless it powers a resistance heater.

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#13
In reply to #12

Re: 50HZ VS 60HZ

02/12/2016 4:25 PM

I wonder what temperature and pressure would one need to make a crystallized noble gas?

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#22
In reply to #13

Re: 50HZ VS 60HZ

02/15/2016 10:35 AM

really low and really high at the same time to make Krypton solid, a.k.a. Kyrptonite.

I really have no idea what to dissolve in it for the colors though. Perhaps red Kool-Aid, there seems to be plenty of that to go around these days.

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#32
In reply to #22

Re: 50HZ VS 60HZ

02/22/2016 2:05 PM

I thought the GOP drank the red Kool-Aid, and the Democrats drank the blue? Did you mistype, did I mishear, or did you intend to slam the Republicans with that?

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#34
In reply to #32

Re: 50HZ VS 60HZ

02/22/2016 3:49 PM

It was an allusion to red kryptonite. Usually all Kool-Aid being drank by whatever uninformed voter block (whether they vote for Dem or GOP) is red. Jonestown Kool-Aid was also red, as I recall, and Lemming Kool-Aid is also red.

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#35
In reply to #34

Re: 50HZ VS 60HZ

02/23/2016 9:20 AM

Ah, I always thought the color was supposed to be a symbol for the ideology being consumed; GOP drinks Red, Dems, drink Blue, Eco-Terrorists drink Green, Trump supporters drink thick, black bile(1). Now I know better, people are ignoring the kool-aid color.

Notes:

  1. I WISH I was making a hyperbolic comment there as a joke, but when you listen to what he's saying, it's all so crude, offensive, and filled with utter hate, It's a wonder he gets away with it up on the debate stage. I heard on the news this morning that Trump is threatening the owners of the Chicago Cubs because they're "spending money against him," and the snippet of the e-mail read/paraphrased on the radio made it sound like classic blackmail: "...you don't want certain secrets to get out, do you?"
__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Reply Off Topic (Score 5)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#14

Re: 50HZ VS 60HZ

02/12/2016 7:41 PM

Q: What's the difference between 50Hz DC and 60Hz DC?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#15
In reply to #14

Re: 50HZ VS 60HZ

02/12/2016 9:31 PM

10Hz DC!!!

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#16
In reply to #15

Re: 50HZ VS 60HZ

02/12/2016 9:53 PM

5Hz on each leg.

Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#17
In reply to #16

Re: 50HZ VS 60HZ

02/12/2016 10:10 PM

That could hurt really badly...

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#18

Re: 50HZ VS 60HZ

02/13/2016 2:42 AM

Dear Friend,

You are not clear in your expression.

1. Do you have equal voltage.

2. Do you have same phase sequence

3. The following combination is possible.

a. Do you switch off 50 Hz. supply and switch on 60 Hz.

b. Do you switch on 60 Hz. supply while 50 Hz. supply is on.

Nett result - Short Circuit and fuse blow-up. happen.

Reply
Anonymous Poster #2
#21

Re: 50HZ VS 60HZ

02/15/2016 9:39 AM

If you have 50Hz equipment and you are supplying 60Hz power, you may damage the equipment. This cannot me bade as a general call, as each piece of equipment needs to be looked at individually to see the results. A light bulb won't care, a motor will run faster (and possibly overheat) a PLC might release the Magic Blue Smoke and stop working altogether.

If you are connecting a 50Hz power supply and a 60Hz power supply to the same bus at the same time, then you are a dangerous idiot who should be fired immediately before you kill someone.

Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#23

Re: 50HZ VS 60HZ

02/15/2016 10:38 AM

What did the 50Hz duck say to the 60Hz duck? Quack! If it looks like a duck, sounds like a duck, and smells like a duck, and even waddles like a duck, it must be a duck.

DUCK!

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#28

Re: 50HZ VS 60HZ

02/18/2016 1:19 AM

I am not an engineer, but the little bit of theory I learnt tells me if its a pure resistive device then frequency has no effect.

Reply
Guru
Engineering Fields - Electrical Engineering - New Member Fans of Old Computers - Commodore 64 - New Member Popular Science - Evolution - New Member United States - Member - New Member

Join Date: Oct 2013
Location: Illinois, 7 county region (The 'blue dot' that drags the rest of the 'red state' around during presidential elections.)
Posts: 3683
Good Answers: 89
#31
In reply to #28

Re: 50HZ VS 60HZ

02/22/2016 2:01 PM

But IS it a pure resistive device? The OP hasn't told us yet.

We've only got part of the question so far, it's like trying to answer "What do you get when you cross - " Cross what with what?

All we know are "a power buss at 50Hz" and "a generator at 60Hz." We don't know what sort of load, we don't know if there is another 50Hz power source on the buss, we know just enough to make wild guesses, and ask leading questions to try and draw out more information, and the OP does not seem to be very forthcoming with the latter.

__________________
( The opinions espressed in this post may not reflect the true opinions of the poster, and may not reflect commonly accepted versions of reality. ) (If you are wondering: yes, I DO hope to live to be as old as my jokes.)
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#33
In reply to #31

Re: 50HZ VS 60HZ

02/22/2016 2:38 PM

No, we can make all sorts of WAG on absolutely no information at all. Just look at all of the previous 32 replies.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#29

Re: 50HZ VS 60HZ

02/18/2016 9:18 AM

One thing I can tell you for sure: There will not be 10Hz leaking off to one side so the bus can still run at 50 Hz. What planet are you from, once again please? Here on Earth, the frequency the power is supplied to the bus is equal to the frequency at the output side of the bus. If there are multiple frequencies, there is a problem, and usually it lets the smoke, fire escape from the conductors.

__________________
If it ain't broke, don't fix it. Just build a better one.
Reply
Reply to Forum Thread 35 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

7anoter4 (2); adreasler (3); Anonymous Poster (1); dhayanandhan (1); eltech (1); IdeaSmith (1); James Stewart (4); jmueller (1); JRaef (2); lrsheldon (1); lyn (2); Munster (1); NeilA (1); North of 60 (1); Phys (3); RAMConsult (2); redfred (3); texasron (1); TonyS (3); Tornado (1)

Previous in Forum: Explosion Proof Certification for Luminaries   Next in Forum: Paralleled Generators' Loss of Load

Advertisement