Concept Of Variable Frequency Drive

04/05/2016 11:25 PM

Guys, we have 132 kW, 1000 rpm motor for fan application. Normally we were started the motor by using dol starter. It consumes 50 kW at 30% of damper position in 1000 rpm. Suction draft is enough as per our process requirements.is there any chances to save the power If I go for vfd...?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Concept of variable frequency drive

04/05/2016 11:43 PM

What is your position in this hypothetical process?

What, if anything, have you done to discover the answer to your question?

Your past posts do not bode well for your technical ability.

Finally, why are you running a 132 kW motor at 50 kW?

Answer all questions, in detail!

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Concept of variable frequency drive

04/06/2016 12:12 AM

The short answer is "yes", but that still leaves the question of whether the energy saved will outweigh the expense of the VFD. It might be better to change the fan impeller and the motor instead, unless there are times when greater flow and/or pressure are needed.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
11
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Concept of variable frequency drive

04/06/2016 12:18 AM

The way that a VFD saves energy in a centrifugal load, such as a centrifugal fan, is by reducing the LOSSES in the system. So IF you are VARYING the flow to match the process you are using this for, then you have two basic options on varying that flow: mechanical restriction, such as dampers, and changing the motor speed such as with a VFD. Both methods reduce energy when flow is reduced, but a VFD reduces the energy MORE than the dampers will.

If you use a damper to reduce flow, there are losses associated with that method; fixed energy losses in the motor, friction losses as the air moves over the dampers, turbulence losses that are being converted to heat in the air stream, noise in the air (which, believe it or not, represents energy input), etc. But still, as you have observed, restricting the flow to 30% nets an energy reduction (we don't know what the energy input is at full flow, so we can't say how much).

When you reduce the flow by reducing speed, you are doing so without adding those comparative losses, plus you also reduce some of the fixed losses inside of the motor itself. The general formula always used is that the energy required by the fan reduces at the CUBE of the speed change. So for example at 50% speed, the energy input required by the fan from the motor is dropped to 12.5% (.5 x .5 x .5 = .125) of what it would have been at full speed. But speed does not directly equate to flow, so you can't assume that 50% speed = 50% flow, it doesn't work that way because you must overcome static pressure first.

Still, the vast majority of situations where a VFD replaces a damper system result in significant energy savings, but only IF there is VARIATION in flow rates. In other words you must have sometimes when you need 100% flow, other times when you need 75% flow, and times when you need only 30% flow. If you ALWAYS need the SAME amount of flow, then a VFD will NOT save you any energy compared to just using a smaller motor.

What we DON'T know in your situation is what your entire flow profile looks like and what your energy consumption is for that flow profile. Without that, nobody can help you determine in advance whether or not you will save energy.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 11)
Guru
Hobbies - CNC - New Member Hobbies - DIY Welding - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Aug 2007
Posts: 23647
Good Answers: 420
#5
In reply to #3

Re: Concept of variable frequency drive

04/06/2016 8:02 AM

Excellent and through response, and I'll have to check the link out.

__________________
“ When people get what they want, they are often surprised when they get what they deserve " - James Wood
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Concept of variable frequency drive

04/06/2016 6:55 AM
  • If here is a supply maximum capacity issue on the incoming cables, or
  • If there is a per-kWh electrical tariff in place

Then it might be possible to justify investing in a VFD on the basis of not needing to up-size the cables or on the power saved.

  • If the damper position is such that 50kW is the maximum power ever taken

Then it would be better to right-size the motor, its protection arrangements and the fan, fully open the damper and forget about a VFD. That way, investment in a smaller-sized motor releases the larger-sized one for redeployment elsewhere.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Aug 2012
Posts: 1071
Good Answers: 92
#6

Re: Concept of variable frequency drive

04/06/2016 8:04 AM

Note to add regarding the option of changing the motor vs. VFD installation- changing the motor will likely lead to greater energy savings than installing a VFD to yield the same end result, as the VFD has its own losses. However, you need to calculate the correct fan rpm to provide adequate suction at full open damper position to fully achieve this potential, or else you continue to lose that parasitic loss.

Register to Reply
Register to Reply 6 comments