Shield Strength of XLPE Cable

06/02/2016 6:56 AM

hi guys, following is the requirement from one of our client with exact statement from the client, please take a look;

"I want to know the shield strength of your 500 mm square cable. I want to interconnect the earthing of two ring main units. The cable shield should be capable of carrying 2,000 amps"

I am unable to find the shield strength value in specifications of XLPE armoured cables, also couldn't find any thing related to this, or may be i am trying to search with wrong keywords.
please help.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Shield Strength of XLPE cable

06/02/2016 8:35 AM

It comes as little surprise to find that individuals are so busy trying to find things using the wrong tools that the information needed remains obscured.

Rather than a mouse and a keyboard and an internet connection, it is far simpler to pick up the phone and actually talk to a human being at the cable manufacturer's premises. The telephone is the correct tool to use for such queries. Such interactions are personal, 2-way, and can yield information far quicker than an afternoon of searching on the internet ever can, with confirmation of understanding being achieved at the end of the call. And "time is money" when there is a problem to be solved.

CR4 does not offer training courses on the use of the telephone despite, according to a significant percentage of posts coming through, a significant need being evident.

<unsubscribes>

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#2

Re: Shield Strength of XLPE cable

06/02/2016 8:36 AM

What is the shield material, method of fabrication and thickness. From this you can calculate the steady state current capacity.

For transients = a little more complex...

What is the shield for (lightning, RF, etc)

Who made the cable? Ask them the shields specs.

__________________
Per Ardua Ad Astra
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Shield Strength of XLPE cable

06/02/2016 8:39 AM

<...calculate the steady state current capacity...> The length, cable construction detail and method of installation are also factors according to protocols to be found in BS7671.

<...Who made the cable? Ask them the shields specs....> Quite. Over the telephone is the quickest way and highly recommended.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#10
In reply to #2

Re: Shield Strength of XLPE cable

06/02/2016 12:07 PM

From the context, it appears to me that OP is the OEM of this cable. Can he not measure the resistance per foot with a DVM? Does he need to use a megger? 2000 amps at what potential (in case of irregularity in the shielding impedance)?

There are so many cable types and brands, I should think it really difficult to give any finite answer based on information presented thus far.

This seems like such an odd ball question. What is the questioner planning to do with/to the cable? Why are they planning that? Who are they doing that for?

So many questions, so few answers.

If they are planning to use this cable as a zip line, I would recommend against this, especially if their soldiers weigh more than 50 Kg.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: Shield Strength of XLPE cable

06/02/2016 8:57 AM

You first need the CSA and the material of the shield, from that you can calculate its resistance. Using the adiabatic equation you calculate the temperature rise.

Failing that look it up in tables, larger cable sizes invariably fail.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Shield Strength of XLPE cable

06/02/2016 9:46 AM

That anyone would want to send 2000A down the shield of a cable for any longer than it takes the circuit protective device(s) to disconnect it is a thing of great mystery.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
3
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#6

Re: Shield Strength of XLPE cable

06/02/2016 9:50 AM

From:- http://www.cmp-products.com/wiring-regulations-and-earthing-requirements

The cable armour is primarily for mechanical protection, and as already stated, this metallic armour must be effectively earthed. In general, the armour wire current carrying capacity must be equal to 50% of that of the largest current carrying conductor in the cable. The cable must be tested to determine its short circuit earth fault current rating, with the earth fault current being carried by the cable armour wires. Users should refer to the cable manufacturers design data for the short circuit fault current carrying capacity of the armour wires of each cable.

The current capacity of the 500 mm² wire is of the order of 900A (Note) so it's unlikely that the armour will carry 2000A

Note: by extrapolating from the armoured XLPE table here:- http://www.aeicables.co.uk/literature/CurrentRatings.pdf

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply Good Answer (Score 3)
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#12
In reply to #6

Re: Shield Strength of XLPE cable

06/02/2016 12:30 PM

Sorry, Randall, I am afraid Lyn is right.

It is not about the ampacity [current carrying capacity] of the cable-500 mm^2 copper/XLPE in trefoil in air at 30oC ambient [900 A], but about short-circuit withstand current [about 70 kA rms for 1 sec.500 mm^2 copper conductor XLPE insulated] and mainly for the shield short-circuit withstand current. According to IEC 60502-2 recommendation for 400 mm^2 [no more than 400 mm^2 is tabulated in Table B1] 35 mm^2 it is the recommended. For 1 second this will withstand 5 kA.[250oC maximum from 90 rated].

However all this are suppositions only. Actually we don't know almost nothing.

__________________
Julius
Register to Reply Score 1 for Good Answer
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#13
In reply to #12

Re: Shield Strength of XLPE cable

06/02/2016 1:29 PM

..."Actually we don't know almost nothing".

Apparently, that means that we do know nearly everything...

I agree that pulsed current capacity would be way higher due to thermal dissipation limit.

How much amperage would they bad boys inject into these two ring grid neutrals before they trip the entire system on fault current?

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#15
In reply to #13

Re: Shield Strength of XLPE cable

06/02/2016 3:14 PM

To quote Rummy:

There known knowns; there are things we know we know.

We also know there are known unknowns; that is to say we know there are some things we do not know.

But there are also unknown unknowns - the ones we don't know we don't know.

And if one looks throughout the history of our country and other free countries, it is the latter category that tend to be the difficult ones.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#7

Re: Shield Strength of XLPE cable

06/02/2016 10:08 AM

I'm sorry, but in my opinion it is a childish jargon:

"strength" usually it is referred to a force-electric field intensity E or D, or magnetic field intensity or density [H or B] or even current density J but not a current since no live force it is in here.

Let's say-in translation-the maximum current the shield could withstand-rms[?],peak[?]how long,[6 cycles,1 sec,3 sec[?][ 500 mm^2] copper, aluminum[?] single-core, three cores, bunched, triplexed [?]

What type of sheath/shield:

[See-for instance:

ICEA[INSULATED CABLE ENGINEERS ASSOCIATION , INC.] P-45-482-1994

SHORT CIRCUIT CHARACTERISTICS OF METALLIC SHEATHS AND SHIELDS ON INSULATED CABLE]

1-wire-helically,braid or serving, longitudinally with corrugations

2-Helically applied tape ,not overlapped.

3-Helically applied flat tape ,overlapped.[new cable, good contact ]

4-Corrugated tape, longitudinally applied.

5-Tubular sheath

Io^2*t/A^2=247E-6*SG*SH*[(To+l)/ro]*Log10(T2+l)/(T1+l))

where:

Io=Short-circuit current ,amperes

A=Effective cross-sectional area of the shield or sheath, circular mils

t=Time of short-circuit ,seconds

SG=Specific gravity of shield or sheath material

SH=Specific heat of shield/sheath

To=Arbitrary temperature [20oC]

ro=Specific resistivity of shield/sheath material

l=Inferred temperature of zero resistance for shield/sheath material oC

T2=Maximum allowable shield or sheath transient temperature oC

T1=Operating shield or sheath temperature oC

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#8

Re: Shield Strength of XLPE cable

06/02/2016 11:13 AM

I am constantly confused as to how some people get into the positions they hold.

1. If you don't know how to reply to this, you should.

2. Only the author of the statement knows what he really meant.

3. Asking total strangers to render a technical opinion based on no useable information is a waste of your client's time AND money.

4. You may not be qualified for your job.

5. Contact the author of the statement for clarification, or you may give them an incorrect answer to the question you thought they asked.

Contact the author of the statement for clarification, or you may give them an incorrect answer to the question you thought they asked.

Register to Reply Score 1 for Off Topic
Associate

Join Date: Oct 2012
Posts: 44
#23
In reply to #8

Re: Shield Strength of XLPE cable

06/05/2016 2:28 AM

you keep commenting like this?

if you don't understand what a questioner is asking, there are two options;

either ask for clarity or keep away from that post.

simple.

this is very rude of you. may be too much pride you have.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#24
In reply to #23

Re: Shield Strength of XLPE cable

06/05/2016 4:27 AM

You're the one who asked the incoherent question.

I suggested that you ask for clarity, since you didn't know the answer.

Register to Reply Score 1 for Off Topic
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#9

Re: Shield Strength of XLPE cable

06/02/2016 11:57 AM

This sounds like a problem with translation, and the requirement is not properly stated....I would think they are asking about the ability of the shielding to withstand 2000v megger for testing their field connections....but there will need to be clarification and you may need a proper translator.....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#11

Re: Shield Strength of XLPE cable

06/02/2016 12:19 PM

The key to answering this is the intended purpose the person posing the original query has in mind: "I want to interconnect the earthing of two ring main units."

Would not the answer to this depend very much on how these ring mains are earthed (grounded) presently? Perhaps the "user" wants special cable made up with this specification?

Are the attempting to inject such a current and disrupt the grid? Weaponize the grid? OMG! Call the NSA!!!

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
7
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#14

Re: Shield Strength of XLPE cable

06/02/2016 3:08 PM

Your client is trying to cheapen-out a number of ways:

1. He wants to use the shield as a grounding conductor between the RMUs, when in fact it is a protective ground for the cable in case it fails internally, the reason being that;

2. He wants to avoid the cost of connecting a separate earthing cable between the RMUs, and;

3. He wants to avoid the cost of using a four core cable,

4. He wants you to verify information that is published in the cable manufacturer's catalog/specification sheet/readily available on the web.

5. He's using an unqualified consultant who doesn't know any of this for himself and has to rely on strangers to do his work for him.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Good Answer (Score 7)
2
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#16
In reply to #14

Re: Shield Strength of XLPE cable

06/02/2016 4:07 PM

6. this client may be looking for an available scapegoat (or Judas goat) for later.

7. If you don't need their business, you really do not need their business.

8. If you need their business that bad, you should not be in business.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply Good Answer (Score 2)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#17

Re: Shield Strength of XLPE Cable

06/02/2016 8:54 PM

"Strength" is not a correct term for current-carrying capacity of a conductor, armor, or shield.

(500 mm) squared is a HUGE conductor. Correct terminology is 500 square mm, abbreviated as 500 mm2.

Capable of carrying 2000 A for how long? Continuously, or until a fault is cleared by a protective device?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#20
In reply to #17

Re: Shield Strength of XLPE Cable

06/03/2016 11:07 AM

Maybe they want to know what the mechanical strength of the shield is while carrying 2,000AMPS.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#18

Re: Shield Strength of XLPE Cable

06/03/2016 1:28 AM

I suggest you run a separate cable for earthing! That way you can install the correct csa of cable capable of carrying/handling a fault current of 2000A.

The other way is to calculate the actual fault current and run cable with either 4 of 5 conductors, one of those conductors being the earth conductor of the correct size!

Failing that, go find a reputable electrical engineer and pay him to sort it out for you!

LINK

__________________
The square root of nothing is what you make it!
Register to Reply Score 1 for Good Answer
3
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#19

Re: Shield Strength of XLPE Cable

06/03/2016 3:12 AM

Depending on manufacturer it is normally 10kA for 1 second and in no way is the shield used for earthing cables via RMU's. Run an earth wire with your cable as is normal if the XLPE is an unarmoured cable.If it is armoured you can utilise the armouring via a proper gland plate and armour gland.

Register to Reply Good Answer (Score 3)
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#21

Re: Shield Strength of XLPE Cable

06/04/2016 12:07 PM

Sorry. First of all, in my humble opinion, mrmuneb did not ask you to assist him but intended to interest YOU in something. It was for us benefit only, I think.

Second ,in my opinion, the cable about has to be medium voltage [6-36 kV] according to British Standard or IEC 60502-2. then ,in my opinion -I have to disappoint you-no 4 cores cable -standard- for medium voltage.

British Standard BS 7430 accepts cable shield as grounding conductor since in IEC World the shield cross section area is 4 times the UL recommended-in my opinion.

One does not need a grounding wire along the medium voltage cable.

Also, in my opinion,2000 A short-circuit current in a case of double ground fault it is very possible.

__________________
Julius
Register to Reply
Associate

Join Date: Oct 2012
Posts: 44
#22

Re: Shield Strength of XLPE Cable

06/05/2016 2:09 AM

I made a mistake by not posting the complete information. sorry for that.

system voltage : 13,800 V

phase to ground voltage: 8,000 V

There are two feeders that are supplying power, but one of them is redundant and will kept standby.

we have laid single core 500 mm2 XLPE armored cables.

definitely, the armor shield has to be grounded from one side.

that is why the client might be interested to know the strength of armor regarding short circuit current.

Also the system is grounded via a 200 Amp, 40 Ohm grounding resistor.

Register to Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#25
In reply to #22

Re: Shield Strength of XLPE Cable

06/05/2016 4:50 AM

And what are your earth fault ratings for the site?

Register to Reply
Associate

Join Date: Oct 2012
Posts: 44
#26
In reply to #25

Re: Shield Strength of XLPE Cable

06/05/2016 6:26 AM

Earth Fault Rating is: 200 Amp

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#27
In reply to #22

Re: Shield Strength of XLPE Cable

06/05/2016 7:14 AM

"we have laid single core 500 mm2 XLPE armored cables.

definitely, the armor shield has to be grounded from one side."

Yes the armour HAS to be grounded, but NOT as an earth path/CPC, but to ensure the cable armour is not floating and in case of mechanical damage to the cable there is an earth.

Remember this is a difference between a CPC and earthing SWA!

"The use of the armour as the means of providing earthing to the equipment supplied by the cable (a function technically known as the circuit protective conductor or CPC) is a matter of debate within the electrical installation industry. It is sometimes the case that an additional core within the cable is specified as the CPC (for instance, instead of using a two core cable for line and neutral and the armouring as the CPC, a three core cable is used) or an external earth wire is run alongside the cable to serve as the CPC. Primary concerns are the relative conductivity of the armouring compared to the cores (which reduces as the cable size increases) and reliability issues." Wikipedia

__________________
The square root of nothing is what you make it!
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#28

Re: Shield Strength of XLPE Cable

06/06/2016 5:59 AM

In a single phase- to- ground fault: the grounding resistor[Ro=40 ohm] will limit the current to 200 A.

In phase-to-ground-to-phase short-circuit case [one at each end of the cable]

if the shield and armor are both ends grounded part of the short-circuit current could flow through shield/armor also.

If Z1=Z2 [far from generator] I"2k=1.05*sqrt(3)*13.8/|Z1+2*Zo|

Z1=Z1sys+Zxfm+Z1cabl Zo=Zocabl+(Rsh*RArmor)/(Rsh+RArmor)

In my opinion, if the cable length is more than 500 ft. the short-circuit current will not be more than 19 kA.

According to Nexans U.K.it could withstand this current.

http://www.nexans.co.uk/UK/files/Underground%20Power%20Cables%20Catalogue%2003-2010.pdf

Ish+armor=20.8 kA for 1*500 mm^2 copper cond. 15 kV XLPE insulated.

According to Prysmian U.K.

http://uk.prysmiangroup.com/en/business_markets/markets/ti/datasheets/1Core_15kV_cc_new.pdf

If the shield and armor are both ends grounded an induced current will flow through shield/armor always and this will produce an increased heating of cable and then a derating factor has to be applied. See IEC 60287-1-1/ 2.3.1.

In my opinion, in this case 62% derating[ampacity around 550 A at 90oC ].

If shield/armor is one end grounded only then an induced built-up voltage could be measured at non-grounded end. Usually up 25 V it is allowable.

There are possibilities to mitigate this voltage [See IEEE 575-cross bonding and sectionalizing ].

__________________
Julius
Register to Reply Score 1 for Good Answer
Register to Reply 28 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

7anoter4 (4); aurizon (1); brich (2); IQ (2); James Stewart (4); lyn (4); mrmuneb (3); PWSlack (3); RAMConsult (1); Randall (1); SolarEagle (1); TonyS (1); Tornado (1)