Affinity Laws

06/23/2016 6:02 PM

Good Morning,

We are using a 4 pole motor on a evaporator motor, The power is about 5.5kw. We would like to replace with a 2 pole. Can someone tell me roughly about the new power will be required. I do understand that there may be other Factors involved, but only looking for a rough idea

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Affinity Laws

06/23/2016 6:19 PM

The more poles a motor has the slower it turns but the more torque it has, roughly speaking...

power = RPM * torque

http://www.engineeringtoolbox.com/electrical-motors-torques-d_651.html

By going to a 2 pole motor you would double the rpm, so you could add a 2 to 1 pulley to make it work....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#2
In reply to #1

Re: Affinity Laws

06/23/2016 6:33 PM

Sorry, I meant to say it was for a fan.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3
In reply to #2

Re: Affinity Laws

06/23/2016 6:36 PM

Is it direct drive or are there pulleys involved?

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#4

Re: Affinity Laws

06/23/2016 6:45 PM

Direct Drive,

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6
In reply to #4

Re: Affinity Laws

06/23/2016 7:31 PM

Well obviously you can't double the speed of the fan....unless by chance it's an inverter duty motor and you have a properly sized VFD laying around....I don't see this working...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11
In reply to #4

Re: Affinity Laws

06/24/2016 3:54 AM

The power needed for a fan is proportional to around the cube of the tip speed. So doubling the speed by fitting the wrong 2-pole motor instead of the right 4-pole one requires an increase in power by a factor of around 8, with attendant issues regarding the incoming supply, cables, starters and overloads; the concept is nonsensical.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#13
In reply to #4

Re: Affinity Laws

06/24/2016 12:39 PM

Dear Mr.eltech,

You have mentioned that you want to use 2 poles motor instead of 4 poles and it is direct drive.

The Affinity Law states that

Capacity is Proportional to the Speed.

Pressure or Head is Proportional to the Square of the Speed.

Power is Proportional to the Cube of the Speed.

Accordingly the fan capacity will be double, the pressure (or draught) will be 4 times, and the Power Demand will be 8 times.

This type of subject was discussed earlier few times

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Apr 2011
Posts: 8006
Good Answers: 286
#5

Re: Affinity Laws

06/23/2016 7:28 PM

If you exclude the differences in efficiency between the old fan (turning at the original rpm) and the new fan (turning at twice the original rpm) and look only at moving the same mass flow rate of air under the same conditions against the same pressure; the new power requirement will be the same as the old.

....but you understand there are other factors involved

__________________
Eternal vigilance is the price of knowledge. - George Santayana
Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7

Re: Affinity Laws

06/23/2016 8:32 PM

~44kW; worry also about centrifugal force and possible supersonic blade tip speed.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: Affinity Laws

06/23/2016 11:28 PM

The way the affinity law for speed of a centrifugal machines works is the the power REQUIRED by the machine (pump or fan) changes at the cube of the speed change. So if your fan was designed to work with a 55kW 4 pole motor and you use a 2 pole motor, the speed will double, so the fan will demand 800% of the power it used at the original design speed. So you would need a 440kW motor.

if you use a VFD to return to the original speed, then you will have insufficient torque with that motor. With the VFD, you are reducing the power rating of the motor. A 2 pole motor already has 1/2 of the torque of a 4 pole motor of the same power rating, then when you reduce the speed you are reducing the power rating at the same rate. So at 1/2 speed it has 1/2 of the power capability; 27.5 kW at what was the original motor speed using a 4 pole, which means the 2 pole motor still doesn't work. You would need to use a 110kW 2 pole motor and run it at half speed

Bottom line, you can't do this.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#9
In reply to #8

Re: Affinity Laws

06/23/2016 11:38 PM

Beat me to it, GA!

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10
In reply to #8

Re: Affinity Laws

06/23/2016 11:58 PM

Minor typo: his motor is 5.5kW rather than 55.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#12
In reply to #10

Re: Affinity Laws

06/24/2016 10:55 AM

Yeah, when I use my iPhone, I can't see the previous post so I was going from memory.

But hey, whats a decimal point among friends?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Jan 2006
Location: Tamworth, UK.
Posts: 1782
Good Answers: 45
#14

Re: Affinity Laws

06/25/2016 6:30 AM

Why change to a 2-pole motor?

As others have said you will double the speed. So if direct drive you need a smaller diameter fan or change the pitch of the blades to give the original air flow.

If you just change the motor and nothing else it is likely to run on overload and get very hot if it doesn't trip out on current to start with when it gets up to speed, but on the plus side the extra cooling of the high speed fan will reduce the motor temperature to compensate - and introduces some interesting factors into the equation. Regardless of the effect of fan speed on the evaporator process.

__________________
When arguing, remember mud-slinging = lost ground.
Register to Reply
Register to Reply 14 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

dhayanandhan (1); eltech (2); horace40 (1); JRaef (2); PWSlack (1); RAMConsult (1); SolarEagle (3); Tornado (2); truth is not a compromise (1)

Previous in Forum: Schematic Needed   Next in Forum: Induction Motor Acting as Generator

Advertisement