I have a couple of split outlets on either side of the bed. The lower outlets on each side of the bed are controlled by a wall switch. The outlets measure 120V when 'on' and 35V when 'off'. Shouldn't the voltage be zero when 'off'? If so, what is my problem and the solution?

Register to Reply
Pathfinder Tags: AC outlets
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#1

Re: Home AC outlet - Voltage on 'off'

10/16/2016 4:28 PM

You are probably just picking up (electromagnetically) induced voltage. If you are checking the voltage with a digital multi-meter, they have a very high impedance, and will show that voltage.

If you can afford it, or you can borrow one, try using something like this instead.

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Register to Reply Score 1 for Good Answer
Participant

Join Date: Oct 2016
Posts: 3
Good Answers: 1
#2
In reply to #1

Re: Home AC outlet - Voltage on 'off'

10/16/2016 5:01 PM

Thank you for your reply. I have a Fluke T5-600 Will it pick up the induced voltage?

Register to Reply
Guru

Join Date: Aug 2007
Location: Earth - I think.
Posts: 2143
Good Answers: 165
#3
In reply to #2

Re: Home AC outlet - Voltage on 'off'

10/16/2016 5:59 PM

Hard to tell. None of the literature I saw, said that it was low impedance.

Hopefully someone else here is familiar with that model, and will answer.

__________________
TANSTAAFL (If you don't know what that means, Google it - yourself)
Register to Reply
5
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#4
In reply to #2

Re: Home AC outlet - Voltage on 'off'

10/16/2016 6:46 PM

Voltmeters are usually high impedance input to avoid loading down the circuit being measured.

Plug a lamp into the socket and then measure it with your meter if you want to verify that it is unenergized.

Register to Reply Good Answer (Score 5)
3
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7
In reply to #4

Re: Home AC outlet - Voltage on 'off'

10/16/2016 9:03 PM

Ghost voltage, no amperage...stick a night light in one of the plugs, any load should make it disappear....If not, you have a short....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 3)
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#5

Re: Home AC outlet - Voltage on 'off'

10/16/2016 7:24 PM

Is the wall switch the type that is illuminated? If so, you could be seeing a voltage bled. With the wall switch off, what's the voltage between "hot" to ground and neutral to ground? You might also check the neutral to ground with the switch in the "on" position and nothing plugged in the outlets.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#6

Re: Home AC outlet - Voltage on 'off'

10/16/2016 7:30 PM

Can't find it on the Fluke site, but several suppliers quote the input impedance for voltage measurement as ">1MΩ". This is definitely high enough to give a reading of 35V from a couple of ungrounded wires running near others carrying mains AC.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply Score 1 for Good Answer
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#8

Re: Home AC Outlet - Voltage On 'Off'

10/16/2016 10:31 PM

This is probably an induced voltage. Induced by the one wire laying next to the other. Could also indicate poor grounding. The earth/ground wire should also be laying next to the A and N wire and conduct induced voltage to ground. I had 240V on an earth/ground wire that was all induced voltage. Found that the installer hadn't connected the wire to the terminal block. Gave a huge, loud spark when put near the tin roof. ( about 5mm ) Jim

__________________
Where's the KaBoom? There should be a KaBoom!
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2014
Location: Hemet, Land of milk and honey.
Posts: 2365
Good Answers: 36
#9

Re: Home AC Outlet - Voltage On 'Off'

10/16/2016 11:30 PM

You didn't mention if the tested voltage was on the switched or unswitched sides of the duplex.

Remember in a system, you have a main panel with circuit breakers. In a simple system, you will have one main circuit breaker ( could be 30-50 amps) and several branch circuit breakers ( 15-20 amps ).

If any or all of the branch circuit breakers are off and the main circuit breaker is on and you detect voltage, this could mean that one or more of the branch circuit breakers are leaking voltage.

If you turn off all of the branch circuit breakers and you turn off the main circuit breaker and you detect voltage, this could mean that the main breaker is leaking voltage.

A voltage leak can be observed by placing your voltmeter leads onto neutral ( white wire ) and ground/earth ( usually the ground is a bare copper lead ) or black to ground, or red to ground - in a 3 wire branch circuit.

Houses are usually wired with Romex. For example, Romex can be 14/2 , this means that there is one black wire and one white wire, then you can have 14/3, this means that one wire is black, one wire is red and one wire is white. Some Romex cables have an uninsulated ground and some have an insulated ground.

In some cases, detected voltages can be between 25-35 volts.

As a matter of safety, when I work on a circuit, I always shut off the main and before i start, I always check for residual or leaking voltage beforehand.

If you believe you have an issue with your system, contact an electrician for assistance.

Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#10

Re: Home AC Outlet - Voltage On 'Off'

10/16/2016 11:45 PM

You may find it useful to review parts of a thread back in February 2013 regarding "LED light bulbs", especially my posts #61 and #71.

http://cr4.globalspec.com/thread/82870#comment1150899

The above link may well take you to some other comment within that thread, but post #61 refers to a set of experiments I did to prove why you are measuring that voltage.

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#11

Re: Home AC Outlet - Voltage On 'Off'

10/16/2016 11:49 PM

It is capacitive coupling, the insulation is your dielectric, the conductors are your plates. One live conductor (the top outlet conductors) runs alongside the switched conductor for a good distance, providing enough capacitance to build up a measurable voltage on the floating plate.

I've measured voltages as high as 85Vac (phantom) on a system with 120Vac supply max, in a mess of cables buried under the floor in an industrial facility. I used to think the maximum was 60V, half of the supply voltage coupled to ground. We see anywhere from 5 or 6, to the highest I saw at 85V.

The current flow is very low, you see the charging current (as mentioned before), is very low, and any kind of load, including your finger (nightlight SolarEage/Rixter)(Wiggy type meter or ET200(Kilowatt0), will drop the voltage to near zero.

Register to Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#12

Re: Home AC Outlet - Voltage On 'Off'

10/17/2016 1:43 AM

Check voltage between Neutral and earth; should be less than 0.5V AC; if not wiring must be thoroughly checked.

__________________
Subramanyam
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#13
In reply to #12

Re: Home AC Outlet - Voltage On 'Off'

10/17/2016 3:18 AM

The voltage on the neutral is a function of the neutral current and the earth loop impedance. So you can't say that.

__________________
Good moaning!
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#14
In reply to #13

Re: Home AC Outlet - Voltage On 'Off'

10/17/2016 4:17 AM

That's the problem with unspoken assumptions, such as neutral being earthed with less than V/I resistance....

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#15

Re: Home AC Outlet - Voltage On 'Off'

10/17/2016 5:20 AM

Plug in a load while it is switched off and the voltage should disappear. If it does then the problem is simply a failure to recognise that a high input impedance voltmeter is picking up an induced voltage as a result of being close to an AC socket and its wiring. If it doesn't, then you have a faulty socket, which is £6 and 1/2 hour's work to fix.

__________________
Good moaning!
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2014
Location: Hemet, Land of milk and honey.
Posts: 2365
Good Answers: 36
#19
In reply to #15

Re: Home AC Outlet - Voltage On 'Off'

10/17/2016 10:04 AM

I didn't know that the, " ( £ ) " was the type of currency used in France.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Apr 2015
Posts: 21
#16

Re: Home AC Outlet - Voltage On 'Off'

10/17/2016 6:18 AM

You probably do not have a problem. Use a "wiggy" to measure the voltage. You will find that the voltage is nonexistant.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Dec 2009
Location: Tampa Florida USA
Posts: 180
Good Answers: 3
#17

Re: Home AC Outlet - Voltage On 'Off'

10/17/2016 7:44 AM

You didn't explain completely where you were detecting power. Presumably, between hot and neutral.

But: It is possible for a "backfed neutral" to be carrying power. This happens when two or more circuits share a neutral. For example, one light bulb can be turned on, the current is returning to the panel through the neutral. Another socket sharing that neutral can show voltage to ground on that neutral.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#18

Re: Home AC Outlet - Voltage On 'Off'

10/17/2016 8:30 AM

You didn't say how old this building / building wiring is. In the north eastern states , if someone hasn't gotten scared enough of old wiring and replaced it, you can still find houses where they switched the neutral, not the live leg. With a multi-meter, you would notice that live side even with out a true ground, as noted in previous replies from others. (I know from experience at my Grandfather's house - sure jolts you when you think you have a light socket turned off)

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#20

Re: Home AC Outlet - Voltage On 'Off'

10/17/2016 10:55 AM

You have a digital switch on the wall that uses a triac. Leakage on triacs is the norm rather than the exception. No big deal. If you need to get zero, you need a digital switch using a relay rather than a triac.

Register to Reply Score 1 for Good Answer
2
Participant

Join Date: Oct 2016
Posts: 3
Good Answers: 1
#21

Re: Home AC Outlet - Voltage On 'Off'

10/17/2016 11:45 AM

Thank you to all who replied to my question. I'll try to answer some of the questions raised. The house is about 8 years old. The voltage measurements are on the switched outlets when the switch was 'off'. The switch is a standard switch without any indicator lights or LED's. The voltage is zero between the neutral and ground at all times. When the circuit switch is 'off' and a lamp is connected to one of the two switched outlets and turned on, the voltage between the 'hot' and 'neutral' is zero, so I must have been seeing an induced voltage. Once again, thank you for your help.

Register to Reply Good Answer (Score 2)
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#22

Re: Home AC Outlet - Voltage On 'Off'

10/17/2016 1:35 PM

I certainly do hope this is "ghost" voltage (EM pickup from nearby wires), and a high impedance measurement, but what if there is a lot of current on neutral somewhere nearby. That could mean there is actual voltage present on neutral that could be a hazard.

Check each against ground, please. Also do the plugged in lamp test. Get back with us.

After further review, I see that my answer is several days and a dollar short of being relevant.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Register to Reply 22 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (2); dj95401 (1); dkwarner (1); James Stewart (1); JIMRAT (1); JohnDG (1); Jpfalt (1); Kilowatt0 (2); kvsubramanyam (1); Phys (1); Rixter (1); rwilliams (1); salisburysenior (2); sharpstick (1); SolarEagle (1); Thomas Wiklanski (1); tonyhemet (2); Tornado (1)

Previous in Forum: ABB ACS800 Problem   Next in Forum: Current Measurement

Advertisement