MCCB Dilemma

11/18/2016 1:11 PM

I would like to replace a series of 6 schneider mccb, NSX 160F with brand new LS'IS TS160N. The breaking capacity and other characteristics are fine. I am worried though about the Ui: Rated insulation voltage which is at 750V instead of 800V like the previous schneider. Is this much of an issue??

Register to Reply
Pathfinder Tags: MCCB rated insulation voltage UI
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: MCCB Dilema

11/18/2016 4:50 PM

Ask Schneider. Their telephone number is on their website.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#2

Re: MCCB Dilema

11/18/2016 6:53 PM

It is an issue if you want 800V operation but not if you want 750V. But you have not given this essential fact!!

Offhand I can only think of 600 and 690V as standard voltages.

Check with Schneider, I think a rated voltage allows for normal tolerances of a supply.

Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: MCCB Dilema

11/18/2016 7:14 PM

To put in more directly, if you are USING it at a voltage of 750VAC or less, then no, it will not make one bit of difference. You didn't say what you are using it for...

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#4

Re: MCCB Dilema

11/18/2016 9:29 PM

Basically your operating voltage are either 380 or 440 volts. Changing the MCCB from rated insulated from 800 V to 750 V does not have any impact to it. You need to ensure that the existing MCCB rated Ampere and the KA are the same as the new unit. For the MCCB mounting holes make sure that they are the same dimension, otherwise you need to drill a new mounting holes.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: MCCB Dilema

11/19/2016 1:32 AM

You don't know the voltage, and maybe the OP doesn't, either.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Nov 2016
Posts: 2
#6
In reply to #4

Re: MCCB Dilema

11/19/2016 1:36 AM

Thanks

The breaking capacity for the various rated voltages are fine. I guess am worried about how likely a voltage 50v above my Ui(750v) is to occur. Any advice??

Register to Reply Score 1 for Off Topic
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#7
In reply to #6

Re: MCCB Dilema

11/19/2016 6:40 PM

Your MCCB "Rated insulation voltage which is at 750V instead of 800V like the previous schneider." is the maximum voltage capacity that the MCCB can withstand before flash over between the phases inside the MCCB compartment if there is an voltage rise.

"Rated "insulation voltage (Ui) is the maximum voltage that the MCCB can resist. It is higher than the rated working voltage, in order to provide a margin of safety during field operation"

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8
In reply to #6

Re: MCCB Dilema

11/19/2016 10:54 PM

So are you USING it at 750VAC? I seriously doubt that, it's not a voltage used anywhere in the world.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#9
In reply to #6

Re: MCCB Dilema

11/20/2016 1:40 AM

At least you should let us know what is your operating voltage. The voltage that is connected to your MCCB or your factory standard working voltage,

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply Off Topic (Score 4)
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#10
In reply to #6

Re: MCCB Dilema

11/20/2016 2:01 PM

So your worried about impulse or voltage spike events potentially causing damage to your MCCBs when running on a standard 3ph 400V, 480V or similar system.

An extra 50V either way is not much of a safety margin when voltage spikes are concerned, if you are concerned then you have to add surge or lightning protection not rely of the impulse voltage rating of the device as the primary method of protection, especially if the downstream connected electrical equipment also cannot handle the higher voltages.

Contact your local Schneider agent directly and ask them, it is likely they just redesigned their product range and that came out to be the new value (possible test standard revision) and it makes no difference to your selection process.

__________________
jack of all trades
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); Drepain_Elec (1); jack of all trades (1); JRaef (2); PWSlack (1); Simon Wan (3); Tornado (1)

Previous in Forum: Neutral Shift   Next in Forum: The RF Magnetics Lab Kit Demystifies Inductors

Advertisement