Electrical Magnet Coil

04/06/2017 2:14 PM

i have abb 11kv contactor work in capacitor bank, its coil energized via electronic cart called current equalizer ,this card damaged , but the coil is ok , i tried to energize the coil from 220v dc source ,the contactor closed ok but when i remove the 220v dc there was very high spark and the coil got hot altho i apply the 220v dc for short time i tried use diode and capacitor and resietor to reduce back emf off contactor coil but it didnt work also i dont know why the coil got hot rapidly (coil resistance <1 ohm) .

any suggestion???

Register to Reply
Pathfinder Tags: magnet coil
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: electrical magnet coil

04/06/2017 2:20 PM

Check the amperage draw, you may have a shorted coil....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Member

Join Date: Apr 2017
Posts: 5
#2
In reply to #1

Re: electrical magnet coil

04/06/2017 2:42 PM

the coil is ok that it energized and attached the contactor and close it.

Register to Reply
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#3
In reply to #2

Re: electrical magnet coil

04/06/2017 2:57 PM

220vdc into 1ohm is nearly 49kW. Are we really surprised by this coil getting warm, Mildred?

__________________
Good moaning!
Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9912
Good Answers: 1141
#5
In reply to #2

Re: electrical magnet coil

04/06/2017 3:50 PM

the coil is ok that it energized and attached the contactor and close it.

220 volts / 1 ohm = 220 amps (assuming your power supply could put out that much). The magnetic field from that current probably attracted the contactor and any other iron that happened to be nearby. I'd say your coil is probably fried.

Register to Reply Good Answer (Score 2)
Member

Join Date: Apr 2017
Posts: 5
#7
In reply to #5

Re: electrical magnet coil

04/06/2017 4:12 PM

the coil is ok,do you know how i can reduce this current and keep the magnetic force at the same time???

Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9912
Good Answers: 1141
#11
In reply to #7

Re: electrical magnet coil

04/06/2017 8:01 PM

Nothing with 1 ohm resistance takes 220 volts dc! Either it should not be energized with 220 volts dc or it should not be 1 ohm resistance, period!

Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#12
In reply to #7

Re: electrical magnet coil

04/06/2017 8:06 PM

If that coil was okay before, it's toast now. Replace it and the card.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#26
In reply to #7

Re: electrical magnet coil

04/09/2017 5:24 PM

The time to discuss this matter directly with the original equipment manufacturer is long overdue.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#29
In reply to #7

Re: electrical magnet coil

04/11/2017 5:46 AM

Yes. Talk the problem through with ABB's technical advisers over the telephone.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: electrical magnet coil

04/06/2017 3:02 PM

i tried to energize the coil from 220v dc source

And it got hot? Is the coil control voltage the card is supposed to produce actually 220V dc or something else? If so then the coil resistance is too low, and I suspect a faulty coil.

Check the ABB datasheets and find out what your installed coil resistance is supposed to be, if it doesn't match replace the faulty coil.

__________________
jack of all trades
Register to Reply
Member

Join Date: Apr 2017
Posts: 5
#6
In reply to #4

Re: electrical magnet coil

04/06/2017 3:59 PM

the card output when i measured working card its output was 200v dc and also when i measured ac output it give 112v ac i check with oscilloscope i found a strange wave i think it is ribble so i energize the coil with 220 v dc and the cont actor already work i need way to reduce the sealing current of the coil and way to decrease the back emf when d energize the coil.the resistance off coil i dont remember if it was 0.6 ohm or 6 ohm.

Register to Reply
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#9
In reply to #6

Re: electrical magnet coil

04/06/2017 5:52 PM

Even if it was 6 ohms, that means your coil was trying to draw 2202/6 = 8067 watts. Come on mate, use your head. NO contactor coil is designed to dissipate 8 kW.

Register to Reply Score 1 for Good Answer
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#10
In reply to #6

Re: electrical magnet coil

04/06/2017 6:03 PM

I have doubts that either the coil is faulty or you are using the wrong supply voltage. Have a look in the manual and on the equipment and see if you can find a part number and voltage. If you put the wrong voltage on the coil it is probably damaged and needs to be replaced like the driver card.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#16
In reply to #6

Re: electrical magnet coil

04/07/2017 5:15 AM

When you measured that 200VDC: was it under load or were you measuring it with a high impedance meter?

Maybe there is a large series resistor on the board.

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8

Re: Electrical Magnet Coil

04/06/2017 4:33 PM

Is an economy resister fitted in line with the coil?

If the resistor has short circuited then the coil will have the full voltage while in the closed position.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Apr 2015
Posts: 21
#17
In reply to #8

Re: Electrical Magnet Coil

04/07/2017 7:57 AM

resistors don't "short", they fail open

Register to Reply
Power-User

Join Date: Dec 2007
Posts: 177
Good Answers: 6
#18
In reply to #17

Re: Electrical Magnet Coil

04/07/2017 9:30 AM

carbon resistors CAN go down in value! That's only one reason they are not used much anymore.

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#13

Re: Electrical Magnet Coil

04/06/2017 8:15 PM

Replace the current equalizing card; it's job is to limit the inrush current until the movable armature is sealed in, then reduce it even further since the holding current is much lower than the inrush. Failure to do so will result in a burnt coil and/or fire.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#14

Re: Electrical Magnet Coil

04/07/2017 12:04 AM

Usually for D.C. Contractors, there will be Economic resistor in series with the coil, and it will be shorted with auxiliary nc contact of the contactor, so that during pickup the coil will get full voltage and after pick up the resistor will be in the circuit to maintain the contactor in on position. After pickup the nc to become open

Check this circuit.

Nc means normally closed

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#19

Re: Electrical Magnet Coil

04/07/2017 2:36 PM

You have phoned someone at ABB about this, haven't you?

__________________
Good moaning!
Register to Reply
Anonymous Poster #1
#20
In reply to #19

Re: Electrical Magnet Coil

04/08/2017 2:40 PM

Funny, it worked yesterday.

Register to Reply Score 1 for Good Answer
Member

Join Date: Apr 2017
Posts: 5
#21

Re: Electrical Magnet Coil

04/08/2017 2:56 PM

dear sirs,

thanks for replying ,may be i couldn't describe what i need,

the equalizer card is damaged and it is very expensive so i need another inexpensive way to energize the coil and in the same time dont damage it ,my friend already rewind another contactor coil in another substation that it work in 110v dc and it already work for more than year now ,but i search for method to energize the original coil without rewind it ., i already agree that 220v dc supply isn't the solution ,but i need suggestions to energize the coil with inexpensive trusted method,i may use resistor with nc contact of cont actor but it need try and error ,also instead of resistor i may use high resistance coil.

thanks..

Register to Reply
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#22
In reply to #21

Re: Electrical Magnet Coil

04/08/2017 3:08 PM

Your electric utility cannot afford replace that card and a new contactor coil??? Surely not! That doesn't sound very promising in the long run. How much does a power-outage cost in comparison to the cost of a proper repair? Cobbling things together with bubblegum and baling wire and your system is living on borrowed time. Trial and error? You tried it once and it resulted in error - you fried your contactor coil and very likely scorched the insulation.

If you're going to rewind it (I'm guessing you have no choice, given that your utility company seems to be flat broke) find a contactor with similar specs whose coil operates on the voltage you wish to use and wind it according to that. We cannot see your contactor from here and so we can only guess as to what its specs are, plus that coil was designed to be used with that card, not in the manner you're proposing.

A coil designed for ~110-220 vdc contactor service will typically have a resistance in the 100s of ohms and in the ballpark of 10 watts' power dissipation or less. NOT ohms and kilowatts.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#23
In reply to #21

Re: Electrical Magnet Coil

04/08/2017 3:36 PM

What is ABB's part number? How big a contactor are we looking at?

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#24
In reply to #21

Re: Electrical Magnet Coil

04/09/2017 3:29 PM

Don't, the risk is too great. Contact ABB for a proper solution which may just mean replacing the coil with a different type. The card is there for a reason. Heck, look online and buy one second hand.

my friend already rewind another contactor coil in another substation

This suggests your application is an 11kV network SUBSTATION!!! See above warning, I don't care what country you are in and what you believe is common industry practice this is a serious application, GET THE PROPER REPLACEMENT GEAR OR YOU WILL REGRET IT!

__________________
jack of all trades
Register to Reply
Guru

Join Date: Dec 2016
Posts: 2914
Good Answers: 115
#25
In reply to #24

Re: Electrical Magnet Coil

04/09/2017 3:51 PM

Exactly!

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#28
In reply to #21

Re: Electrical Magnet Coil

04/10/2017 3:11 PM

The card may have been damaged by a contactor coil failure, 6 ohms is too small except for a 25 volt dc rated coil with an economize resistor, or maybe an ac coil, still less than 100 volts ac.

As long as you have a circuit through the coil, the magnetic field may pull in the armature, but that doesn't make the coil good. It just has enough ampere turns to pull in the contactor, the amperes are just unsustainable.

The rewind is likely your only option, other than repairing the card and likely repairing the coil.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#30
In reply to #21

Re: Electrical Magnet Coil

04/13/2017 7:21 AM

<...it is very expensive...> So, what is the cost of not doing it? Why bother to carry out a repair? Why not just lock the door and throw the keys away (rhetorical questions - NNTR)?

That would be cheap!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Anonymous Poster #2
#27

Re: Electrical Magnet Coil

04/10/2017 12:07 AM

hello Dear,

first of all u have to clear about electronic cart?

which type of circuit you are using as well as their values.

Register to Reply Off Topic (Score 4)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#31

Re: Electrical Magnet Coil

04/13/2017 9:41 AM

How did the telephone calls with the manufacturer go?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 31 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andrew Westman (5); Anonymous Poster (2); Crabtree (2); gutmonarch (1); jack of all trades (3); lrsheldon (1); mkhalifa (4); PWSlack (4); RAMConsult (1); ramvinod (1); Randall (1); Rixter (2); rwilliams (1); SolarEagle (1); Thomas Wiklanski (1); TonyS (1)